My furnace (heil n9mp2) short cycles. Once it reaches temp it's fine and only cycles about every 15-20 minutes. But if I raise the thermostat setting it short cycles til it reaches temp
  • 70 Answers
SOURCE: Furnace not cycling properly
sounds like the flame sensor needs to be replace. You can try cleaning it with steel wool. This will get you by for a little while.
Posted on Jan 20, 2009
  • 587 Answers
SOURCE: goodman furnace\ blower comes on,unasked
Sounds like the fan switch on the furnace is set to low. Turn power off to furnace, take door off of furnace look for a fan switch, it may be a fan - limit together. The limit settings should be approximately 160° to 200°, and the fan settings should be about 100° to 140° set it to 120° it it's already set there then you probably need to replace it.
Posted on Aug 23, 2009
Therinnaiguy
  • 1420 Answers
SOURCE: Furnace cuts off before reaching set temp.
You can make sure it is not the thermostat by crossing or jumping the R and W terminals (or associated wires) together. This will keep the furnace calling for heat. As it is approaching set temperature, get in front of the furnace and inspect the air filter to make sure it is clean, watch the control module for any error codes that may be turning off the system prematurely.
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
Posted on Mar 07, 2010
  • 69 Answers
SOURCE: heil furnace blower motor stays on won't shut off at thermostat blows cold air continuously
Do you have t sat fan switch in on position??? If so blower will run continously set it to auto and it will cycle with heat call
Posted on Nov 25, 2012
SOURCE: furnace wont start when thermostat sends signal
bad primary control (the box with the reset button), maybe your thermostat but unlikely. Try the Primary Control first. How old is your burner?
Posted on Dec 14, 2012
Model sf35f furnace wont quit heating after reaching thermostat setting
Sounds like the heat anticipator in your thermostat is either bad or out of adjustment. Turn of the furnace power. Remove the thermostat wires from the thermostat. Turn the power back on. Connect the white and red wires together. The furnace should start up. Let it run a couple of minutes. Then disconnect the wires. The burners should shut off immediately. The blower will continue to run for 60 to 360 seconds then shut off. If this happens replace your thermostat. If the burners continue to burn, then your problem is either the furnace or the thermostat wires.
Sep 12, 2014 | Heating & Cooling
My furnace will not reach the desired house temperature in one cycle. It will run for several minutes, shut off, and repeat. It eventually reaches the desired temp but it take a long time and I feel it...
There are a few different reasons for short cycling of a furnace.
1. Inadequate air flow. Not enough air moving through the furnace can cause it to overheat and trip the high temperature limit switch.
check to see that all registers are open and returns are not blocked.
2 Improper heat anticipator setting on thermostat. Some thermostats have a heat anticipator and too low of a setting can cause short cycling.
4 Partially blocked drain hoses. If the condensate backs up into the furnace it can shut the flame off and then when the condensate drains the furnace starts again. Check all drain hoses to make sure they are clear.
These are just some of the possible reasons for short cycling .
Hope this helps.
Dec 26, 2013 | Heating & Cooling
Electric furnace/air handler short cycles
check that the replaced thermostat is the same temp degree setting of the last one
Dec 16, 2013 | Goodman Heating & Cooling
Fasdfas
Does the furnace stays off?.
Furnace are ment to cycle on and off because of limits .If you set to 70 furnace would cycle several times before reaching that temperature.
Just make sure your filters are clean and you got proper return air flow because lack of air flow will cause furnace to shut off sooner than normal
Jun 08, 2017 | Heating & Cooling
Heil furnace blower motor stays on won't shut off at thermostat blows cold air continuously
Nov 12, 2012 | Heating & Cooling
Mar 07, 2010 | Honeywell Programmable Thermostat Heater
Temp shows 2 degrees warmer than what is was set to
sometimes the furnace does a better job than anticipated, i wouldn't worry about it, especially if the furnace shuts off.
the setpoint is the temperature you want it to be
cycle lenghts are determined by how much recovery you are requesting. for instance, in the morning when you wake up, you want the temperature to be at its setpoint. what the thermostat will do is make the furnace run a limited lengths during the recovery process.
Nov 11, 2008 | Honeywell Programmable Thermostat Heater
Heating & Cooling Logo
26 people viewed this question
Top Heating & Cooling Experts
paulcarew
Dan Webster
Dan Webster
Donni Steen