Need some help. I rebuilt my old wall heater and it won't turn on. New thermopile, pilot and gas valve. The pilot works, but burner won't ignite. New thermostat too.

Posted by on

Ad

1 Answer

  • Level 3:

    An expert who has achieved level 3 by getting 1000 points

    Superstar:

    An expert that got 20 achievements.

    All-Star:

    An expert that got 10 achievements.

    MVP:

    An expert that got 5 achievements.

  • Heating & Co... Master
  • 2,550 Answers

Turn thermostat to off position check wires from thermopile to stat and gas valve for damage etc . Thermopile has to warm up and make 600 mille volts to work . Try this then open stat and see if it fires up .

Posted on Dec 05, 2016

Ad

1 Suggested Answer

6ya6ya
  • 2 Answers

SOURCE: I have freestanding Series 8 dishwasher. Lately during the filling cycle water hammer is occurring. How can this be resolved

Hi,
a 6ya expert can help you resolve that issue over the phone in a minute or two.
Best thing about this new service is that you are never placed on hold and get to talk to real repairmen in the US.
New users get to try the service completely Free afterwhich it costs $6 per call and covers almost anything you can think of (from cars to computers, handyman, and even drones).
click here to download the app (for users in the US for now) and get all the help you need.
Goodluck!

Posted on Jan 02, 2017

Ad

Add Your Answer

Uploading: 0%

my-video-file.mp4

Complete. Click "Add" to insert your video. Add

×

Loading...
Loading...

Related Questions:

2 Answers

Just replaced thermopile generator and pilot will not stay lit


Check the new thermopile with a millivolt meter and make sure it has the correct output not connected to the gas valve.If it does,then the gas valve is defective.Make sure to test ONLY the thermopile.If it does not generate enough millivolts the gas valve will not open.If the piliot is dirty it will not generate enough heat for the thermopile.Make sure you have a good,strong,blue flame at the pilot.You said the piliot will not stay lit?If not then start by blowing air back through the piliot where the flame comes out with compressed air.hopefully that will clean it well enough.If not you may have to take the pilot tubing loose from the valve and use compressed air to clean it.Make sure when you reconnect the tubing to the valve USE FINGERS ONLY to start tyubing or you may crossthread the tubing....and thats NOT a good thing.Good Luck.

Jan 16, 2015 | Williams Wall Heaters: 35,000 Btu/hr...

2 Answers

Outlet water gets so hot it ballooned the PVC pipe like an anuresum. Lights and shuts down, assuming that is a limit switch working properly. Filters cleaned last month/water pressure seems adequate.


Your thermopile that tells the heater how hot the water is has failed. It should kill the heat at a temperature of 104f. This also indicates that the limits are not doing their job, as they should be killing the heat at 135f (low limit) or 150f (high limit). Schedule 40 pvc is rated at about 140f.
This many failures at once is rare, and typically indicates that the heater has been rigged. Get a tech out to fix it correctly. You are literally playing with fire.

Nov 28, 2013 | Hayward H Series Pool & Spa Heater 400k...

2 Answers

Pilot won't stay lit on mr heater vent-free propane heater


if it is direct vent chances are it has electronic pilot.. it does not have a standing pilo and match size upt. if in fact it did have a buning pilot there is a part called thermocoupling. it will look like a 1/8 in. copper wire coming out of the bottom of the gas valve and goes right to the pilot. anywhere from 10 in. to 20in.. unscreew nut at gas valve pull out from pilot area [ it just clips in at pilot] take it to any home center

Nov 25, 2012 | Kitchen Ranges

1 Answer

When I turn on the heater, sometimes it comes on and sometimes it doesn't. The pilot remains lit. The repair person ruled out gas problems. Then he said it was the Thermostat but ruled that out and...


It sounds like your problem is delayed ignition.

This can be caused by low pilot flame height (Clean the pilot orifice or increase the pilot gas flow if necessary, by adjusting at combination control valve). Or the burner ports near the pilot flame are clogged and need cleaning. But, don't enlarge the holes. Low gas pressure can also cause this, but your repair person already ruled this out. If you have a wall thermostat, the Thermopile or Pilot Generator (it's the same thing) may be weak and failing. It's not generating enough millivolts of electricity to open the gas valve, when the thermostat is turned up. Or the Pilot Flame is not always touching it. If it is the Pilot Generator, the Cozy Part # is 70098 and cost around $40.00. A talented service man can install it easily.

Generally, these are the first things that you troubleshoot for delayed ignition.
Hope this helped to get you started.

Mar 23, 2011 | Cozy Enclosed Front Console Heater 70,000...

1 Answer

I replaced the gasvalve and thermalpile in my 35,BTU wall heater I light the pilot and turn the heat on it goes out I ran a new state wire in case of a short but it still does it, did I get a bad...


