Arcoaire unit, the air set on auto, after the heat goes off cool down fan will not shut off, when I turn the unit off it will not shut off!
  • Heating & Co... Master
  • 1,862 Answers
You either have a bad fan relay or a bad tstat. Remove the t stat from the wall (as long as its not mercury), just the cover plate and see if the fan shuts off. If so, bad t stat. If not, bad relay
Posted on Dec 16, 2016
2 Suggested Answers
meBNme
  • 334 Answers
SOURCE: arcoair central heat /air conditioning unit
The blower motor kicks on when there has been a 24 volt control failure.
This usually means that a limit switch has tripped.
Most likely that would be a high temp limit switch or a rollout switch.
First, make sure the filters are clean. and the evap coil is clean. If eaither are dirty/clogged, it will partially block airflow, causing the furnace to overheat, causing the high temp limit to trip.
A rollout switch typically trips for three reasons.
1 flame rollout into the burner compartment due to poor airflow.
2 overheating af teh metal plate the rollout is mounted to, due to dirty, old, rusted components.
3 a bad limit switch.
If your unit has an LED light, count the flashes and it will hepl popint out the problem.
(locate the wiring diagram/flash code list, and correspond the flash count, with the code.)
First, check filters.
Posted on Jan 14, 2009
Have installed a new Honeywell thermostat. The fan does not turn off even when the room has reached the desired temperature. I originally replaced th ethermostat because the old one the fan ran forever and...
Most T-Stats have a On / Auto on a forced air system. On means the fan will run all the time even if it is not calling for heat. Auto only runs when calling for heat. Does the fan turn off in the auto mode at all? To test it...BE SURE THE FAN IS IN THE AUTO MODE ON THE T-STAT... Turn the thermostat all the way down and keep it there for appox 15 mins. If it is wired properly and the fan limit is set properly the fan should turn off. If it doesn't it is not the thermostat were the problem lies.
Most forced air units have a fan / high limit switch. There is a setting on the switch for the fan to turn on and a setting for the fan to turn off or it has a setting and a differental switch for it to turn off/on. Example - the fan comes on when the temp in the heat exchanger reaches 110 degrees F and will shut down at 95 degrees F after the thermostat is satified...this would hav a differental of 15 degrees F. It may be set to low and the fan continues to run long after all of the heat has been removed from the heat exchanger. This in turn will cause cool air to be coming out of the registers.
Mar 09, 2011 | Honeywell CT87B ROUND HEATING&COOLING...
The fan has auto ond on selections, the heat looks to be running fine but the fan will NOT shut off.
The thermostat needs to be set for AUTO. If you have it on auto and the fan still goes even though the heater is off then you probably have a stuck fan limit. The limit has a long probe which goes n the plenum. As the heat builds in the plenum at the start-up of a warming operation the bi-metal inside that probe slowly twists around till the temp inside is 110 degrees, the fan comes on and we have warm air in the vents. Then when we have a cozy house the heat shuts down. The fan keeps a going till the heater cools down and the bi-meta twists back around and shuts down the fan. So what goes wrong? The bi-metal simply gets hung up in that position. Tapping on the dial will sometimes release it but it will keep occurring and become aggravating. themobilian_306.jpg
These limits come in various sizes and brands but this is the most common one. If your machine is a newer model then that control board has a fried or stuck relay on it.
Nov 28, 2010 | Heating & Cooling
The fan will not turn off when the cooling unit or heating unit shut off
Your thermostat should be set to auto your fan is most likely in the on postition
May 19, 2010 | Heating & Cooling
Lg heat runs all the time
It sounds like you have the fan turned on. If you go to the stat, you should see an auto button, or switch for the fan. If you just switch it to auto, the fan will stop, and only start when the unit calls for it, hope that helps
Feb 15, 2009 | LG Heat cool Window Air Conditioner
Arcoair central heat /air conditioning unit
Jan 14, 2009 | Heating & Cooling
Vornado heater doesn't work on high setting but only at low setting
Dust on the inside of the unit can cause the overload switch to shut many vornados down. Blowing the dust out of the unit with compressed air or a blower may help.
Another problem that causes vornados to stop working (light on - no heat no fan) is when one of the bearings starts to go bad in the unit. This causes the fan to be slower and less effective and the unit’s inability to move the heat away from the thermal overload switch again causes it to shut down.
Though you could remove the front and rear bearings and try to get replacements if it's even replaceable ... Once the bearing starts to go bad there is little that can be done ... HOWEVER, here is one solution to get more life out of the unit.
First, use a blower to blow all the dust out of the unit.
Then, because it is typically the front bearing that goes bad first, lay the vornado on it’s back (so the unit would be blowing air up toward the ceiling), this will relieve the front bearing somewhat and rely more on the rear bearing which tends to last longer.
The vornados I’ve had are all thermistor units ... that is, they don’t just turn on and off when the set temp is reached but in fact slow themselves down (both heat and fan) to keep some level of air circulation in the room. This is a good thing by the way.
There are usually two toggle switches .... one is a heat switch - usually Low & High .... the other is the thermistor switch (this sometimes is labeled “fan”) - usually Auto & High.
Once the unit is on its back ... Now, change the settings as follows:
Turn the Heat switch to LOW
Turn the Fan switch to HIGH
Turn the dial (with the temperature in degrees on it) to the lowest setting - which is somewhere around 60’ish.
Now turn the unit on and it should stay working.
Three things that could cause it to turn back off ...
You turn the Fan switch back to Auto.
You turn the Heat switch back to High
You turn the temperature selection dial too high ... though, you can cautiously turn the dial up a few degrees at a time ... the unit will start shutting down again when you set the temp too high ... then just dial it back down ... unplug for a couple minutes, then turn back on.
Oct 22, 2008 | Vornado EH1-0014-01 Compact Heater
Soleus KFGHP-09-ID Mini Split
This is normal operation for these styles of minisplits. The thermostat is not in the remote but is located on the return air of the indoor coil, so the air needs to be flowing in order for the thermostat to measure the rooms temperature. Set your fan speed to auto and the fan will slow down when setpoint tempurature is met.
Phil Hodges,
Tech support Soleusair
May 18, 2008 | Soleus KFS18GW 18,000 BTU Heat & Cool 230V...
No Heat!
Sometimes too much dust around the heating elements can cause the heater to switch off to prevent a fire. Check for dust build up first. You can try using a can of compressed air that can be found at many electronic stores.
Oct 26, 2007 | Vornado EH1-0014-01 Compact Heater
Heating & Cooling Logo
37 people viewed this question
Top Heating & Cooling Experts
Paul Carew
Dan Webster
Dan Webster
Tim Whalen