Have two ruud 3.5 gas furnaces twined. getting a error code 5 power light is ok. they service a 7.5 ruud three phase condensing unit-
  • 1,272 Answers
It seems to be an issue with Rollout switch.
Regards
Anand
Posted on Jul 18, 2009
Replace compacitor on Carrier 5 ton 3 phase AC
Your 3 phase unit should not have a capacitor. I'm guessing it's single phase. If it's a single capacitor than the compressor should not be going to it also. To test the motor, common to start plus common to run should equal the ohms you get between start and run. For instance, 1.2 ohms+ 2.2 ohms= 3.4 ohms. Follow the wiring diagram on the inside of the door, send model number!!
Aug 29, 2017 | Carrier Heating & Cooling
Protech 62-24084-02 troubleshooting
62-24084-02 LED CODES
POWER LED - GREEN
ON - Normal
OFF - No power to board
OK LED - GREEN
One Blink - One hour retry delay
Two Blinks - Pressure switch failure (remains open)
Three Blinks - Limit switch fault
Four Blinks - Pressure switch failure (remains closed)
Five Blinks - Twinning fault
FLAME LED - YELLOW
ON - Good flame
Rapid Blink - Flame present with gas valve de-energizing
Slow Blink - Marginal flame
Jan 01, 2014 | Protech Rheem/62-24084-82-1PK - Integrated...
LP Ruud furnace achiever 90+. Strange problem.
Sounds like two problems. Not enough combustion air or a defective high temperature limit switch. You enclosure may not be getting enough outside air to properly sustain combustion. If the unit has a rollout thermostat it may be defective and stopping everything.
Oct 10, 2009 | Heating & Cooling
RUUD UPGH air/furnace just quit....no response...where to begin?
is the power light on the board lit? IF NOT THE 3 AMP OR 5 AMP FUSE COULD HAVE BLOWN ON THE BOARD
Apr 27, 2009 | Heating & Cooling
Ruud Silhouette II Fails to Ignite
sounds like you have bad flame sensor or the sensor is in a bad postition. To get eliminate the lockout turn the power off to the unit and back on again. Look at the circuit board light and see what the troubleshooting code is.
Jan 13, 2009 | Heating & Cooling
Goodman GMP050-3
If you do not have two furnaces hooked together, you have a bad circuit board or an improper ground or neutral wire.
Dec 09, 2008 | Goodman GMS90703BXA Heater
My urka-a030jk0 ruud air/heat is showing a error code 8e with five flashes what is wrong
An error code 5 is a twinning error. This only applies when the unit is "Twined" with another unit. When the unit is not twined it is because of dipswitch 3 on the SW1. It is either in the in position or it has developed a bad connection. Disconnect power from the unit and work switch 3 back and forth several times and place in the "Single" position or "OFF" and restore power. This should resolve the issue. If it does not the board must be replaced.
Richard (Rick) Drennan
Global HVAC Distributors
RUUD Field Support Representative / Instructor
rdrennan@globalhvac.com
900 Spreckels Ave
Manteca, Ca. 95336
Office (877)448-7263
Dec 04, 2008 | Ruud UBHC Air Conditioner
Ruud RKKA Series Split Unit
the pressure switch has to pull in for the gas valve to be powered so check switch and venting