Did you get the right gas valve for a thermapile and not a 24 volt gas valve? Also I would recheck my wiring.... Here is a article that may be of HELP....... Hope this Helps.....
Thermocouple: A thermocouple is a device made of two different metals which creates a small electrical charge when heated at one end.
Thermopile: A thermopile is a probe that contains multiple thermocouples, therefore it can produce a larger electrical current. Millivolts: 1/1000 of a volt - thermocouples and thermopiles typically produce from 25 to 600 millivolts of power.
Piezio - a spark producing device often used to ignite gas pilots and burners.
Gas Valves Types:
A. Single Thermocouple Only - Used on some gas logs
B. Valves with Thermocouples and Thermopiles - Used on most hearth appliances and gas logs with switches or remote controls or thermostats.
C. ODS Systems - Used on Mostly Vent-Free. Available in manual control or thermostat/remote/switch (combination) valves.
valvepict.jpg
Typical Gas Valve A. Thermocouple-Only
Found in: Most gas log sets with standard safety pilot knob control. Also found in certain gas space heaters and construction-site portable heaters.
Explanation: This type of gas valve used a single thermocouple. A thermocouple is a device made of two different metals which creates a small electrical charge when heated at one end by the gas pilot. This small charge causes an electromagnet inside the gas valve to open and allow gas to flow to the main burners. Since the thermocouple must be heated before the burner will start, gas appliances often have a startup mode, during which a knob must be depressed and held for 30 seconds or so after lighting the pilot. At the end of the 30 seconds, the pilot should be generating enough electricity for the valve to operate correctly. At this time, the startup knob can be released and the valve turned to an "on" position for appliance operation.
pilotclose.gif Troubleshooting:
Most problems with this type of valve are due to thermocouple problems. Check the following:
1. Connection from the thermocouple to the valve. Clean the threads of the connecting nut with a pencil eraser and re-tighten.
2. Pilot hood and flame direction. The pilot should engulf the top 5/8" of the thermocouple with a decent flame. If the flame hits the thermocouple too low, this can cause the appliance to go out or not generate enough millivolts for valve operation. The pilot hood and orifice should also be clean from soot which could slow or block the pilot flame.
3. Pilot pressure. Many of these valves have an adjustment screw to adjust the pilot flame. A pilot that is too short may allow the pilot to stay lit after ignition, but may not create enough charge to allow the burners to ignite.
4. Overheating: If the unit works for a few hours and then shuts down, it's possible the thermocouple has become overheated. Repositioning of the gas valve and/or pilot may be needed to avoid this problem.
Problems with LP units can also be due to a tank that is nearly empty or a bad regulator at the tank.
B. Thermocouple & Thermopile valve
gas1.gif Found in: Most modern VENTED gas stoves, fireplaces and fireplace inserts as well as vented gas log sets with thermostat or remote control.
This valve is similar to the thermocouple only valve, however has a pilot which heats up BOTH a thermocouple and a thermopile. The thermocouple still acts to prove that the pilot flame is on and allows this flame to continue after startup. The thermopile is used to power a second circuit which is used to open the main valve. This second circuit is powerful enough (300-600 millivolts) to allow the use of a thermostat, wall switch or control switch to operate the main valve. Control of the valve is obtained simply by hooking a pair of wires to two terminals located on the valve.
Startup is similar to the thermocouple-only valve. A piezo spark ignition is used to ignite the pilot after the gas knob is turned to the "pilot" position and depressed. Once the pilot is lit, the knob is held in for 30 seconds to "prove" the heat and then released and turned from the "pilot" to the "on" position. The main burner will then respond to the switch, thermostat or remote control.
Troubleshooting
Since there is both a thermocouple and thermopile in this valve type, it is important to isolate where the potential problem may be. If the pilot can be lit and stays on after the knob is released, then the problem is probably with the thermopile side of the valve. Here are the most common problems and solutions.
1. Pilot does not light or stay lit after knob is released - Make certain that the Piezo igniter works by checking for a spark between the igniter tip and the pilot hood. If there is no spark, the piezo may be bad or the piezo wire might be shorting to the appliance chassis. It is also possible that the igniter tip needs to be bent slightly toward the pilot hood so the spark jumps to it.
Check carefully that gas to appliance is on and that the valve is in he correct (pilot) position and fully depressed when lighting.
If pilot ignites but does not stay lit after knob is released, then the problem is with the thermocouple not generating enough voltage to the valve. It may be that the pilot adjustment needs to be turned up, or the thermocouple replaced. Another possibility is that the thermocouple may not be being "bathed" fully by the pilot flame. Check your owners manual for a diagram and description of the proper pilot flame and hood adjustment. It is also possible that there is soot or other blockage in the pilot tube, orifice or hood which is reducing the size of the pilot (and also the voltage of the thermocouple).
2. Pilot stays lit, but appliance will not turn on - There are two common causes for this. It is possible that the thermopile is not producing enough millivolts to power the control circuit. The millivolts can be checked with a simple voltmeter (consult the owners manual for proper setting) and adjusted with the pilot adjustment screw. Improper millivolts will also cause the appliance to shut down in the middle of operation.
Another common problem is loose or poor connections or circuits to your appliance switch, thermostat or remote transceiver. This can be isolated by simply using a small piece of wire to jump the "TP" and "TH" terminals located on these valves. If the appliance turns on when these terminals are jumped, then you can be sure that your problem is not in the appliance itself, but further down the switch circuit. Make certain you have used the suggested gauge of wire and that the length for your control runs does not exceed the specs given in your manual.
3. Other possible problems - include wind or back drafts affecting the pilot flame and checking of "spillage" circuits which may be wired into the valve in most B-Vent units.
If all the above checks out, and your valve is still acting weird (i.e., works some of the time), then you may have a defective gas valve in the appliance. Problems with LP units can also be due to a tank that is nearly empty or a bad regulator at the tank.
C. ODS System
Found in: Unvented (Ventless, Vent free) gas logs, fireplaces and stoves. These systems are available in manual or remote control.
ods.gif ODS stands for "Oxygen Depletion Sensor" , a term which accurately describes this valve type. The valve itself is similar in many ways to the two valve types above...with one exception. The pilot tube is a precision mechanism that creates a very stable flame as long as the room air contains the proper amount of oxygen. If the oxygen level in the room air drops even slightly, the pilot becomes unstable and lifts off of the thermocouple (see diagram) causing the gas valve and appliance to cease operation. This type of valve is very reliable, and there have been very few failures of this system - even with tens of millions in use worldwide.

