My Rheem gas furnace Model#RGLG-10EAUEA is cutting out a few second after it ignites and the main blower kicks in for two minutes. It does not seem to have a flame sensor. What could be the problem?
  • don-ohio Jan 04, 2017
    Look for the flame sensor again. Can be a glass lens(they don't all reach back into the burner) opposite side of the igniter or down below igniter connection.Probably is the problem.
  • Heating & Co... Master
  • 3,315 Answers
Pressure switch or dirty flame sensor
Posted on Dec 31, 2016
  • 3,228 Answers
No luck in looking up your model number...
Try Rheem contact... (below)
http://www.rheem.com/productdocuments.aspx?RGLG-10EAUEA
Posted on Jan 04, 2017
RHEEM RGLG-05EAUER Occasionally, on startup, there is a fair gas smell from the vents for a few seconds.
I think I'd have it checked for a bad heat exchanger. At the very least, make sure you have working Co2 detectors on all levels of the house. You should not be smelling gas from your hear ducts. This is not normal. If anyone in the house is developing a head ache, that would indicate a heat exchanger problem.
If you need further help, I’m available over the phone at https://www.6ya.com/expert/david_29ad5d1dd86564b0
Nov 20, 2016 | Heating & Cooling
LX2000 gas furnace. It starts and runs for about 5 seconds, then why does it shut off?
Fix Furnace Flame Sensor (Flame That Goes Off) - YouTube
? 1:22
https://www.youtube.com/watch?v=fBJ3r9MUa-U
Nov 29, 2011 - Uploaded by RochNoure
A Furnace Flame Sensor is a safety device that reads the temperature and ... easy fix, but the furnace is ...
Troubleshoot the ignitor of the Rheem RGDA model gas ...
? 5:53
https://www.youtube.com/watch?v=Bx1pXONg2Oc
Dec 12, 2012 - Uploaded by grayfurnaceman
Troubleshoot the ignitor of the Rheem RGDA model gas furnace.... Jun Sim 5 months ago ... My lennox ...Missing: lx2000
Rheem Criterion II No Heat - YouTube
? 0:47
https://www.youtube.com/watch?v=yOSk6qvpWbA
Jan 7, 2010 - Uploaded by Work12Progress
Rheem Criterion II gas furnace model # RGPH-07EAMGR. When a call for heat is made t wo green led's ...Missing: lx2000
Heater will not kick on unless... [Archive] - Self Help Forums
www.selfhelpforums.com/archive/index.php/t-2153.html
Oct 19, 2004 - 25 posts - ‎9 authors
After a certain amount of time of not running, the heater will refuse to kick back on. ... 2 flashes, then a 2 second pause = pressure switch is open. What do .... On LP gas furnaces, the spark starts and the gas valve opens. ... Buffing them up with a little steel wool (5 minute job) is a good annual PM thing to do.
Dec 16, 2015 | Heating & Cooling
I have a Rheem Furance that has turned off. Just a few hours ago the main fan turned off. The Furnace doesnm't light even the draft fan does turn on and then the main fan blower motor turns on. I can hear...
You will need to reset the furnace by turning the power off to it. Then as the furnace tries to light, watch the LED for blinking. Hopefully it will give a code other than 1. Try checking the air filter for blockage, make sure all hoses are free of moisture and any drains are not blocked. Check the air intake and exhaust pipe for sags where water could block it.
The sequence of operation is this:
Thermostat calls for heat, the LED may blink telling you it registers the call. The inducer (exhaust) blower starts closing contacts in the pressure switch (small disc shaped thing), the igniter glows orange (seen thru a small window high up on furnace front), gas valve opens allowing main burner to light, flame travels to all other burners, flame rod senses flame within a few seconds and keeps gas on. Room air blower starts within 90 seconds.
Any deviation or delay in this sequence and it goes into lock-out.
Jan 22, 2011 | Heating & Cooling
Hello, I have a Amana Air Command 80 model #GHI90A50, 22 years old. This furnace is on its third ingnition module (last one two yeras ago). The symptom I am trying to diagnose has been ongioing since this...
