Question about MGE UPS Galaxy 3000 UPS System
When loaded,displays Rectifier fault
When loaded to the equipments , MGE 3000 displays "Rectifier fault".
with no load, the MGE displays normal.What would be the probable
components or circuit module suspected to be the cause of the trouble?
Hello, our MGE GALAXY 3000 20kva, front panel display is frosen. UPS still operates but not able to use any buttons to see ups status. Also alarm states "internal communication fault". Would appreciate...
you need an MGE expert engineer to check on the internal components, maybe the display by itself it dead can be replaced while UPS is on no problem. if you want to switch off the UPS you go for force shutdown but I cannot guarantee will restart if you do not fix the fault.
Aug 09, 2013 | MGE Galaxy 3000 UPS System
Temperature fault. Q5N open
pls cheak by pas slecter not normal position load on by pas temperature fault 1st cheak coling water 2nd room temp 3rd cheak temperature sencer battary breakr to batt bank side 2 wair
Jul 25, 2013 | MGE UPS Galaxy 3000 UPS System
Temperature fault
What is the temperature around the batteries?
MGE Galaxy 3000 UPS, do i require to reconfigure the ups after battery replacement? Thanks.
No you don't have to reconfigure the UPS after battery replacement. However you may have to reset the battery Timer. There are 4 possible ways.
1. Press and hold the fault reset button for 3-5 seconds
2. Press and hold the fault reset and security key simultaneously for 3-5 seconds
3. Press an dhold the fault and alarm silence buttons simultaneously for 3-5 seconds
4. Cycle the logic Power. This means to remove power from the main processor.
5. Call MGE. They have the software to reset the battery replacement alarm
Oct 19, 2011 | MGE Galaxy 3000 UPS System
Galaxy 3000 30kVA showns battery charge fault.beacause battery?
UPS battery must be tested individually before you can decide it is a battery problem or if charging fault can cause by defective rectifier/charger board.
Sep 09, 2011 | MGE Galaxy 3000 UPS System
How to fully shut down the MGE MX5000 UPS?
1 - Press the "0" button (28) more than 3s. The buzzer beeps once, and the load is no longer protected by the UPS. It is powered via the Normal AC source. If the UPS is set in frequency converter mode, the equipments will not be powered. If the Normal AC source is out of tolerance, the UPS will generate a 10ms output calibrated break. 2 - For a full shutdown of UPS and connected load, the upstream circuit breaker (notincluded) should be set to the "0" position.
Sep 09, 2011 | MGE Pulsar MX 5000 (68505) UPS System
Ups temprature fault
From what info you gave me. It sounds to me like it is either too small for the load, or it is in a confined space where heat is building up (UPS has to be outside of a desk office, etc.) or the rectifier is going bad and heating up. I would check to see if it does it by hooking up a small load to it like a radio or something, and if it is in the open, not overloaded then rectifier is bad,I see it alot. I am a Master Electrician and have worked on many UPSs'. Remember that if you keep a UPS loaded to it's full potential (which you shouldn't do) it will get hot. The rule is to only load it up to 80% of it's rating and you will be fine. To find out how many amps it will handle you simply devide the VA of the UPS by the supply voltage. Example: 1200va UPS supplied by 120v. is good for 10 amps. 1200/120 = 12 amps, then it is wise to add 25% more to the watts or amps when sizing them. Also, if it has a cooling fan make sure it isn't blocked by lint and is working, if it isn't working it will get hot fast. Good luck!
Nov 10, 2009 | MGE UPS Galaxy 3000 UPS System
Rectifire internal fault
the mge galaxy 3000 ups dont start atall when switch to normal position
Apr 06, 2009 | MGE Galaxy 3000 UPS System
MGE Galaxy 3000 UPS shows charger internal fault .
mge galaxy 3000 battery circuit breaker shut off when normal power shut off too.plz help !!!!!!
Jul 29, 2008 | MGE Galaxy 3000 UPS System
MGE UPS Galaxy 3000 UPS System Logo
Top MGE Computers & Internet Experts
Raj Patel
Are you a MGE Computer and Internet Expert? Answer questions, earn points and help others