The unit does not come on however there is power to the unit and the blower for the furnace is working
  • annac_22 Jul 11, 2009
    There is power at all connections in and out.
  • t1m130
    t1m130 May 11, 2010
    there is power going to the contactor but is there power coming out of it is there 24v at the contactor
    Champion:
  • 233 Answers
Have you verified line voltage to the line side and load side of the contactor? is the contactor pulled in when there is voltage to it? if you have line power but no load pwer, and the contactor has 24v to it replace the contactor.
Posted on Jul 12, 2009
Screen went blank looks like this hard wired for power ac unit has power but won't come on due to thermostat not working
T-stat take batteries? The furnace should/may have a circuit board which should have a 3 to 5 amp fuse that is/may be open. You can try checking that first. If the fuse is open there is probably a short in the control wiring or components. Check the wires at the o.d. unit(small control wire). Chewed on, pulled on, sun baked? If you see any lights on the board, with the furnace powered up, then its not the fuse. Jump R to G at the tstat, should start the cooling, blower or both. If it works by jumping replace the tstat. Work safe!!!
Aug 03, 2015 | Heating & Cooling
Suburban rv furnace.
The best thing to do for these units is replace the ignition module, on Ebay they are cheap usually. Clean all orifices where any pressure switches or tubing connects on the induced drafts assembly, Does the pilot ever light?
Dec 09, 2013 | SUBURBAN MANUFACTURING Rv Motorhome...
Where is the switch to the furnace to shut blower off?
There is a switch, activated when you open the service panel, that kills most power to the unit, including the DI Blower motor. Your furnace should also be equipped with an exterior kill switch, or there's always the good old breaker box. Good Luck!
Mar 15, 2013 | York Furnace Draft Inducer Blower Fasco #...
Auto fan does not start electric furnace
see this causes and fix it. God bless you
If the furnace won't run, check the electrical service panel for a blown fuse or tripped breaker. Also make sure the power switch on or near the furnace is turned on. Check the unit for a reset button and try it. Some units have a built-in breaker or fuse panel.
If there is not enough heat, raise the thermostat setting five degrees to see if it turns the unit on. If the unit still does not generate enough heat, check the comfort controls . Clean or replace a dirty filter, clean the blower assembly (see the Forced-Air Distribution Fix-It Guide), and make sure that all registers are open and not blocked.
If the furnace turns on and off repeatedly (cycles), clean or replace the filter; and clean the blower assembly (see Forced-Air Distribution Fix-It Guide).
If the furnace is noisy, make sure access panels are mounted and fastened securely; spray squeaking belts with fan-belt dressing and replace worn or damaged belts; adjust the blower belt; lubricate motor and blower oil ports.
If the element does not heat, refer to the Heating Element Fix-It Guide for guidance.
Oct 08, 2012 | Coleman Mobile Modular Home Electric...
Removing furnace blower fan
1)Flip the furnace circuit breaker to the "Off" position to turn off the power to the furnace unit.
2) Press in the release button and pull the door off.
3)Remove the nut holding down the control panel of the furnace unit using a 7/16 socket wrench. The control panel is often found below the burners of the unit. Let the control panel hang in place.
4)Remove the two nuts holding the blower assembly in place with a 7/16 wrench. Lift the blower out.
5)Remove the bolts holding the assembly together and remove the fan from the unit.
Jul 22, 2012 | AO Smith Lennox Furnace Motor P-8-6426 3/4...
Why two 24 Vac on aprilaire 700's control unit?
Okay, I looked up the installation manual online to see exactly what you are working with.
Yes the R anc C need to be hooked to the transformer supplied with the unit. The primary 120v side needs to be hooked into the power coming into the furnace. this can easily be done were the L and N get hooked into your furnace or circuit board on the furnace. This will provide the contiuous power to the unit. Preferably you will hook this after the door switch of the furnace so that you will kill the power toit if you take the blower door off.
The ODT terminals are for the outdoor sensor if you want to hook that up it will vary the humidiy in your home according to the outdoor temperature then.
Now the W/G and Cf terminals. If you have 24v coming from the HUM terminals of your furnace you DO NOT need a second transformer. You must check your furnace manual or check the voltage to them with the furnace blower energized. The HUM terminals will only have power to them when the blower should be running.
If the HUM terminals are 120v then you need to get another transformer and hook up the primary side to the HUM terminals so it is powered only when the the blower is running. Hook the secondary side to the W/G and Cf terminals.
So bottom line is that you need to figure out what voltage your furnace is giving to the HUM terminals and then go from there. Some times the EAC terminals or the ACC terminals will be 24v on the furnace board. Either of them could be used also, as they are only energized when the blower is running also.
Heatman101
Jan 25, 2010 | Aprilaire 700 Humidifier
1994 Carrier 58 PAV
sounds like the relay for the unit may be bad, usually if a blower motor goes it stops or has a very loud humm and only goes slow
Aug 03, 2009 | Heating & Cooling
AC unit turns on blower doesn't come on
The thermostat is the controller.
Jun 19, 2009 | Heating & Cooling
My blower motor will not stop running,and my ignitor doesn't light.
I am assuming you are talking about a Natural Gas or LP furnace. The blower motor is powered by a separate 120 volt circuit, so flipping the 240 volt breaker for the furnace will not shut it off. There should be a regular light switch at the furnace that will turn off the blower for servicing the unit. When you take the cover off the unit, there should be instructions on how to re-set the igniter. If it won't re-set, try shutting off the gas for a few minutes, then turn it back on and then reset. If none of this works, and you can't find the owners manual, call a service technician.
Feb 22, 2009 | Electric Circuit Breaker Kit for Furnace
Furnace blower motor turns on with no flame burning
Hi!!! You might have a bad flame sensor its a single rod located in the burners its white..If the unit runs and then shuts off and on and off.change your flame sensor..Good luckk..
Jan 04, 2009 | Honeywell Power Humidifier: Furnace...
Heating & Cooling Logo
Top Heating & Cooling Experts
Paul Carew
Marvin
Marvin
john h