If your furnace lights and the gas stays on for 8 to 10 seconds, then shuts right back off, then you need to clean your flame sensor with light sand paper or steel wool. You might need a new flame sensor, but most of the time they can be cleaned an will work well after cleaning.
Dec 05, 2010 | Heating & Cooling
Have a rheem furnace/ten yrs old.just replaced thermocoupler and gas valve,furnace will turn on thermocoupler will get red but no heat? whats up?
I know it may sound strange but check to make sure the gas cut-off valve is turned parallel with the gas pipe. If its open, you may have a failed fan proof switch. air pressure from draft induced blower causes the switch to click and open the main gas valve. if this this switch doesn't click(close contacts) the maing as valve will not open to ignite the burners. its a sequence of events that a furnace goes through before it ignites the burner for heat.
Nov 28, 2010 | Heating & Cooling
Rheem 90+ NG Furnace. When furnace starts, draft inducer starts, ignitor glows and gas ignites. Burners stay lit for 10 seconds or so, then the flame reduces for a few seconds then goes out. Main blower...
Check the draft inducer air switch ( vacuum diaphragm switch) If the switch is opening when the burner starts, you might have a blockage on air piping coming into the furnace. Also prime the condensate trap on the condensate drain from the combustion fan. Also check the gas pressure, if your gas pressure is dropping, the gas pressure switch will shut it down. If it's too high the moment it comes on could raise the pressure in the furnace dropping out the combustion fan proving switch.
Oct 29, 2010 | Electric Circuit Breaker Kit for Furnace
Furnace blower fan problem
Hi check out the fan control switch could be dirty itsounds like this is nit cutting to let fan run also check setting fan off fan on , temp rise and fall
Feb 06, 2010 | Heating & Cooling
Furnace not kicking on when thermostat calls for heat
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
Jan 10, 2010 | Heating & Cooling
Rheem Furnace sometimes takes a couple of ignition cycles before
Try cleaning the flame sensor. It is located right besides the last burner. Looks like a thick piece of wire. Take steel wool and gently remove the carbon that has built up. Should only take 4 or 5 strokes. Let me know how it goes after that. ken
Dec 23, 2008 | Heating & Cooling
Dayton blower fan repeatedly kicks on and off
chech the air filter is clean and the fan limit switch look to change fan limit
Nov 01, 2008 | Dayton Gas Furnace Heater
Open Questions:
vulcan bonaire comfort control External natural gas electronic ignition 2004. ISSUE: Fan blowing only cool air continuously. Forced to kill power to stop it. model is one of the following. MB514E,20E or 30E. Going by mech drawing parts list. i can confirm what type of sensors i have cleaned with very fine sandpaper. flame sensor PN 5441603SP and IGNITER ELECTRODE PN 5441602SP The fault code i see is described as the following. There are x4 LED's. Sequence Left to Right. LEGEND: 1 Flame Sensor 2 Pressure switch 3 OverTemp 4 Diag. R Red G Green S Solid Colour B Blinking LED Behaviour. In order 2RS & 4GS Until i hear ignition. 2RS & 3RB Duration: split second 2RB,3RS & 4GB Duration: split second 3RS & 4GB Duration: Until it has completed blinking x4 times. 3RS Duration 4 seconds Repeat last two mentioned behaviour. in my own opinion, as a safety feature, the unit thinks that it has overheated or is about to. so kills the gas and force feeding cool air to heating components to save it from frying. Does this mean i have fault 04 if so does this mean i may have a faulty igniter or flame sensor or maybe a faulty as described in the mech drawing SWITCH OVER TEMPERATURE 120 degrees celsius. Am i correct here? Is this the over temperature cut out switch? if no one can really pinpoint which part requires replacement, can you at least, in sequence advise which parts to purchase? so then ill just try my luck. i wonder how to properly test if flame sensor, igniter, over temp etc is faulty with a multimeter. do i just perform a continuity test. I wonder what other parts can i test related to this fault im getting.