Heater not working on amana ghe75-3.5 gas furnace. Replace gas valve, fan limit switch. igniter controler and clean What could cause it not to work
Thermostat is working fine. Jump across the white and red wire at the thermostat and nothing work. Jump across the red and white wire at the control panel nothing work. The two other switches are ok.
  • Heating & Co... Master
  • 2,464 Answers
Did you check out the pressure switch
Posted on Dec 09, 2016
Gas furnace short cycles 2 minutes or less. Multiple troubleshoot steps and replaced components - no help. Any advice?
I did not see that your indoor fan motor started. Near your indoor fan motor there is a temperature switch that is called the fan delay relay. On a temperature rise the relay shuts a contact that turns on the indoor fan motor. If the contact does not close the high temperature limit will shut the gas controls off like your getting. A fan delay relay also allows the fan to run a minute or so to carry away the remaining heat in the furnace and help cool the furnace down. The fan delay relay is normally mounted in a recessed area in the fire wall of the furnace plate. I have also seen them on the top of the furnace heat exchanger. Anyway, the fan delay relay will probably not be available on a sunday, so temporarily until parts are available, try turning the thermostat fan from auto to on and try the furnace again. By turning on the fan to on the high temp limit will not shut you down again.
I have had high temp limit change there trip points, but you said you bypassed it and did the same thing.
Another cause could be using the wrong type of air filter. The new pleated filters sold block to much air flow. If air mass flow rate drops the difference in temperatur go up and when the difference in temperature go up, it gets nearer the high limit and causes it to trip. All pleated filters drop normal air flow through ducts by at least 35%. To make your air duct system work properly use the what is called throw away filters which cost about 1/3 the cost of the pleated filter. Remember to either clean or change the throw away filter monthly to reduce dirt being drawn into your duct system.
Hope this helps.
Feb 13, 2015 | Heating & Cooling
Gas furnace with Honeywell smart valve code error 6:2, replaced the following: pressure switch, smart valve, ignitor flame sensor and control board. Cleaned out the condensate line. Still getting 6:2 flash...
Hello, it sounds like your Furnace might be shutting off due to your high limit switch.A limit switch will open when the furnace overheats due to low airflow, . check air filter, clean blower wheel, and check to make sure the blower wheel is running at proper speed and not dragging sometimes cause by a weak capacitor. Anything that restricts airflow will cause a limit switch to open.
Mar 08, 2011 | Honeywell Heating & Cooling
I have a coleman evcon gas furnace that keeps giving me an error code (Limit switch open, and sometimes it wont kick on when i get this code, I have replaced the Lower Limit Switch, and workd fine for a...
i hope the heater doesnt come on when a limit switch is open,you really have problems. so a limit is telling you that your furnace it over heating. first check filter and heat vents and returns they must be clean and open. closing heat vent or blocked returns will cause over heating. after chacking this look at firing rate. furnace could be overfired. you would need a "u" gauge to check manifold pressure. your name plate will tell you what this should be. find the tap on the burner manifold or outlet of gas valve. fire furnace and see what it is. 3.5"wc for nat and 10" wc for propane maybe.
Feb 10, 2011 | Coleman Propane Forced Air Heater...
My heater isn't blowing any heat. I hear the fan come in, and i think i hear the gas come on, but nothing comes out of the vents. The fan only comes on for a couple of minutes and then goes off.
Ok so here is a sequence of the heater lighting and the solution for your problem...
1. Thermostat calls for heat. 2. Draft inducer motor starts. 3. Pressure switch attached by a small plastic or rubber tube senses the negative pressure produced by the draft inducer and closes. 4. Draft inducer runs for 30 seconds to a minute before you hear a gas hissing sound. The ignitor did not glow, the flame sensor (a small metal probe about 1/8" in diameter, with a white porcelain base) does not sense the flame, so after 8 to 10 seconds the hissing sounds stops with no ignition of gas to heat your home. Your furnace shuts down and goes into a lock out condition until you turn your power switch back off and on again. Then the sequence starts all over again with no ignition of the gas. Solution:You probably need to purchase and install a new ignitor. I would suggest that you inspect your ignitor closely for cracks.Make sure you do not touch the ignitor with your bare hands. If you do not visually see a crack, then you could have a furnace control board problem or a limit, rollout switch problem. Please see "limits, rollout switches & furnace control boards" further down on this page. The furnace's control board might not be supplying the voltage to the ignitor. If your furnace lights and the gas stays on for 8 to 10 seconds, then shuts right back off, then you need to clean your flame sensor with light sand paper or steel wool. You might need a new flame sensor, but most of the time they can be cleaned an will work well after cleaning. Please see the pictures below to help you identify a flame sensor.
Thanks and I hope this helps. Feedback apprec.
Jan 28, 2011 | Honeywell Electronic Programmable...
Coleman furnace -- fan runs, ingniter won't light,
The chances are that the furnace was running when the power went out. This will cause the high limit switch to cutout and needs to be manually reset.
You will find that switch in the blower compartment near the blower. Usually somewher near the highest point of the cabinet.
Push the little red button firmly till it clicks.
When the power goes out while the furnace is running the heat builds up because the blower shuts down immediately and causes this limit switch to cut out.
If you have a electric tester you can also follow the low voltage circuit till you find the open switch. Ther is usually a wiring schematic on the door cover of most furnaces.
I hope that this will help you to solve your problem!
Thanks for using Fixya!!
Heatman101
Dec 09, 2009 | Coleman Propane Forced Air Heater...
Question on a day and night gas forced air heater
it very well sounds like your fan switch , does your fan work at all, like in ac mode on by turning the fan on/auto switch on the thermostat to ON. If the fan does come on its the more and likely the limit switch. if it doesnt come on it could be the motor or the run capacitor. the limit switch has a dial on it that as it heats up it spins clicking on at a desired set temp ussually about 120 to 150 degrees F. turning on the fan if the fan doen't come in the the next setting clicks off the gas valve turning off the burners ussually set at about 220 degrees F. now if the fan is working when the heater is satisfied there is a setting at about 90 deegrees F. that shuts the fan off hope this helps
Jan 05, 2009 | Honeywell L4064B2236 Fan/Limit Control...
Heater will not light,ignighter glows,fan comes on,wont light,then shuts off
If your igniter comes on but no ignition, that eliminates the possibility of a bad or clogged pressure switch, high limit or flame rollout switch. Sounds to me like you have a control board, or a gas valve going bad. Could even be some loose, corroded, or faulty wiring. Before the igniter comes on the furnace does a self diagnostics to ensure everything is working, or the furnace will not make it to the igniter sequence. Inducer motor, pressure switch/s, limit controls are closed…then comes on the ignitier, gas valve opens, pilot runners and burners ignite, flame sensor detects the flame, blower comes on and all operations are working.
Hope this helps
Nov 30, 2008 | Heating & Cooling
Code continous flashing
Hope this helps
Oct 27, 2008 | Goodman GDS80904BNA Open Flame Heater
Ignition failure after three attempts then sits for an hour.
try cleaning the burners and or adjust the distance the igniter is from the actual burner .
Oct 01, 2008 | Goodman GDS80904BNA Open Flame Heater
Goodman GMP075-3 ignition problem
Goodman gmp075-3 gas furnace and the flame cycles for 4 sec
Heating & Cooling Logo
Top Heating & Cooling Experts
paulcarew
Dan Webster
Dan Webster
Donni Steen