My bryant furnace fan will not turn on. Everything is sequencing, the induction fan starts and the flame lights, but the fan will not turn on. The capacitor reads 4.86 uf. Any suggestions?
Your fan delay relay is not functioning. On most furnace fan controls, there is a fan delay relay that delay the fan from turning on until it senses the temperature increase, typically around 130 degrees. once the relay senses the temperature increase it closes a contact inside the sensor and turns the blower on. It is the same device that keeps the fan running once the furnace turns off. Just take the Model number and serial number to your local dealer and get a fan delay relay and replace it.
Dec 07, 2014 | Bryant Heating & Cooling
Intertherm Furnace Model #mmhb070abhr06. Burner lights up but shuts down after about 10-30 seconds then recycles over & over again when fan is set to auto (because fan does not cycle on when set to...
Sounds to me like it is going off on a weak high limit switch. With the fan on it will prolong the event but will not stop it. I would check all of the high limit switches. It would most likely be one close to the heat exchanger.
Apr 06, 2014 | Intertherm 56000 Btu Gas Furnace
Fan does not shut off
If everything else appears to be working properly could be the thermostat calling for fan or installed improperly.
Mar 13, 2014 | Ruud Rheem Furnace Blower Motor...
AC unit comes on, but fan doesn't work. It works with furnace.
check for loose wiring to Tstat, or the new stat has failed.
if the stat has a fan on switch and when on the fan works then replace the stat
Apr 10, 2013 | Heating & Cooling
Furnace tries to start. Blower fan moves momentarily but doesn't.
May have a start capacitor on fan to get it started. If fan only jerks, it is probably bad. Replace if needed. Be sure to short it out with a rubber handled screwdriver or something to make it spark before removing.
Feb 18, 2013 | Rheem Water Heaters
I recently switched out an anolog thermostat for a programmable one. I programmed it and everything looks fine except the furnace isn't turning on. I manually bumped up the temp and nothing happ
My suggestion is you made a wiring error. Does the furnace come on when you turn the thermostat DOWN?
Re-check your wiring.The AUTO-MAN switch for the fan only switches the fan on, leave it in auto.
Feb 11, 2013 | Heating & Cooling
Furnace doesn't turn on.
When I experienced the symptoms you describe the problem turned out to be the igniter.
Dec 29, 2012 | Heating & Cooling
How can i wire in an auxilary fan to run with the furnace blower
Hi, if the fan doesn't draw too much power, there is no problem wiring it in parallel. I'm assuming it runs on the same voltage as the blower. If not, or if the fan requires a lot of power, you can wire in a relay to run the fan. If you provide details on the furnace and the fan I can be more specific.
Jul 03, 2011 | Heating & Cooling
How do you perform an electical test on the "automatic fan switch" in a Williams wall furnace blower accessory? Part number is P-322395. Everything else including the two-speed switch and fan...
disconnect power from fan. use an ohm meter should be open when cool and closed when hot. you can do same with 110v but be carefull. 110v to one side when cool and 110v on both sides when calling for fan.
Feb 09, 2011 | Heating & Cooling
My AC unit wont blow the cold air.
if the ac outside is working, but not the furnace, means there is a control problem with the furnace, check wires in the furnace, make sure there is a blower wire plugged into the contact marked cool on the control panel of the furnace
Jul 09, 2009 | Fedders A&B Chassis A1A07W2B Air...