Question about Spa Parts Plus GFCI, Circuit Breaker, 30 Amp
50 amp GFCI breaker trips after spa runs for 45 mins or trips after 5 mins if jets are turned on.10 year old cal spa. I found leaks and fixed all of them, but breaker still trips after same amount of time.
    President:
  • 1,730 Answers
More than likely, it's the element. They begin to 'leak' small current as they get old and this will trip the GFCI
If you need further help, I’m available over the phone at https://www.6ya.com/expert/craig_3fa289bf857b1a3c
Posted on Jul 11, 2009
I just wired my hot tub into my new house. And GFCI keeps tripping?
Still would go with Miswired.
if this is an auxiliary GFCI Spa Disconnect,
240 VAC, 50 Amp, then...
All of the following needs to be this way:
  • 4 wires from MAIN Circuit panel, into GFCI disconnect box, 2 hots, 1 Neutral, 1 ground
    • 2 hots go onto the disconnects Power Bus Bar for breaker
    • 1 white Nuetral goes to Isolated nuetral bus bar
    • 1 green Ground goes to ground lug directly on the box
  • 1 GFCI in the auxiliary disconnect box
    • The White Pigtail of the GFCI Breaker goes onto the Isolated Nuetral bus bar. There are now two wires there.
  • 4 wires come into box from Spa. (Unless the spa is Specifically a 3 Wire Connection Spa!)
    • 2 Hot/Line wires will go into the L1 & L2 lugs of the breaker respectively.
    • 1 White Nuetral Wire will go into breaker as well at the "Load Nuetral lug, usually marked as 'LN'.
      • It will NOT go on the Isolated Nuetral bus bar.
    • Green Ground wire will be connected to ground lug, 2 wires are now connected there.
  • Connections at spa will be respectively connected: the 2 hots on line 1 and line 2. White wire goes to Nuetralnd green ground will go to a Ground Lug, most likely to metal control box.
If it's not wired in this manner, it is wired WRONG.
May 27, 2015 | Electrical Supplies
Spa blower trips gfi
call an electrician to do an insulation check
insulation will eventually break down under ground normally from ants eating it
Mar 09, 2017 | Pool & Spa
Qo260gfi not tripping
Question is not fully clear.
2-pole 240Volt gfci circuit breaker requires the white wire be connected to neutral busbar.
Easy solution for 240Volt spa that comes with gfci:
Replace spa gfci with regular non-gfci breaker.
Install 2-pole GFCI breaker in main panel, and connect wire to spa breaker.
http://waterheatertimer.org/How-to-wire-GFCI.html#2-pole-gfci
Having 2 breakers is not a problem.
Having 2 GFCI on same circuit is a problem.
If you need further help, I’m available over the phone at https://www.6ya.com/expert/gene_9f0ef4df2f9897e7
Apr 18, 2013 | Pool & Spa
Why is the gfci tripping on my hot tub after being on for 30 min. After resetting the breaker after the 30 min. run, it trips immediately!!!
You will want to make sure that all of your spa equipment is functioning properly. It is best for a spa technician or electrician to determine this issue.
It is likely that a particular piece of equipment is turning on around the 30 min time frame and causing the breaker to trip. Pump, ozonator or similar. Also check the heater element, a pin sized hole in the element will cause it to fail. Lastly your spas breaker itself could be bad.
Nov 20, 2012 | Pool & Spa
My breaker is conected to a hot tub. tub was working fine in auto mode. Turned on jets and breaker tripped. will not reset can you help me
I am assuming this is a GFCI circuit breaker? If it is it will have a "test" button on the breaker. When you say "jets" i'm assuming you mean when you turn on the blower to make the air bubbles? It could be you have a problem with the blower motor. When you start the blower, it trips the breaker. Be sure the blower is in off position when you reset the breaker. The most common fault though on a spa/hot tub is with the heater. If the element goes bad, and current flows to ground, it will trip the GFCI breaker. Again try and turn all functions off. Reset breaker, and then turn on one at a time till the breaker trips. First the pump, then the heat, then the blower.
Oct 06, 2010 | Square D Trilliant 40 Amp Circuit Breaker...
Gfci breaker keeps tripping
sometimes gfi outlets go bad and trip try testing with a heavy draw machine in it or just replace it and see if this fixes the problem
Jun 22, 2009 | Balboa Instruments Duplex Digital Panel 2...
Gfci breaker for spa
gfci's are designed to trip if they receive voltage on there ground/neutral side, therefore my vote is for Smithbrother I would say there is probably a partial short somewhere in you system.
Mar 15, 2009 | Spa Parts Plus GFCI, Circuit Breaker, 30...
Spa Parts Plus GFCI, Circuit Breaker, 30 Amp Logo
832 people viewed this question
Top Spa Parts Plus Electrical Supplies Experts
Craig Butler
Craig Butler
Gene Haynes
Are you a Spa Parts Plus Electrical Supply Expert? Answer questions, earn points and help others