Turns on & off..but, no heat.
Clicks on & off....pilot light glows...it, does Not ignite Blower will work IF turned to fan only.
  • Heating & Co... Master
  • 3,253 Answers
Check pressure switch and check flame sensor is clean .
When I try to use my Thermolaire model SU402E, the pilot lights( and stays lit), but the main burner will NOT ignite.. any suggestions as to what could cause this if the pilot stays lit?
Bad igniter? When you 1st try it the gas valve will give enough gas that you would get the burner lit if the igniter was glowing red. If you're desperate you can light the igniter area w/ an aim n flame, but you definitely want to do that w/ caution and crank up your t-stat so the furnace stays on awhile Cuz you'll have to do it again for heat or buy an igniter($40 or so)
Jan 14, 2015 | Heating & Cooling
Pilot lights up but would not fire up into heating, I have brivis buffalo 85
This is the proper cycle of a furnace and what should happen.
Inducer motor kicks on, it runs for a little bit, about 3-5 seconds, then you should see a bright yellow glow, this is the igniter, shortly after, you should hear a click and the gas should start to flow, almost immediately it turns to a blue flame. Then your igniter should turn off and the blower motor start up.
If the pilot turns on and the gas ignites, then shortly after the unit shuts off, chances are this is your blower motor. It is not starting up, then the heat limit is reached in your unit and the safety shuts it off.
Mar 02, 2011 | Honeywell Programmable Thermostat Heater
No flame
Several steps here to check...
turn power off unit and back on
set thermostat to heat
watch for pilot to ignite..igniter should glow orange or cherry red or spark if its a spark type ignitor
Did you see a pilot light ignite?
If not you probably have a bad igniter.
If pilot lit....in a little bit you hear a click of the gas valve opening..then the main burners will ignite
If you see the pilot and the main burner lights but goes out in a few minutes or immediately you may have an issue of the "high limit" switch tripping.
Is the blower fan turning that blows air out of your vents?
are all your vents open in your house? too many times i see homes with almost all vents shut.
Jan 08, 2011 | Goodman GMS90703BXA Heater
Fan turns on, pilot on left side turns on red light at bottom stays solid during entire time then pilot goes out and blower stops no heat please help
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remaing solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
Oct 05, 2010 | Goodman GMS90703BXA Heater
I HAVE A RUUD SILHOUETTE GAS FURNANCE. The pilot light keeps blowing out. When I light the pilot flame it seems to work perfectly at ignition. As the Manual instructs, I hold down the ignition switch for...
Short answer, yes. However you could have another problem. Replace the thermocouple that keeps the pilot lit. You can get a universal one at any good hardware or farm store. Make sure the new thermocouple is well into the pilot flame. If the blower knocks out the pilot flame again, I would be suspecting cross contamination from a crack in the heat exchanger. As the exchanger heats up, it may be causing a small crack to open and allows the blower to extinguish the flame. It may also be causing a leak of Carbon Monoxide into the heated room air. I would get it checked out very quickly.
Mar 07, 2010 | Ruud UBHC Air Conditioner
I have a Trane xe 70. The Heat is not turning on. The ignitor will glow but NO gas or blower. I turn on the fan and the blower does work but not when HEAT is selected on the t-stat. Also the LED light...
Check to see if you get 24 volts AC at the gas valve from the circuit board when the igniter is glowing. If yes, bad gas valve or blockage in gas train. If no, bad circuit board or broken wire
Feb 07, 2010 | Heating & Cooling
Turn heat on, I hear it ignite and furnace runs and runs fine then usually there is a slight delay and blower turns on and blows heat, but now it does not, I put my hand up to a nearby vent to no heat and...
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
Jan 06, 2010 | Goodman GMS90703BXA Heater
We have a Janitrol PGB 048125-1 unit and it is not blowing heat. the fan comes on when in fan only mode on thermostat but once we turn it to auto it goes off. we cannot get the unit to blow hot air. does...
If the unit is newer than 10 years I guess there will be no pilot light per sey. You will have to look at it to tell for sure. Here it is supposed to work. When there is a call for heat the thermostat will close and send a signal to the furnace to start the exhaust blower. When the blower gets up to speed, it closes a pressure switch that will send voltage to the gas valve and to the igniter. The igniter glows or sparks lighting the pilot. Once the pilot lights it sends a signal that all is well, then the gas valve opens up more and the burner(s) light. There is a sensor that tells the control board when the flame has stayed lit. Once that is done, after a period of time or as the heat exchanger gets to a specific temperature, it will turn on the room air blower and blow hot air. Once the thermostat has been satisfied, the furnace turns off. Now, get in front of the furnace and with the door panels off (you may need to tape down the door safety switch to make this work) watch the furnace go thru each step I described. Once you see where the problem is, you can start the proceed of repair. There may even be a flashing light indicating a problem. Find the wiring diagram on the furnace and look for a diagnostic chart and compare the number of blinks to this chart.
Oct 17, 2009 | Goodman Heating & Cooling
Blower works but no heat
If in fact you have the above listed furnace, you do not have a pilot but electronic ignition. You will need to remove the front cover on the furnace, tape down the door safety switch and then have someone help you by turning up your thermostat to a very high setting. Watch and listen inside the furnace. There should be some blinking going on at the control board followed by a small blower fan starting up. Then after 10-15 seconds there should be a click followed by an orange glow viewed thru the viewing window to the burner section. In a few seconds the gas valve should click and the burners will ignite. There is a safety switch that will sense flame and then keep the gas going to the burners. If it does not sense it, it will shut it off within 10 seconds. If all is well so far, your blower will turn on in about 90 seconds after flame. There is a diagnostic code chart on the back side of the access door if you get an error code (blinking) on the control board.
Always check little things like air filter, condensate drain and broken or loose wires.
Nov 05, 2008 | Goodman GMS90703BXA Heater
Heating & Cooling Logo
Top Heating & Cooling Experts
Paul Carew
Dan Webster
Dan Webster
Tim Whalen