Question about Panasonic Heating & Cooling
Hi there, I have a H23 fault code up on my CS-E24PKR Panasonic inverter AC. Could you please advise what to check relating to the Indoor heat exchanger temperature sensor?
    Scholar:
    New Friend:
  • 148 Answers
The system has already determined that the thermistor is faulty so I wouldn't bother checking it as they are cheap and easy to obtain. The thermistor in question is one of two located at the right hand side of the indoor heat exchanger (the metal radiator-like assembly). One is the air temperature sensor and the other is the pipe/heat exchanger sensor. The air temp. thermistor is the one just in front of the heat exchanger held by a plastic clip. The pipe/heat exchanger sensor is the one that sits in a small metal tube near the copper pipes leading to the heat exchanger. It is usually a fairly tight fit because of a small metal insert to keep it in place. Use some small needle nose pliers on the metal insert to pull the thermistor out - NOT THE WIRES! Of course, make sure power to the A/C is completely off first.
You will probably have to replace both of the thermistors as they usually have the wires going to the same single plug on the controller board.
Posted on Apr 28, 2017
SOURCE: panasonic cs-pw9gke i need wiring diagram
Split A/C-Cold:
You need four wires(two #10 and two #12) to the outdoor unit, leaving you house, and three wires(#10) coming from the breaker to tye indoor unit inside your house.
Split A/C-Cold and Hot:
You need five wires(two #10 and three #12) to the outdoor unit, leaving your house, and thee wires(#10) coming from the breaker to your indoor unit inside your house.
This ypical arrangment(all of them use three wires fro the breaker), yet there are other units which may require 6-7 wires connected to the the outdoor unit depends on the added features to the unit.
Regards,
Gulftecheng
Posted on May 02, 2009
Therinnaiguy
  • 1420 Answers
SOURCE: How do I change the battery in the remote control
slide the cover of the remote up higher. It is hiding the batteries.
Posted on Nov 26, 2009
  • 534 Answers
SOURCE: Panasonic CS/CU-A242KR Air conditioner leaking water
OK lets see what we can help you with here. The condensate drain is clogged. There are a couple of ways to clear this clog so lets give it a try. If you know where the drain for the a/c is located outside (usually by the outside condenser unit) it will be a pipe that is just sticking out of the side of the house, if you find it take a wet/dry vac and place it on this pipe and turn the vacuum on and make a seal with your hand this should unclog the drain. If you don't find this pipe outside the house then go to the furnace and you will see at the bottom of the furnace a pipe (PVC) white, this is the drain for the unit inside. Take the wet/dry vac and have it at the ready in the event the clog is further down the line than at the furnace itself now the fittings on this pipe should not be glued together due to the ability to access for this very purpose. Take the pipe apart at one of the fittings and place the wet/dry vac on the end of the pipe towards the furnace and using your hand make a seal and evacuate the line. Do this to both sides since you don't know where the blockage is. If you are unable to separate the pipe at any fitting you will need to cut the pipe and at the spot of the cut you will need to repair it with a sleeve. Remember that the drain pipe is plastic and is made of pvc so you can get a repair coupling from any home improvement store for this repair.
Hope this helped you some
Dave
Posted on Feb 21, 2010
  • 9 Answers
SOURCE: Hi I have 1.5 ton samsung split AC. the problem is...
the water comes from the coil, start there make sure there is no obstruction coming out to your condensate line and make sure its properly pitched.
Posted on May 22, 2010
hvac1960
  • 2133 Answers
SOURCE: i have a panasonic cs e12 ckp. timer light flashes
Press on/off button continuously for 5 seconds.Helpful?
Posted on Jan 16, 2011
How do I get the fault codes up on a Panasonic split air conditioning system CUE24FKR
14.2.2 To Make a Diagnosis1 Timer LED starts to blink and the unit automatically stops the operation.
2 Press the CHECK button on the remote control continuously for 5 seconds.
3 "- -" will be displayed on the remote control display.
