When the heater is on the outside ac unit runs I've temporarily turned off 220 breaker low voltage pull in switch still energized how does the furnace control board fault occur
  • Heating & Co... Master
  • 1,799 Answers
Are you sure this is not a heat pump. The outdide unit is supposed to run with a heat pump. If its blowing cool air its likely in defrost mode, this has to happen, though you probably have heat strips inside, possibly not wired right.
Posted on Dec 18, 2016
How do I get my AC running again? Ruud UBHC AC unit isn't running. Started yesterday or today.
Sounds like there is no control voltage. Either the transformer to reduce the voltage from 110 volts to 24 volts is not producing the 24 volts needed for control voltage, or most furnaces have a small 3 or 5 amp fuse mounted on the main control circuit board that may be blown. Other "outside circumstances" may involve a break in the thermostat wire...more than likely the red wire if you are getting nothing to work. I have seen evidence of "critters" that have chewed through the low voltage thermostat wiring that would keep the thermostat from controlling anything. To check this, go to the furnace and jumper the red & green wire to get the fan running just to isolate if it is a thermostat wiring severred. Good Luck.
Dec 11, 2014 | Ruud UBHC Air Conditioner
Tip
Heater check out list for heater failures
Almost all furnaces built after 1978 have intermittant type pilots.
Ca banned them requiring electronic spark or hot surface ignitors, followed by induced draft motors, pressure switches or centrifigal switches that "prove" a induced draft exists, allowing the pilot sequence to commence.
electronic spark type units have a high voltage low amperage spark that is AC. Fire rectifies electricity that passes through it meaning AC becomes DC ! Fire is a terrible conducter however as a result , the DC signal is only milliamps/volts signal strength. the DC prescence is proof a flame exists for pilot, and safe to commence to mainburners.
As long as pressure switches stay closed, safeties and limits stay closed
and the DC signal to the ignition module is not broken, the furnace will run.
The normal sequence of operation is upon a call for heat from the thermostat a 24 volt signal is sent to W white (heat circuit) at the low voltage terminal board on furnace.
from there depending on unit and age the heat circuit may include a circuit board, but it still has the typical limits and safetys reqired for operation
its just not using electromechanical relays to control fan and induced draft motor etc.
for the induced draft to begin ,all limits, safetys in heat circuit must be closed.
induced draft begins and a proving switch, either pressure or centrifigal close allowung the pilot to begin, a spark or hot surface ignitor is energized and a pilot flame established,modern types use flame rectification to prove a flame, older Carrier, Payne,types have a 3 wire switch in the piloyt assembly that is a bi metal that expands and contracts clicking open and shut, allowing pilot or main burners, depending if cold or hot.
pressure switches are attached with tubing to the induced draft wheel housing and sense pressure differential and close upon induced draft running, the orifices that the tube attaches to on induced draft housing often plugs or is restricted causing pressure switch to fail to close, or waver on open and close , open , close, .
if you can run the fan in the on postion , you have both high and low voltage to the furnace.
if you dont have fan control check power, breaker , fuses.
on Dec 04, 2009 | Heating & Cooling
Brand new furnace wont start its a aruf 14 electric air handler with a 10 amp heater coil
the 3 amp fuse protects low voltage side of transformer. if it's blowing on a call for cooling wire pair going to outside unit bad or contactor in outside unit.
Nov 18, 2013 | Goodman Heating & Cooling
Model 363616ba There is no control voltage going to the outside unit. Outside unit will not energize. What is the routing for control voltage? Do you have a schematic with details of the control...
The control voltage comes straight from the furnace or thermostat. Its 2 to 5 wires depending on if you have a heat pump or conventional system. If you have a control board on the inside of the furnace that has the terminal (y), then your control voltage will come from that terminal and the common terminal. Sometimes they have it connected to the (y) terminal from the thermostat, but will usually still be hooked up inside or right by the furnace. In (COOL) mode, the thermostat energizes the y and g terminals, (cooling and fan), which is sent to the outside unit on the contactor. You need 24v going to the contactor outside for it to pull in and make contact. If you have lost the low voltage, then it usually means bad transformer on the furnace (which nothing would work), faulty control board on furnace, faulty thermostat, or your low voltage wires could of been cut, chewed through, etc. If you do have the low voltage by chance, then it could be a faulty contactor on the condensing unit. I'm just throwing some things out there, its kind of difficult without knowing all the equipment you have. Have anymore questions, just ask. Good luck!
