Where can i get a pump-down valve for an
Where can i get a pump-down valve and sight glass for an RAWL-090CAZ? R-410a split system
  • 614 Answers
Any air conditioning parts warehouse or order on line just type in ac parts. you need 3/8 inch solenoid vavle 24 volts. sight glasses dont help much in domestic ac. Rus
Posted on Jul 15, 2009
Tip
Charging an air conditioner by superheat or subcooling
Charging AC by superheat and subcool
First charging a unit by superheat, this is only for Acs with an orifice or capillary tube.
Optimum superheat is 12° to 15° at the compressor or suction line outside the unit.
Hook up your gages and put a thermometer on suction line (large line), start the AC. Measure the temperature of the suction line and read the pressure on your gages. Theres a temperature scale on your gages for R-22 or R-410A the needle will show you the pressure on the outer scale and if you follow it down to the R-22 or R-410a inner scale that is the saturation temperature for that refrigerant, (you can also use a temperature pressure chart), now read the thermometer, let’s say the suction temperature( the thermometer) is 67° and the saturation temperature (the gages or temp. press. Chart), is 55°, subtract the saturation temperature from the suction temperature, 67°- 55° = 12° superheat.
Charging by Subcooling, this is for Acs with a thermostatic expansion valve, it’s common to see a sight glass on the liquid line (on these units with a sight glass just clear it, when, indoor room is at approximate set point of the thermostat). If there is no sight glass then the Optimum sub cooling is 12° to 15° at the outdoor unit.
Hook up your gages and put a thermometer on liquid line (small line), start the AC. Measure the temperature of the liquid line and read the pressure on your gages. Theres a temperature scale on your gages for R-22 or R-410A the needle will show you the pressure on the outer scale and if you follow it down to the R-22 or R-410a inner scale that is the saturation temperature for that refrigerant,(you can also use a temperature pressure chart), now read the thermometer, let’s say the liquid temperature( the thermometer) is 100° and the saturation temperature (the gages or temp. press. Chart), is 114°, subtract the liquid temperature from the saturation temperature, 114°- 100° = 14° subcool.
This is also the only way to know if your a/c has the proper charge.
on Dec 28, 2009 | Heating & Cooling
There's a little glass jar that screwed onto our pool pump and it has gotten broken. Where can I get a n replacement?
The pump or the filter? I believe what you are looking for is the sight glass found in the backwash port of the filter valve. If that is correct what brand is the valve and what numbers are on it if you can still read them? I should be able to get you a part number with that information or take what is left of the old one to a local pool supply store and match it up to a replacement glass. Most of the sight glasses are the same no matter whose name is on the valve.
John
Mar 30, 2011 | Jacuzzi Pool & Spa
I have a 4 ton outside and a 5 ton coil inside square footage of the house is 2495 living.my preasures are 75 low side and 225 hi side i'm not getting any flood back is this ok are do i need to add more...
Charging by Subcooling, this is for Acs with a thermostatic expansion valve, it’s common to see a sight glass on the liquid line (on these units with a sight glass just clear it, when, indoor room is at approximate set point of the thermostat). Optimum sub cooling is 12° to 15° at the outdoor unit.
Aug 09, 2010 | Amana Heating & Cooling
How to refill gas in home spli a/c, advise presure details as wel
Mar 19, 2010 | Panasonic CW-1006FU Air Conditioner
Gas pressure
It depends on the indoor and outdoor temperature and humidity. The low side pressure can be in the area of 135# to 145# with an indoor temperature of 80° and 50% relative humidity, and the outdoor pressure can be in the area of 300# to 330# on a 95° day depending on effeciency rating.
If your asking this to charge your a/c this is not how to charge your a/c.
Dec 25, 2009 | Heating & Cooling
When i was fixed a problem in central ac trane i found decreased in freon r22 and the suctione line was freezed, i charged the ac with froen gas r 22 then i found that the suctione line changed and begin...
You are still low on freon. Charging AC by superheat and subcool
Oct 05, 2009 | Heating & Cooling
GSH13 Goodman heat pump split system is running a long time in cooling mode and will not cool below 74 degrees. A lot of condensation generated. The low side pressures 78 to 81 and high side pressures are...
Check sub cooling and super heat. the New ac units are very critical to charge. There is a charging chart on the inside of the cover to the unit outside. Check temp difference across coil. Should be 18 to 22 degress. If you have an ampmeter. Check the heat strips one 5 kw might be stuck.(sequencer). This would cause you not be able to pull down temp. Goodman unit are hard to charge to get the temp difference across coil. Feedback please
Jun 14, 2009 | Goodman CLQ36AR49 Air Conditioner
Senville Mini Split Error Code
thanks for your question, you will need a set of gauges on the unit to determine if the unit came precharged, if it didn't then you will need to vacuum down the unit, at least three times, after each time release a little 410a into the system them evacuate again, 410a is bad for drawing moisture, did you put an in-line filter dryer on as well ? after you find out about the freon level, then look at the name plate rating for amount of 410a needed, before adding the freon, use nitrogen to leak check the system, then weigh in the proper amount of 410a, unit should run really well after that, hope that helped, thanks again for your question, please feel free to come back if you have any more questions, thanks, mr.grzz