Mar 02, 2011 | Heating & Cooling

1 Answer

I replaced the thermalpile in my wall heater and when I turn the stat up the pilot goes out what do I do


The air intakes of the burner may be clogged or you wired the "thermopile" to the wrong contacts on the control valve.

You didn't mention if this was a vented or vent-free heater. If it's a vent-free heater the same things listed above still apply. However, it may be that the Oxygen Depletion Sensor (ODS) which is part of the pilot may be clogged with dust, lint and/or pet hair. When the T-stat calls for gas to light the burners, the ODS senses there's not enough oxygen for safe combustion and closes the gas valve.

Also, gas pressure to the heater may be low. Only enough to keep the pilot burning, but not enough to ignite the burner(s).

Hoe this helps to head you in the right direction on further trouble shooting the problem.

Mar 02, 2011 | Heating & Cooling

1 Answer

My empire wall furnace does not ignite. It has gas flowing because the pilot is light, i have changed the thermostat and wired it two different ways in case I reversed them. What is next? Could it be the...


It could be several things: Is the Control Knob turned from Pilot to ON? If that is the case, wait a few minutes after turning it to ON. That will allow the Thermopile to heat up sufficiently. Be sure the flame is touching the Thermopile. If everything looks correct turn up your Thermostat to higher than the ambient room temperature and see if the burners light. Remember to turn your Wall Thermostat down to the lowest temperature setting before turning the knob from Pilot to ON.

FYI - That Wall Furnace does not have a Thermocouple. It uses a Thermopile instead to generate millivolts of electricity to open the gas valve and maintain the pilot flame.

If it is the Thermopile, you can order it directly from Empire Comfort Systems, as well as download your Owners Manual at www.empirecomfort.com

Feb 04, 2011 | Empire GWT-50 Wall Mounted Panel Heater

1 Answer

Pilot light will go out when internal thermostat turns off main burner


Could be the thermopile or bad gas valve. Lets hope for a bad thermopile (costs much less). Are you able to re-light the pilot and does it stay on without the main burner on?

Nov 27, 2009 | Procom QL300TYLA Heater

1 Answer

Heater will not turn on


If these are newer units 5 years or newer, there may be a thermal safety device up near the top. Follow the wires to find it. if you have this, bypass it by connecting the two wires going to it to each other and not the little disc. If this does not get the burner to ignite, then the next culprit or you do not have one then next is the pilot generator. This is the round cylinder next to the pilot flame. It and has 2 wires connecting to the gas valve. Remove it from the pilot assembly, it usually is just a clip, unscrew the 2 wires and pick up a new one. The connection on the gas valve has these wires labeled as TP for thermopile (dont ask, I don't know) replace in reverse as removed.

Dec 16, 2007 | Reddy R70ET Utility Heater

Not finding what you are looking for?
Heating & Cooling Logo

Related Topics:

30 people viewed this question

Ask a Question

Usually answered in minutes!

Top Heating & Cooling Experts

Paul Carew

Level 3 Expert

2550 Answers

Dan Webster
Dan Webster

Level 3 Expert

8220 Answers

Donni Steen

Level 3 Expert

659 Answers

Are you a Heating and Cooling Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...