I have volt230 at board but not when i plug in to contactor
  • Thomas Woodburn
    Thomas Woodburn Dec 24, 2016
    You can find a service manual i believe on manualslib.com. This gives detailed trouble shooting on electrical problems. What i saw, unlike airconditioners, is all your safety switches are high voltage. This means that you likely have 230 leaving the board its just not making it to the contactor because one of your safety switches is tripped. (Pressure/thermal etc.) You can bypass every switch in the circuit to pin point which one it is but dont recommend using machine until the problem is fixed. Test continuity through all switches or find where the voltage stops. Good luck
  • Heating & Co... Master
  • 1,873 Answers
You have to narrow further. 230 in to board, 230 out of board with no contactor, 230 to the contactor with no load, 230 thru contactor with a load. Likely the board, not sure what you are using the contactor for. If its a heater than you possibly have a bad limit switch or bad element.
Posted on Dec 17, 2016
Testimonial: "Barrel contractor on Taylor 706 ice cream mach"
Indoor unit powers up indoor fan runs, has call for cooling outdoor unit will not run, has coms issue
Good. When it calls for cooling the wire conncets to a contactor in the outdoor.
Unscres the center of contactor and then check the contactor by pressing thr' ur screw driver maually. Just only for 5 seconds.
If it works, the contactor coil is defective.replace contactor
Feb 03, 2014 | Midea Heating & Cooling
Reset the contactor relay
the contactor does not have a reset button 24 volts will energize a magnet and pull the contactor in you can also manually push in the contactor for testing purposes the airhandler has the transformer which produces 24 volts this power then goes to the tstat then you select a mode which then goes to the contactor you most likely have a blown fuse on the circuit board or simular problem the contactor could have shorted causing this
Jun 27, 2012 | Goodman Heating & Cooling
Butters
Based on your description there should be 2 contactors. One is the contactor that controls power to the welder primary winding, this one should be quite large compared to the other one, the other controls the 24 volt (most common) supply to the wire feed speed control board and gas solenoid. If you do have 2 of these contactors, the 24 volt contactor may supply the control current to the larger contactor..
If blowing out the cabinet has not helped, and at this point it is not likely, the 24 volt contactor should be replaced. If a sealed one is available I would upgrade to that style. The ratings should be embossed on the contactor somewhere, otherwise your control voltage should be 24 volts, use a meter just make sure you are in that range, US, UK and Euro standard share some common specs. You may have a 2 pole or 3 pole type- it depends if the gas solenoid is powered off the same pole as the motor control board, or if it is powered by it's own pole. These would be the "N/O" contacts, and all would have current supplied by the 24 volt supply/control supply. The larger contact coil winding would be on it's own pole. Contacts should be rated at 15 Amps minimum
Replacing both contactors at the same time if so equipped is a cost effective bit of maintanence.
If you have only the single 24 volt contactor, the tip will be live at all times and it will only be the gas and the wire feed control board that would be switched by the contactor.
Again, based on description, I would replace the 24 volt contactor. Contacts should be rated at 15 Amps minimum
I would also just check the gas solenoid with a jumper wire to make sure it opened and closed as it should.
Feb 21, 2012 | Welding Tools
Shorted out contactor on a bryant air conditioner. Will the circuit board burn out from this?
Usually not if there is a fuse on the low voltage side of the board...if there is no fuse then often the board and the transformer are toast...
Check for 24v coming out of the transformer and then test the board by unhooking the leads to the contactor and then checking for 24v going to the contactor leads without them hooked to anything...
heatman101
Jul 14, 2011 | Heating & Cooling
Tempstar air handler model #nfcp2400c2 with 5kw heat strip someone has installed a contactor on inside and taken the control board out is there anyway to bypass board to use as a straight cooling only...
Yes, you need a tstat, a contactor, and a transformer.
Contactor runs the fan, transformer sends the low voltage to the tstat. Tstat turns on contactor for fan and compressor for cooling
May 17, 2011 | ICP Vortex Fan Timer Control Board For Air...
Ruud heat pump outside unit not starting. Open and found contactor disengaged even though I have system on from inside. Low voltage wires come out of a circuit board checked for 24v, none. Then bypassed...
If you are getting the low voltage to the relay and it is not closing, then the relay may be either bad or stuck. Disconnect the 220v and see if the contacts can be manually closed. I always use a piece of wood or something non-conductive. If the contacts will close manually, try re--energizing the circuit to see if the relay will now close on its own. If not, you are probably looking at having to replace the relay switch. I had to replace mine last year. As always, be extremely careful working around electrical boxes and capacitors.
Jul 04, 2009 | Heating & Cooling
The contactor well not pull in.
Also if it where the circuit board that had gone bad. Your furnace would not turn on at all not even the blower motor. You can test them both by looking for 24 volts to the board, and 120 volts per leg of the contactor
May 23, 2009 | Weather King 10AJA3001AH Air Conditioner
Goodman CPB 42 Heat/air packaged unit
did you turn off the air handler when you changed the contactor could have shorted and blown a fuse on the control board. did you get a 24v coil on your contactor. do you have 24v at the contactor when unit is calling. check your wire connections
Jan 31, 2009 | Heating & Cooling
Ice Maker
this could be a result of a stuck switch, bad switch, or swaped wires. or if a contactor is used in the wire ing a bad contactor
Jan 21, 2009 | Frigidaire FRS26R4A Side by Side...
Heating & Cooling Logo
41 people viewed this question
Top Heating & Cooling Experts
Paul Carew
Dan Webster
Dan Webster
Tim Whalen