Status light is flashing.....low flame signal...what should I do
3 Suggested Answers
Therinnaiguy
  • 1420 Answers
SOURCE: low flame signal
There is a small probe that is located inside the firebox and the flame from the burners will touch it. Typically it is located to either the far left or far right of the fire box if it is a vertical furnace. if the flame is not touching it or if it is taking the flame too long to travel across the burners (right to left or left to right) you will get this error code. Find the sensor and clean it with a small wire brush. Make sure what you think is the flame sensor is the flame sensor because the ignitor is very brittle and has two wires going to it. The flame sensor will have only one wire going to it. Also since you have the burner compartment open, inspect the flame spreader tray for blockage not allowing the flame to spread quickly. A can of air and the small wire brush will aide you in this cleaning.
Good luck to you!
Posted on Dec 05, 2008
  • 96 Answers
There is an L-shaped wire in the back by the flame that is the flame sensor you can take it out and take fine sand paper or emory cloth and try cleaning it
What does 3 flashes of the red light mean on an amana model ptc153a35ac ?
Here are your Amana flash codes:
Steady On - Normal
Off Controller Failure
1 System Lockout
2 Pressure Sw stuck closed
3 Pressure SW Stuck Open
4 Open - High Limit
5 Flame sense without gas valve
6 Open rollout or open Fuse
7 low flame signal
8 Check igniter or improper ground
continuous flashing - reversed AC polarity
Sep 11, 2014 | Heating & Cooling
How to find ink levels in hp932c printer
Print Cartridge Status The Print Cartridge Status Light flashes when one or both of your print cartridges are low on ink, improperly installed, or malfunctioning. It will also flash if you are trying to use the wrong print cartridge type. If the problem is low ink, the light will stop flashing when you open the top cover. For any other print cartridge-related problem, the Print Cartridge Status Light will continue to flash. To check the status of your print cartridges, open the printer's top cover. The yellow arrow on the print cartridge cradle aligns with one of five Print Cartridge Status icons.
Jan 08, 2011 | HP DeskJet 932c InkJet Printer
Hi, the lights on my circiut board are flashing the one on the left is on all the time and the one to the right of it flashes two times and then waits and then flashes two times again
Error Codes
A green LED indicates system faults
Steady On: System OK
Steady OFF: Board control fault or no power applied
1 Flash: Ignition failure (control in one-hour lockout)
2 Flashes: Pressure switch fault, fails open (switch is
stuck open)
3 Flashes: Limit switch open (main or auxiliary)
4 Flashes: Pressure switch fault, fails closed (switch is
stuck closed)
A yellow LED indicates flame status
Steady on: Normal flame is sensed
Flashes: As flame weakens, frequency of LED flashes
increases
hope this is helpful.
Dec 21, 2010 | Ruud Central System Air Conditioner
Tappen furnace pilot will not light.status light keeps blinkink
If the light keeps blinking, its not getting the signal back from the thermocoupler. Look to make sure the flame is touching the thermocoupler. If it is not bend the bracket so that the thermocoupler tip is inside the flame of the pilot. If it is, the thermocoupler is bad and need to be replaced.
Dec 12, 2010 | Heating & Cooling
What are the carrier 8000ts led error codes?
They are listed inside the front panel of the main unit.
LED CODE
EACH OF THE FOLLOWING STATUS CODES IS A TWO DIGIT NUMBER WITH THE FIRST
DIGIT DETERMINED BY THE NUMBER OF SHORT FLASHES AND THE SECOND DIGIT BY
THE NUMBER OF LONG FLASHES.
STATUS
11 NO PREVIOUS CODE - Stored status code is erased automatically after 72
hours. On RED LED boards stored status codes can also be erased when power
(115 VAC or 24 VAC) to control is interrupted.
12 BLOWER ON AFTER POWER UP (115 VAC or 24 VAC) -Blower runs for 90
seconds, if unit is powered up during a call for heat (R-W closed) or R-W opens
during blower on-delay.
13 LIMIT CIRCUIT LOCKOUT - Lockout occurs if the limit or flame rollout switch is
open longer than 3 minutes.
- Control will auto reset after three hours. - Refer to #33.
14 IGNITION LOCKOUT - Control will auto-reset after three hours. Refer to #34.
21 GAS HEATING LOCKOUT - Control will NOT auto reset.
Check for: - Mis-wired gas valve -Defective control (valve relay)
22 ABNORMAL FLAME-PROVING SIGNAL - Flame is proved while gas valve is
de-energized. Inducer will run until fault is cleared. Check for:
- Leaky gas valve - Stuck-open gas valve
23 PRESSURE SWITCH DID NOT OPEN Check for:
- Obstructed pressure tubing. - Pressure switch stuck closed.
24 SECONDARY VOLTAGE FUSE IS OPEN Check for:
- Short circuit in secondary voltage (24VAC) wiring.
