Unit failed test no heat but blower come on changed board now 2days later no heat blower will not run in auto or manual no burnt smell what voltage should you get on speed taps at com to cool
Unit failed test so changed circuit board start unit all runs well now 2days later fan not running in auto or on no burnt smell and now will not run on test
watugot
  • 290 Answers
SOURCE: Ruud heat pump outside unit trips circuit breaker
Check your wiring between the contactor and compressor for a short to ground, or check the compressor windings for short to ground.
With the Tstat off, the contactor should be open so the only way for the compressor to be trying to do anything is if the 110 volts from the unbroken side are traveling through the compressor to ground. Since 110v is not enough to run it, the overload is kicking it out, cooling off, and repeating the cycle. When you kick on the Tstat, the contactor is supplying voltage directly to ground without going through the resistence of the compressor windings and kicking the breaker.
Post back and let me know what you find.
Posted on Nov 20, 2007
koolbreezes
  • 540 Answers
SOURCE: KELVINATOR KSR20C
One might think so, YES! look on one of the door panels that you can remove! Thank-you-very-much!
Posted on Aug 23, 2008
muttandjeff
  • 359 Answers
SOURCE: Blower in Attic not running
inside unit has fan control relay , either on control board or can be separate ,except for the 24 volt transformer and the t-stat the units operate separately concentrate totally on the inside unit this is where the problem lies
Posted on Nov 08, 2008
SOURCE: Goodman Air unit - Blower Fan will not kick on
same problem....any solutions yet?
Posted on Nov 12, 2008
jigsaw_9077
  • 308 Answers
SOURCE: 1998 BMW 328i heater/AC blower is not running
You have clean the blower unit , may be its dirty then . and then check the blower resistor unit for malfunction.
Posted on Aug 04, 2009
Blower motor on Trane 4TEE3C04A1000AA not coming on.
could be a number of things. heat may have blown a fuse now nothing works, heater may not have worked because the blower wasn't. you need a meter to test voltage.
Jan 15, 2018 | Heating & Cooling
Amana PTAC PTH093E Fan runs at single speed only regardless of setting-auto/low/high Hot or cool air is coming out so compressor/heat coil is working. Reset unit and replaced fan motor-no change.
I've replaced many Amanda control boards. They have micro relays attached to the board. These relays are about a half inch by 1 inch in size, and control line voltage to the compressor and blower motor, and give up quite often. Its probably the board if its a digital controlled board. If it has manual, turn to select, type knob, it will be in that fan section knob. Hope this helps!
Mar 13, 2017 | Amana Heating & Cooling
What are the carrier 8000ts led error codes?
They are listed inside the front panel of the main unit.
LED CODE
EACH OF THE FOLLOWING STATUS CODES IS A TWO DIGIT NUMBER WITH THE FIRST
DIGIT DETERMINED BY THE NUMBER OF SHORT FLASHES AND THE SECOND DIGIT BY
THE NUMBER OF LONG FLASHES.
STATUS
11 NO PREVIOUS CODE - Stored status code is erased automatically after 72
hours. On RED LED boards stored status codes can also be erased when power
(115 VAC or 24 VAC) to control is interrupted.
12 BLOWER ON AFTER POWER UP (115 VAC or 24 VAC) -Blower runs for 90
seconds, if unit is powered up during a call for heat (R-W closed) or R-W opens
during blower on-delay.
13 LIMIT CIRCUIT LOCKOUT - Lockout occurs if the limit or flame rollout switch is
open longer than 3 minutes.
- Control will auto reset after three hours. - Refer to #33.
14 IGNITION LOCKOUT - Control will auto-reset after three hours. Refer to #34.
21 GAS HEATING LOCKOUT - Control will NOT auto reset.
Check for: - Mis-wired gas valve -Defective control (valve relay)
22 ABNORMAL FLAME-PROVING SIGNAL - Flame is proved while gas valve is
de-energized. Inducer will run until fault is cleared. Check for:
- Leaky gas valve - Stuck-open gas valve
23 PRESSURE SWITCH DID NOT OPEN Check for:
- Obstructed pressure tubing. - Pressure switch stuck closed.
24 SECONDARY VOLTAGE FUSE IS OPEN Check for:
- Short circuit in secondary voltage (24VAC) wiring.
31 PRESSURE SWITCH DID NOT CLOSE OR REOPENED - If open longer than
five minutes, inducer shuts off for 15 minutes before retry. Check for:
- Excessive wind - Proper vent sizing - Defective inducer motor
- Low inducer voltage (115VAC) - Defective pressure switch
- Inadequate combustion air supply - Restricted vent
- Disconnected or obstructed pressure tubing
- Low inlet gas pressure (if LGPS used)
If it opens during blower on-delay period, blower will come on for the selected
blower off-delay.
