New install GUH 92A burner shuts off before temp. setting is reached Gas valve shuts off then back on
This is upflow furnace
  • 946 Answers
Have you cleaned the flame sensor? don
Posted on Dec 23, 2016
Testimonial: "flame, rollout,air in out filter all good"
  • 2 more comments
  • don-ohio Dec 24, 2016
    This can also be a bad limit switch,cutting off and then resetting. Make sure your air filter is not dirty or restricted in the return air plenum.This will cause too hot air and trip the limit. don-ohio
  • don-ohio Jan 10, 2017
    Check gas pressure to gas valve. May be too high. don-ohio
  • Duane Hughes
    Duane Hughes Jan 11, 2017
    turned out to be breaker at load Center
  • don-ohio Jan 11, 2017
    Thanks for posting back on the solution,Duane! don (:^)
I install 2 new honeywell non programmable thermostats. The temp never reaches the setting temp. Always 5 to 8 degrees off. I can not get the furnace to heat the home over 70 degrees. Even set at 80. Any...
If the furnace is cycling on and off and not reaching temp there is a problem in the control circuit. If the thermostat is not satisfied the furnace should be running without shutting off in which case the capacity of the furnace is inadequate because of size or problems reducing the capacity. This could be caused by an increase in home size, poor air flow (dirty filter, loose fan belts, fan running slow, obstructions in the duct), dirty heat exchanger or burner, reduced gas flow, over temperature switch bad causing the burner to shut off early, or a few more technical reasons. You may do well to call a technician to troubleshoot this problem.
Feb 09, 2015 | Heating & Cooling
Pilot and burner light then gas shut off model 7900
How many degrees before it reaches desired temp, does it shut off? A thermostat is designed to shut the furnace off a couple/ few degrees before it reaches set temp. It has what is called a heat anticipater, which shuts the burner down, and lets the blower use the remaining heat from the heat exchanger to bring it up to desired temp making it more efficient. If it is more than a few degrees, replace the thermostat. You can jump out the red and white wires to confirm the faulty thermostat. If by doing this, the furnace never shuts down, until you separate the red and white wires. That confirms a faulty thermostat. Hope this helps someone.
Oct 06, 2014 | Coleman Propane Forced Air Heater...
Is it normal for my furnace to have burner cycle once or twice
That sounds normal. When the bonnet reaches a preset temperature the burner turns off then when it cools down a bit the burner turns back on. Clean filters etc will help to keep the burner on longer in a cycle.
Aug 24, 2014 | Heating & Cooling
I have an early 80's mobile home with an "intertherm gas atmospheric furnace" pilot light is lit but can't get the furnace to "fire". Seems as though the limit control is stuck open. ...
If your pilot light is lit then I would first check your thermostat. Make sure it is on heat setting and fan is on auto, turn stat up to where it should be calling for heat. If you don't get burner to light remove front cover from thermostat and see if it has a mercury switch, if it does move temperature selector up and down and see if you can see a spark in mercury switch vial. If y ou cannot see a spark remove screws that attach t-stat to base.Remove carefully and disconnect wires that go to r and w terminals on stat base. Temporarily connect these two wires together. This should make burner light if you have power to thermostat. If burner does light disconnect wires and replace thermostat. Also if you have a volt meter check across these two wires and see if you have power there. Should be around 24 volts a.c. If your thermostat has a fan on setting try that. If fan runs you know you have power to furnace The gas valve needs 24 volts to operate and inside the electric control box in furnace there is a transformer to step down 110-120 supply voltage to 24 volts. If transformer is working you should be able to hear a low buzz or humming sound. You can also check across gas valve terminals when t-stat is set for heat, you should read about 24 volts. If you have 24 volts to gas valve and it is not opening then you need to replace gas valve. The main purpose of the limit switches is to turn blower on when temperature in heat exchanger reaches fan on temp,shut off blower after burner shuts off and heat in heat exchanger reaches fan off temperature, and limit if temperature exceedes set point without blower coming on. I hope this helps you. Thanks
Nov 25, 2010 | Heating & Cooling
Furnace fires up and heats to desired heat setting and burner shuts down , but the main blower continues to run on.
its the fan control AFC not shutting off , it comes on at temp rise say 150f drops back to 130f with fan on , burner shuts off fan runs untill temp falls to 100f the fan shuts off in this case it keeps running
Nov 13, 2010 | Dayton Gas Furnace Heater
Furnace cuts off before reaching set temp.
You can make sure it is not the thermostat by crossing or jumping the R and W terminals (or associated wires) together. This will keep the furnace calling for heat. As it is approaching set temperature, get in front of the furnace and inspect the air filter to make sure it is clean, watch the control module for any error codes that may be turning off the system prematurely.
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
Mar 07, 2010 | Honeywell Programmable Thermostat Heater
Blower and ignitor work and then kick off but will work again after shutting furnace off for a while and turning it back on. This problem seems to occur when it is colder outside rather than above 30...
I had the identical problem with my York. Problem was the burners. The heating element would light the first burner but the flame wouldn't move to the other burners. The flame sensor didn't detect a flame on the last burner so the gas valve would shut off. I removed and cleaned the burners then reversed the first and last.
Dec 05, 2009 | York Furnace Draft Inducer Blower Fasco #...
Goodman Furnace flame still burns at the rod when heat cycle done
Your gas valve is leaking and must be replaced. They are not serviceable. When it is replaced the gas pressure should be adjusted with the use of a manometer. The turbulence may be caused by the gas valve or the burner may be dirty. If the burners are dirty the should be removed and blown out or rinsed out - if you rinse them be sure to shake all the water out!
Please rate my answer!
Mar 25, 2009 | Dayton Gas Furnace Heater
Heating & Cooling Logo
69 people viewed this question
Top Heating & Cooling Experts
Paul Carew
Dan Webster
Dan Webster
Tim Whalen