Note: Display only for "- -" (No signal transmission, no receiving sound and no Power LED blinking)
4 Press the TIMER ? or ? button on the remote control. The code "H00" (no abnormality) will be displayed
and signal will be transmit to the main unit.
5 Each press of the button (? or ?) will increase error code
number and transmit error code signal to the main unit.
6 When the latest abnormality code on the main unit and
code transmitted from the remote control are matched,
Power LED will light up for 30 seconds and a "beep" sound
(continuously for 4 seconds) will be heard. If no codes are
matched, Power LED will light up for 0.5 seconds and no
sound will be heard.
7 The breakdown diagnosis mode will be canceled unless
pressing the CHECK button continuously for 5 seconds or
operating the unit for 30 seconds.
8 The LED will be off if the unit is turned off or the RESET
button on the main unit is pressed.
Diagnosis
display Abnormality / Protection control Abnormality
Judgement Emergency operation Primary location to verify H00 No abnormality detected - Normal operation H11 Indoor / Outdoor abnormal communica
tion > 1 min after starting
operation Indoor fan operation
only • Internal / external cable connections
• Indoor / Outdoor PCB H14 Indoor intake air temperature sensor
abnormality Continue for 5 sec. - • Intake air temperature sensor (detec
tive or disconnected) H15 Outdoor compressor temperature sensor
abnormality Continue for 5 sec. - • Compressor temperature sensor
(detective or disconnected) H16 Outdoor Current Transformer open cir
cuit - - • Outdoor PCB
• IPM (Power transistor) module H19 Indoor fan motor mechanism locked 7 times occurance
continuously - • Indoor PCB
• Fan motor H23 Indoor heat exchanger temperature sen
sor abnormality Continue for 5 sec. O
(Cooling only) • Heat exchanger temperature sensor
(detective or disconnected) H24 Indoor heat exchanger temperature sen
sor 2 abnormality Continue for 5 sec. - • Heat exchanger temperature sensor
(detective or disconnected) H27 Outdoor intake air temperature sensor
abnormality Continue for 5 sec. O • Outdoor temperature sensor (detec
tive or disconnected) H28 Outdoor heat exchanger temperature
sensor abnormality Continue for 5 sec. O • Outdoor heat exchanger temperature
sensor (detective or disconnected) H30 Outdoor discharge air temperature sen
sor abnormality Continue for 5 sec. - • Outdoor temperature sensor (detec
tive or disconnected) H33 Indoor / Outdoor wrong connection - - • Indoor / Outdoor supply voltage H38 Indoor / Outdoor mismatch (brand code) H50 Ventilation motor abnormality 7 times occurance
• Ventilation motor H51 Nozzle lock abnormality 2 times occurance
continuously - • Nozzle H52 Limit switch abnormality - - • Indoor PCB H97 Outdoor fan motor mechanism locked 2 times occurance
within 30 minutes - • Indoor PCB
• Fan motor H98 Indoor high pressure protection - - • Air filter dirty
• Air circulation short circuit H99 Indoor heat exchanger anti-freezing pro
tection - - • Insufficient refrigerant
• Air filter dirty F11 Cooling / Heating cycle changeover
abnormality 4 times occurance
within 30 minutes - • 4-way valve
• V-coil F90 PFC control 4 times occurance
within 10 minutes - • Voltage at PFC F91 Refrigerantion cycle abnormality 2 times occurance
within 20 minutes - • No refrigerant
(3-way valve is closed) F93 Compressor rotation failure 4 times occurance
within 20 minutes - • Compressor F95 Cool high pressure protection 4 times occurance
within 20 minutes - • Outdoor refrigerant circuit F96 IPM (power transistor) overheating pro
within 30 minutes - • Excess refrigerant
• Improper heat radiation
• IPM (Power transistor) F97 Outdoor compressor overheating protec
within 10 minutes - • Insufficient refrigerant
• Compressor F98 Total running current protection 3 times occurance
within 20 minutes - • Excess refrigerant
• Improper heat radiation F99 Outdoor Direct Current (DC) peak detec
tion 7 times occurance
continuously - • Outdoor PCB
• Compressor
Note:
"O" - Frequency measured and fan speed fixed.