33 LIMIT CIRCUIT FAULT - Indicates a limit, or flame rollout is open. Blower will
run for 4 minutes or until open switch remakes whichever is longer. If open
longer than 3 minutes, code changes to lockout #13. If open less than 3 minutes
status code #33 continues to flash until blower shuts off. Flame rollout switch
requires manual reset. Check for: - Restricted vent
- Proper vent sizing - Loose blower wheel - Excessive wind
- Dirty filter or restricted duct system.
- Defective blower motor or capacitor. - Defective switch or connections.
- Inadequate combustion air supply (Flame Roll-out Switch open).
34 IGNITION PROVING FAILURE - Control will try three more times before lockout
#14 occurs. If flame signal lost during blower on-delay period, blower will come
on for the selected blower off-delay. Check for: - Control ground continuity
- Flame sensor must not be grounded
- Oxide buildup on flame sensor (clean with fine steel wool).
- Proper flame sense microamps (.5 microamps D.C. min., 4.0 - 6.0 nominal).
- Gas valve defective or gas valve turned off - Manual valve shut-off
- Defective Hot Surface Ignitor
- Inadequate flame carryover or rough ignition
- Green/Yellow wire MUST be connected to furnace sheet metal
45 CONTROL CIRCUITRY LOCKOUT Auto-reset after one hour lockout due to;
- Gas valve relay stuck open - Flame sense circuit failure
- Software check error
Reset power to clear lockout. Replace control if status code repeats.
If status code recall is needed, briefly remove then reconnect one main limit wire to display
stored status code. On RED LED boards do not remove power or blower door before initiating
status code recall. After one status code recall is completed component test will occur.
Thanks for Choosing FixYa.
Kelly
Oct 05, 2010 | Heating & Cooling
Motherboard,It just went, burnt, for no reason,I sent it
Usually a "fried" motherboard will result from a faulty AC adapter / power supply. If the voltage it provides is too high, kiss the motherboard good bye! Most adapters output voltages around 18-19 volts at around 90 watts. If the adapter malfunctions, the voltages do not have to go much above the range to cause havoc.
If the repair shop did not FIRST check the voltage of the AC adapter before plugging it into a new motherboard, I would seriously consider a new repair shop!
Jan 07, 2010 | HP Computers & Internet
GMPN 100-4 furnace. Blower motor runs when not calling for heat.
The board is bad. The unit thinks a flame is present, so it tells the blower to come on. Replace the board.
Oct 07, 2009 | Goodman Heating & Cooling
Inside blower not starting every time
You have a voltage bleed somewhere or a short, whatever you want to call it. Do you have a control board on this unit where the relays are integrated into it or do you have the old type where the relay is separate? Anyway, you need to take a meter and take voltage readings to the motor when it's acting up and when it's running right. I have had the same problem with a Goodman unit before and it turned out to be the tstat! What I would do is remove the cover off the tstat and take a small jumper wire and touch the r terminal to the y terminal. If the motor starts right up, you know it's the tstat. If you have the same problem, then the only thing it can be is a low voltage short to the unit from the tstat, bad control board if you have one, or a bad relay. But if the unit is working fine in heat, it's probably not the relay. I hope this helps.
Apr 08, 2009 | Goodman Heating & Cooling
Heater no longer works on auto fan, only manual fan
When you call for fan in auto ensure your getting 24 volts at pin on control board, if it is not energizing then there is a problem with the relay.. Before you change out the expensive control board, try the therm..
Dec 09, 2008 | Heating & Cooling
Overheating? burnt oil smell
There is a seal between the compressor and the motor that in failed condition will leak oil into motor windings causing burnt oil smell. Some hitachi compressors suffered from failed valves or head gasket causing extra heat but not oil smell. These compressors also have a thermobreaker built into the windings that when failed will prevent motor from starting or would start and run for only a few moments then open. This part is not replaceable. enjoy
Oct 31, 2008 | Hitachi EC12 Portable Electric 2hp Air...
Goodman Heat/Air unit Model # A49-20 Serial # 9909502720
It sounds like the blower motor has burnt up.(the one inside) The unit running for a few minutes then shutting off, is due to the high pressure/temperature safeties. When you removed the panels, did you notice any fan running?
Feb 17, 2008 | Goodman CKL49AR49 Air Conditioner
Heater problem model PHK 080-1
THE BURNING SMELL IS NORMAL. BEFORE HEATING SEASON OPEN ALL DOORS AND TURN THE HEAT UP AND LET RUN TILL ALL DUST IS BURNT OFF. IF BLOWER IS NOT COMMING ON NOW. THERE ARE 2 TIME DELAY RELAYS, AND ANOTHER RELAY FOR "FAN ONLY OPERATION". ALWAYS MAKE SURE THEY ARE NOT THE PROBLEM BEFORE REPLACING AN EXPENSIVE MOTOR.
Feb 07, 2007 | Goodman PHKJ060-1 Air Conditioner
Heating & Cooling Logo
32 people viewed this question
Top Heating & Cooling Experts
Paul Carew
Dan Webster
Dan Webster
Tim Whalen