31 PRESSURE SWITCH DID NOT CLOSE OR REOPENED - If open longer than
five minutes, inducer shuts off for 15 minutes before retry. Check for:
- Excessive wind - Proper vent sizing - Defective inducer motor
- Low inducer voltage (115VAC) - Defective pressure switch
- Inadequate combustion air supply - Restricted vent
- Disconnected or obstructed pressure tubing
- Low inlet gas pressure (if LGPS used)
If it opens during blower on-delay period, blower will come on for the selected
blower off-delay.
33 LIMIT CIRCUIT FAULT - Indicates a limit, or flame rollout is open. Blower will
run for 4 minutes or until open switch remakes whichever is longer. If open
longer than 3 minutes, code changes to lockout #13. If open less than 3 minutes
status code #33 continues to flash until blower shuts off. Flame rollout switch
requires manual reset. Check for: - Restricted vent
- Proper vent sizing - Loose blower wheel - Excessive wind
- Dirty filter or restricted duct system.
- Defective blower motor or capacitor. - Defective switch or connections.
- Inadequate combustion air supply (Flame Roll-out Switch open).
34 IGNITION PROVING FAILURE - Control will try three more times before lockout
#14 occurs. If flame signal lost during blower on-delay period, blower will come
on for the selected blower off-delay. Check for: - Control ground continuity
- Flame sensor must not be grounded
- Oxide buildup on flame sensor (clean with fine steel wool).
- Proper flame sense microamps (.5 microamps D.C. min., 4.0 - 6.0 nominal).
- Gas valve defective or gas valve turned off - Manual valve shut-off
- Defective Hot Surface Ignitor
- Inadequate flame carryover or rough ignition
- Green/Yellow wire MUST be connected to furnace sheet metal
45 CONTROL CIRCUITRY LOCKOUT Auto-reset after one hour lockout due to;
- Gas valve relay stuck open - Flame sense circuit failure
- Software check error
Reset power to clear lockout. Replace control if status code repeats.
If status code recall is needed, briefly remove then reconnect one main limit wire to display
stored status code. On RED LED boards do not remove power or blower door before initiating
status code recall. After one status code recall is completed component test will occur.
Thanks for Choosing FixYa.
Kelly
Oct 05, 2010 | Heating & Cooling
I have a RUUD Silhouette II and every once in a while the house gets cold and I check my furnace and the Status Light blinks-pauses-blinks-pauses ect. It is only flashes once so it tells me ''One Hour Time...
You will need to reset the furnace and have it run thru a cycle (or try). After three attempts, it will blink another error code that may tell you more.
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
Mar 03, 2010 | Ruud Matching Split Air Conditioner
Armstrong upflow,unit works intermittent problem,call for heat nothing happens,error code of 5 blinks then 6 blinks. i have no manuel, and the panels dont have the codes on them. anyone have access to the...
Armstrong
FAILURE CODES
LED Status Fault Description
Off
No Power to the System Control
Steady Flash (11 or more flashes with no pause)
Normal Operation (Standby or call for heat)
2 Flashes
Pressure Switch Closed When It Should Be Open
3 Flashes
Pressure Switch Stuck Open 30 Seconds or Longer After Call for Heat (System in 5-minute delay mode before next call for heat). On/off switch in "off" position during a call for heat will generate this code.
4 Flashes
Open Limit Switch or Limit Switch Circuit
5 Flashes
Flame Sense Signal Sensed Out of Proper Sequence
6 Flashes - pause - 1 Flash (see Note 1)*
Soft Lockout Type 1 (Failure to light within 4 trials for ignition)
6 Flashes - pause - 2 Flashes (see Notes 1 & 2)*
Soft Lockout Type 2 (Flame sense lost during run)
6 Flashes - pause - 3 Flashes (see Notes 1 & 2)*
Soft Lockout Type 3 (Pressure switch opened during run)
6 Flashes - pause - 4 Flashes (see Notes 1 & 2)*
Soft Lockout Type 4 (Limit or limit circuit opened during run)
6 Flashes - pause - 5 Flashes (see Note 1)*
Soft Lockout Type 5 (Flame has gone away after Error Code 5)
6 Flashes - pause - 7 Flashes (see Note 1)*
Soft Lockout Type 7 (Self-check failure)
10 Flashes* - SV9520H8034 only
Line Input Voltage Polarity Reversed
Dec 12, 2009 | Coleman Heating & Cooling
Low flame signal
Good luck to you!
Dec 05, 2008 | Goodman GMS90703BXA Heater
Low flame signal
Dec 05, 2008 | Goodman GMS80904BNA Open Flame Mid-Size...
Heating & Cooling Logo
27 people viewed this question
Top Heating & Cooling Experts
Paul Carew
Dan Webster
Dan Webster
Tim Whalen