Nordine mgbb limit switch trips after blower comes on
  • Heating & Co... Master
  • 3,044 Answers
I'm guessing that is the "mgbb" is short-hand
for a real number...
The SHORT-HAND answer is that TOP END limit switches
trip because things have gotten hotter than the design intent...
(or ... unlikely that switch is bad).
More likely... the switch that should have turned on the blower (sooner) is not turning on the blower soon enough to dissipate the heat from the exchanger (into the desired area)...
Some of the OLDER VERSION switches are adjustable...
I don't know about NORDYNE (see below, part type).
If you don't mind the risk of electrocution try to start the blower motor sooner... to see if you can avoid the high-temp situation I BELIEVE is causing your grief.
JUST replace the blower motor sensor...
If I'm wrong you have a SPARE sensor you always wanted anyway
$15 ( @ sears)
Posted on Dec 24, 2016
Goodman gms90703bxa tripping overheat limiters, keeps flashing 6 times, open roolout
When unit come on you need to watch the flames that shooting in all should blue. If there is any red flame kick out that would trip the flame role out switch. If the is the case you need a need heat exchanger.
Feb 09, 2015 | Goodman GMS90703BXA Heater
Armstrong ultra advantage 93, propane. blower kicks on right away when i call for heat via thermostat. will not ignite. blower keeps running. fan set to auto. help!
Make sure that there is not a manual limit that has tripped and needs to be reset. Roll out limits, and check primary limit. On some models if a limit is tripped the blower starts to run right away.
I don't know if this will fix it. But that is where I would start if I was working on this problem. Then I would check if the combustion blower starts and then if it makes the pressure switch. Then check if the ignitor is sparking or glowing and getting power to it. A good volt meter will help in checking.
Good Luck.
Oct 26, 2013 | Honeywell Furnace Air Pressure Switch...
How to fix a pressure switch on a goodman Gms807034ana
Since the burners light this eliminates the pressure switch as the problem. Typically when the burners come on and shut off quickly a flame sensor, ground problem or the limit switch tripping are the main reasons. Since the flame sensor has been replaced, check the limit switch
Jan 04, 2013 | Goodman GMS80453ANA Open Flame Mid-Size...
Gmp075-3 which is the main limit switch ?
The limit switch is a credit card size shaped switch right behind the burners which has two wires attached to it. This switch will trip if the Furnace is overheating, this can be causes by a weak blower motor, dirty air filter, dirty blower wheel....anything that restricts airflow.
Dec 17, 2012 | Goodman GMS90703BXA Heater
I have a goodman model gms80703ana the burner comes on and when the blower comes on the burner goes out.
This can be due to a dirty flame sensor or a high limit switch tripping. Clean the flame sensor first, this is a metal rod on the opposite side of the igniter, take steel wool and scrub it, then reinstall. If this does not work then the limit switch is tripping due to dirty filter, dirty blower wheel, weak blower motor. Aything that restricts airflow will cause the limit switch to trip.
Nov 30, 2012 | Goodman GMS807034ANA Heater
Furnace blower runs continuously but no heat
sounds like the furnace control (low voltage) circuit is open, or in other words you either have a fuse blown or a limit switch that needs to be reset. Most newer furnaces have a small knife like fuse, usually 3 or 5 amp located directly on the circuit board. Limit switches that have a manual reset are usually located in the fire box just above the burner. There may even be a limit switch located on the blower assembly. If you fuse was blown, you may need to find out what caused the short in the circuit or it will do it again. If the limit switch was tripped, you need to turn the furnace back on and watch the flame to see if there is "roll out". It it continues to trip or blow fuses you need to have the unit serviced.
Apr 10, 2011 | Dayton Gas Furnace Heater
Unit not producing heat but fan cuts on and off
Most newer unit the fan comes on if the limit is tripped. The limit is located in the blower section and in the burner section.
Jan 05, 2010 | Heating & Cooling
Carrier 58 Series Furnace Blower Motor Won't Shut Off
Yes. If the high limit is tripped, the furnace will bring on the fan continuously until the limit resets. Often, they will not reset if tripped repeatedly. If the furnace is too large for your application, you probably are not able to move enough air to keep the heat exchanger cool enough.
Oct 03, 2009 | Heating & Cooling
Main limit switch
I am providing some information, but I encourage you to have a furnace technician look at your furnace. The reason is; the limit switch trips when there is a problem that may present a fire or combustion hazard. I've seen these switches go bad, but not very often. Usually they are tripping because the plenum is sooted up and excessive heat builds in the combustion chamber. This is common in older furnaces that have pilot flames- the flame runs all year and soot deposits in the plenum, plugging the air flow through the combustion chamber after years of use.
The limit switch is a safety control switch located on the furnace just below the plenum. If the plenum gets too hot, the limit switch shuts off the burner. It also shuts off the blower when the temperature drops to a certain level after the burner has shut off. If the blower runs continuously, either the blower control on the thermostat has been set to the ON position or the limit control switch needs adjustment. Check the thermostat first. If the blower control has been set to ON, change it to AUTO; if the blower control is already on AUTO, the limit switch needs adjusting.
To adjust the switch, remove the control's cover. Under it is a toothed dial with one side marked LIMIT; don't touch this side. The other side of the control is marked FAN. There are two pointers on the fan side; the blower goes on at the upper pointer setting and turns off at the lower pointer setting. The pointers should be set about 25 degrees apart. Set the upper pointer at about 115 degrees Fahrenheit and the lower one at about 90 degrees Fahrenheit.
Mar 15, 2009 | Heating & Cooling
Goodman GMP125-5 limit switch open
There may be as many as 6 limit switches on the furnace. The first thing to do is turn off the power to the furnace. Look around the burner box. You will see possibly 3 small maybe brown plastic swithes with two wires to each and a button between the wires. Press the button on each one. If it clicks that's the one tripped. There may also be the same kind of switch(s) in the blower compartment. There's a self resetting limit on the middle of the furnace it also has two wires but looks like a black or dark brown plate about 2 1/2 X 3 1/2 inches. You have to check that one with an ohm meter. If any of these switches are tripped there is a reason. Check your filter and overall air flow. with low airflow the furnace may overheat. The switches around the burner box are roll out switches. Watch to see if flames are coming out of the burner area. especially when the blower comes on. DO NOT bypass any of these switches. Call a certified tech. to check it out.
Mar 02, 2009 | Goodman CLJ30AR32 Air Conditioner
Heating & Cooling Logo
29 people viewed this question
Top Heating & Cooling Experts
Paul Carew
Dan Webster
Dan Webster
Tim Whalen