Gas heating system GUH-92A burner shuts off bfore reaching temp. setting
  • 10,045 Answers
Check the thermostat operation.
Posted on Dec 21, 2016
Testimonial: "brand new install,complete sys. When blower starts,gas valve shuts off,on,off sometimes 0sec.,10sec.30sec,60sec. flame sens.good, no change in flame,not a flicker,till valve shut off"
  • Duane Hughes
    Duane Hughes Dec 21, 2016
    Has outside ex. and in. straight up out roof
I install 2 new honeywell non programmable thermostats. The temp never reaches the setting temp. Always 5 to 8 degrees off. I can not get the furnace to heat the home over 70 degrees. Even set at 80. Any...
If the furnace is cycling on and off and not reaching temp there is a problem in the control circuit. If the thermostat is not satisfied the furnace should be running without shutting off in which case the capacity of the furnace is inadequate because of size or problems reducing the capacity. This could be caused by an increase in home size, poor air flow (dirty filter, loose fan belts, fan running slow, obstructions in the duct), dirty heat exchanger or burner, reduced gas flow, over temperature switch bad causing the burner to shut off early, or a few more technical reasons. You may do well to call a technician to troubleshoot this problem.
Feb 09, 2015 | Heating & Cooling
Pilot and burner light then gas shut off model 7900
How many degrees before it reaches desired temp, does it shut off? A thermostat is designed to shut the furnace off a couple/ few degrees before it reaches set temp. It has what is called a heat anticipater, which shuts the burner down, and lets the blower use the remaining heat from the heat exchanger to bring it up to desired temp making it more efficient. If it is more than a few degrees, replace the thermostat. You can jump out the red and white wires to confirm the faulty thermostat. If by doing this, the furnace never shuts down, until you separate the red and white wires. That confirms a faulty thermostat. Hope this helps someone.
Oct 06, 2014 | Coleman Propane Forced Air Heater...
Carrier gas furnace does not cycle right.
Check out the flame sensor see if it is clean and check the connections .
May 21, 2017 | Carrier Heating & Cooling
Jandy LX250-L Burner shuts down and no errors
It is more likely the board on the LX.
If you have a volt meter check the IND connection on the Fenwal for 24volts while running and keep your meter on it until it shuts down. If the power is still present at the IND while shutting down then it would appear to be a Fenwal problem. It sounds like the temp circuit on the board or the temp sensor it self is bad. Try dipping the temp sensor in a glass of water with a confirmed temp to see if it is accurate.
Apr 03, 2017 | Pool & Spa
Furnace cuts off before reaching set temp.
You can make sure it is not the thermostat by crossing or jumping the R and W terminals (or associated wires) together. This will keep the furnace calling for heat. As it is approaching set temperature, get in front of the furnace and inspect the air filter to make sure it is clean, watch the control module for any error codes that may be turning off the system prematurely.
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
Mar 07, 2010 | Honeywell Programmable Thermostat Heater
Burner clicking on and off rapidly when reaching restart temp.
the gas orifices may be plugged try to poke them out with a fine wire . shyt off power and gas before cleaning as you don't want to be burned
Dec 13, 2009 | Heating & Cooling
Viking oven only one burner will light
Go to this web site. It has a manual on Viking ovens.
Usually, when the set temp is reached, the flame will cycle down to what is called "Minimum Blaze". This is to put heat into the unit at the rate that it leaves the unit. It helps to hold temp rather than cycle off and on. It cycles high when temp goes below set and then cycles down when set temp is reached.
Jul 09, 2009 | Refrigerators
Heating & Cooling Logo
32 people viewed this question
Top Heating & Cooling Experts
Paul Carew
Dan Webster
Dan Webster