The memory data of error code is erased when the power supply is cut off, or press the Auto Switch until "beep" sound heard following by pressing the "CHECK" button at remote controller.
Although operation forced to stop when abnormality detected, emergency operation is possible for certain errors (refer to Error Codes Table) by using remote controller or Auto Switch at indoor unit. However, the remote controller signal receiving sound is changed from one "beep" to four "beep" sounds.
Oct 13, 2017 | Panasonic Heating & Cooling
PANASONIC CS-CU E24PKR fault code H00
You may have a problem with the outdoor controller, the indoor controller or both. Power outages can do some strange things to the electronics. Turn the A/C isolator off for five minutes and back on again to be sure the problem is still there. You could also try this:
• To clear memorized error (Protective operation) status
after repair:
1. Turn power on.
2. Press the AUTO button for 5 seconds (A beep
receiving sound) on the main unit to operate the unit
at Forced Cooling Operation mode.
3. Press the CHECK button on the remote controller for
about 1 second with a pointed object to transmit
signal to main unit. A beep sound is heard from main
unit and the data is cleared.
Jan 31, 2015 | Panasonic Heating & Cooling
Panasonic fault codes
H14 = Indoor intake air temperature sensor abnormality.
Replace the indoor air thermistor.
Jul 12, 2014 | Panasonic Heating & Cooling
We have 2.0 HP inverter wall mounted LG aircon, when we turn on the ac, the indoor unit only is running and shut down after 3 mins. What is the solution?
Hi Marie, does the green indicator light on the front panel flash after it shuts down? If it does...count how many times it flashes this will refer to a fault code diagnostic.
Keith.
Jan 02, 2014 | LG LS-K2430HL Heat Cool Mini Split Air...
Panasonic CS-A12DKD Air conditioner does not
This could be an inoperative reversing valve or bad reversing valve solenoid coil.
Oct 31, 2013 | Panasonic Heating & Cooling
H23 fault code
Diagnosis display = H23
Abnormality / Protection control = Indoor heat exchanger temperature sensor abnormality
Abnormality Judgement =
Emergency operation = O (Cooling only}
Primary location to verify = • Heat exchanger temperature sensor (detective or disconnected)
This is from the following link:
http://errorcodeairconditioning.blogspot.com/2010/10/panasonic-error-code.html
May 05, 2012 | Panasonic Heating & Cooling
Hi i have a panasonic cs28 cassett units both have F27 01 fault codes. have checked power at indoor and outdoor units can i do anything else
f27- indoor outdoor unit disconnected.
Check power in output of indoor and input of outdoor, if power variation, replace wire.
Normally in this fault code, one of the wire burnt or rat bitten.
Dec 27, 2010 | Heating & Cooling
Panasonic air conditioner CS-E24GKR...The unit stops and the timer indicator blinks. Also displays error code H 11...Help...Please...its hot in here
H-11Indoor / outdoor abnormal communication. Check • Internal / external cable connections
Jan 04, 2010 | Panasonic CS-A12C Air Conditioner
Remote doesn't work on air con
Should be current detect pcb faulty, or compressor drawing too much current.
I don't have your model a/c, but panasonic fault codes stay pretty much the same
Normally panasonics have this info on the inside of the access panel.
Plus fault codes from the indoor unit make it easier to look up.
if the compressor is running, check the amps and refrig pressures.
Sep 19, 2009 | Heating & Cooling
Heating & Cooling Logo
140 people viewed this question
Top Panasonic Heating & Cooling Experts
Bill Long
Fotis Papastamatiou
Dennis Boxerman
Are you a Panasonic Heating and Cooling Expert? Answer questions, earn points and help others