Question about Goodman Heating & Cooling
Goodman Furnace gms91155dxa not staying on. The system ignites, but shuts off after 3 minutes. 1 blink LED system light
Here is what happens: -The blower starts and pressurizes the compartment -The igniter glows and the flame rolls out -The system runs for about 3 minutes and then the flame flickers and shuts off -The blowers stay on for a bit and the system tries to reignite the flame 3 times which triggers the system to shut off -The system LED blinks 1 time stating that it exceeded the retry/recycle limits Any help would be greatly appreciated. Thanks, Billy
    Habit-Forming:
  • 107 Answers
100% sounds like an electrical problem, something is not allowing it to go into a duty cycle.
Posted on Dec 04, 2016
Testimonial: "Any suggestions as to where I can begin troubleshooting what is causing this?"
  • Ron the Don Dec 04, 2016
    You could have a wire inside the machine grounding out, or shorting out to something, is the control panel digital? Can you access any settings, if so I would look through them to see if anything looks out of place. The control board could be fried in a spot, or have a wire with soder that overheated and separated I have seen that before, when the blower starts does it have a release hatch that may not be opening? that would surely cause the system to not go into duty cycle. Good Luck!
  • Billy Cabrales
    Billy Cabrales Dec 04, 2016
    It turned out to be that one of the drain hoses was clogged and was causing one of the pressure switches to trip. I unclogged the hose and cleaned everything out. All is well now.
I have a goodman furnace GMP100-4 REV B..about a year ago it was not working. The fan would start but it would not ignite. We found out we need a new ignitor and it was a good quick easy fix. Now a ye
Any light flashin on the control board? If not then look for a small fuse blown on the board. See lights a flashing count them flashes
A sampling of various failure codes on a furnace:
Read one LED flash that stays on continuously to mean your furnace has no signal coming from the thermostat and will not operate. Turn the power off and check the thermostat for improper settings or connections.
Interpret one LED flash that blinks on and off to mean your furnace has locked out because it could not ignite after three tries, and must be reset. Interrupt power to your furnace for 20 seconds or lower the thermostat so your furnace does not try to heat, then reset the thermostat to the previous setting. After one hour of lockout, your furnace will automatically reset itself and try to operate as usual.
Decipher two LED flashes to mean the draft blower is not working, or your furnace has a short in the pressure switch circuit. Turn off the furnace power and repair a short or replace the pressure switch.
Read three LED flashes to mean your furnace has an open pressure switch circuit or it has an induced draft blower operating. Check the pressure switch hose of your furnace for blocks or an improper connection. Also, look for blockages in the flue, and tighten any loose wiring.
Translate four LED flashes to mean your furnace has a primary limit circuit open, possibly from loose wiring or blocked filters. Check and clean filters, tighten wiring and check the flue for blockages.
Interpret five LED flashes to mean your furnace senses a flame without a call for heat. This could be from a gas valve closing slowly or a burner flame lingering.
Read seven LED flashes as a warning of a low flame sense microamp signal. This could happen with a coated flame sensor or a lazy flame from poor gas pressure. Turn off the power and adjust the gas pressure according to the information on the rating plate.
See eight LED flashes as meaning an igniter circuit problem due to a bad igniter or an igniter connected improperly. Replace the bad igniter or check the ground wiring, making necessary corrections.
Decipher nine LED flashes to mean the high-stage pressure switch circuit will not close during a high-stage-induced draft blower operation. Your furnace may have a pinched or blocked pressure switch hose, a blocked flue or loose wiring.
Read continuous flashing on the LED to mean your furnace has a reversed polarity of 115 volts. Turn off the power and correct the wiring polarity after reviewing the wiring diagram.
If you need further help, reach me via phone at https://www.6ya.com/expert/dan_73bbd84fe1d95b61
Nov 29, 2011 | Goodman Heating & Cooling
I have a Goodman GMP 125-5 furnace. It had a 3 light code i replaced the presure switch now it is giving me a 1 light code please help
Oct 28, 2011 | Goodman Heating & Cooling
The Goodman Heater was installed in 2004. Thermostat set at 75F, the fan that blows CO2 out was on for about 1 minute, then I could hear the sound of the gas blowing into the furnace, but the ignitor...