Jun 12, 2011 | Goodman Heating & Cooling
Model # ckl49-il serial # 0506126514. This unit stopped working yesterday, noticed the fan on the outside compressor wan't turning, how do i test the capacitor and fan to see which one to replace?
By far the most common problem with air conditions is the relay (known as a "contactor") by the air conditioner industry. This allows a low voltage (24 volts) electromagnet to turn on the 220 volt motor for fan and compressor. A replacement will generally cost about 50 to 75 dollars on Amazon.com.
Look for the wires entering the unit, The pair of wires entering the unit will go into a small (4" x 2" x 2") unit (the contactor). Another pair small diameter wires will go into the contactor (those are from the thermostat (or control panel of your furnace blower) and control the electromagnet switch.
The pair of output wires exit the unit and go to the compressor motor and fan.
You can check the output power by
1) Turning off the circuit breaker to the A/C
2) Unplugging the switch (must be a second switch within 3 feet of the A/C) near the house
3) opening up the outside panel on the A/C
4) Set voltage meter probes on the two output wires on the Contactor (make sure voltage meter is set to 220 volt AC range or higher)
5) turn on the outdoor switch
6) turn on the circuit breaker (if no body is near the unit and you can see the voltage meter without touching it)
7 check voltage meter to see that is says 220 volts AC
If not, then the contactor is bad and needs to be replaced.
A professional can usually do it for $200 including service call. I highly recommend calling a professional if you feel uncomfortable in any way about working with 220 volt systems. This voltage will kill you if you make a mistake!
-Mark
May 28, 2011 | Goodman CKL49AR49 Air Conditioner
Compressor on Ruud Unit UAMA-042JAZ and its fan won't run. Electric comany said low voltage circuitboard problem. Suggested replacing the fuse on the circuitboard. I could not find a fuse, where...
The units has what you call a contactor which is actually a relay but it does not look like a relay. You can get a none conducting material to depress it. and the compressor should run and the fan. Be very careful since that contactor has exposed parts and it has 220 volts running through it. That contactor coils is energized by low voltage current usually around 12 to 24 volts and it is supplied by a small transformer near the evaporator in the attic. There is a contact and when the contactor is energized magnetic field pulls it in so the contact on the 220 volts touches and the AC unit runs. Another word of caution, do not turn the unit manually one after another. this may damaged the compressor. Wait a few minutes each time you manually push the contactor to see the problem. Good luck.
May 28, 2011 | Ruud UBHC Air Conditioner
My miller ac outside unit will not come on unit is only 2 years old. I checked breakers and capacitor I have voltage to outside unit? any recommendations?
If you were able to check the voltage, did you check to see if you had 24volts at the contactor? Did you
have 220 volts coming into the contactor? If no to the
first question and yes to the 2nd question, take a
insulated screwdriver and push the contactor in, the
unit will run. You have a low voltage problem.
2nd, do not reference the 220 volts to ground, if you
dont have 220volts feeding into the contactor,
example read voltage between L1 and L2.
Jun 14, 2010 | Heating & Cooling
As I was cutting weeds away from my outdoor ac unit, I accidentaly cut through a small wire that has a red and white inside of it, we wired them back together and still have no ac or heat or air, we just...
first try turning off the power to the furace for 15 sec and tunr it back on (reset the computer) you may have blown a control fuse on the contol board inside the furnace, turn off power and becareful of hazardous voltage conditions
Aug 15, 2009 | Intertherm P3RA-048K Air Conditioner
Unit not coming on. air isn't getting cold
First check the breakers for the condensing unit (outside unit) and the disconect outside by the unit (could be a breaker ,a pull off/on switch or fuses)If its ok , you should have 220 ,240 volts to the unit contactor (you'll see it after removing the cover on the condensing unit).When the termostat is in the cold position and the temperature its set is lower than the one inside the house the contactor should be pulled in and give power to the compresor and the fan.But if the termostat is in the cooldest set and the blower inside the house works and the contactor in the condensing unit is not pull in the problem is in the termostat or in the low voltage wire.
Apr 24, 2009 | Heating & Cooling
3 amp fuse blows on a carrier 58mcb furnace board
Hi!!! Does your ac unit work fine?If not check your low voltage problem..You have a low voltage problem check the wire going out to your condensor make sure that they are not touching..Good luck..Check low voltage wires..short in progress..
Jan 04, 2009 | Carrier 52CQ-312-4 Comfort Series Heat...
Heating & Cooling Logo
Top Heating & Cooling Experts
Paul Carew
Dan Webster
Dan Webster
Tim Whalen