Problem: Your furnace will not ignite the gas to produce heat for your home. When a furnace has a bad ignitor what I see most of the time is the following sequence of operation:
1. Thermostat calls for heat. 2. Draft inducer motor starts. 3. Pressure switch attached by a small plastic or rubber tube senses the negative pressure produced by the draft inducer and closes. 4. Draft inducer runs for 30 seconds to a minute before you hear a gas hissing sound. The ignitor did not glow, the flame sensor (a small metal probe about 1/8" in diameter, with a white porcelain base) does not sense the flame, so after 8 to 10 seconds the hissing sounds stops with no ignition of gas to heat your home. Your furnace shuts down and goes into a lock out condition until you turn your power switch back off and on again. Then the sequence starts all over again with no ignition of the gas. Solution:You probably need to purchase and install a new ignitor. I would suggest that you inspect your ignitor closely for cracks. Make sure you do not touch the ignitor with your bare hands. If you do not visually see a crack, then you could have a furnace control board problem or a limit, rollout switch problem. The furnace's control board might not be supplying the voltage to the ignitor. If your furnace lights and the gas stays on for 8 to 10 seconds, then shuts right back off, then you need to clean your flame sensor with light sand paper or steel wool. You might need a new flame sensor, but most of the time they can be cleaned an will work well after cleaning.
Nov 30, 2010 | Goodman GMS80903BNA Heater
Goodman GMP075-3 Has 1 single blink on the light
The blink codes are differant on every furnace. Read your code on the schematic found on the inside of the door. You most likey have a dirty flame sensor. Under the burners you should find a "single" wire going to a connector. This will be to the far left or right. Just opposite of a "two" white wires going to the hot surface igniter. Remove the 1/4 inch screw closet to the single wire under the burner. carefully pull out the flame sensor. Clean it with a small piece of sandpaper. Re install it. This should fix your furnace. KEEP IN MIND Goodman GMP models are noted for defective heatexchangers. Pull out the blower assembly and turn it over. If small rings about the size of a dime falls out.... this furnace is unsafe and should replaced!
Mar 08, 2009 | Goodman GMS90703BXA Heater
Thermostat at 70, shuts off at 62. stays only 1/2 hour at at time
What LED are you talking about that keeps flashing?
If it's the LED on the controller board in the furnace, they blink with a cadence that you need to watch. There will be a data sheet somewhere on the furnace that will tell you what the cadence (flash cadence) is.
Replay back and I can help you more.
Jan 30, 2009 | Goodman GMS90703BXA Heater
Furnace won't stay running
1 FLASH
Furnace fails to operate.
• Integrated control module
diagnostic LED is
flashing ONE (1) flash.
• Furnace lockout due
to an excessive
number of ignition
“retries” (3 total)1.
• Failure to establish flame.
Cause may be no gas to
burners, front cover
pressure switch stuck open,
bad igniter or igniter
alignment, improper orifices,
or coated/oxidized or
improperly connected flame
sensor.
• Loss of flame after establishment.
Cause may be
interrupted gas supply, lazy
burner flames (improper gas
pressure or restriction in flue
and/or combustion air
piping), front cover pressure
switch opening, or improper
performance.
• Locate and correct gas
interruption.
• Check front cover
pressure switch
operation (hose, wiring,
contact operation).
Correct if necessary.
• Replace or realign
igniter.
• Check flame sense
signal. Sand sensor if
coated and/or oxidized.
• Check flue piping for
blockage, proper
length, elbows, and
termination.
• Verify proper induced
draft blower performance.
Nov 23, 2008 | Goodman GMS90703BXA Heater
Goodman GMS90904CXA Wont ignite, light blinks 3 times
I had the same problem, I had to remove the lower black rubber stopper right next to the exaust fan and hook up a drain to the unit, as soon as the water drained out the furnace fired right up.
Nov 19, 2008 | Heating & Cooling
GOODMAN CMA80905CXBA FURNACE. INDUCTION BLOWER NOT ENERGIZING. GETTING 3 "BLINKS" FROM DIAGNOSTIC LIGHT (LOW PRESSURE SWITCH OPEN). THE A/C WORKS & THE BLOWER FAN COMES ON WHEN THE STAT IS IN...
the pressure switch is closed before the draft motor closes it.the board is telling you that this is not right.pull the wire(either) off of the pressure switch to see if furnace tries to light.if it does,you should replace the pressure switch.
Oct 02, 2008 | Goodman Heating & Cooling
Heating & Cooling Logo
62 people viewed this question
Top Goodman Heating & Cooling Experts
Paul Carew
Tim Whalen
christian nielsen