Where do i find the expansion valve on a 3.5 ton trane air handler. Model no of the trane air handler is: 2TEC3F42C1000AA
I looked on the evaporator core trace the big line, just could not find the expansion valve. can it be hidden somewhere?
    Master:
  • 456 Answers
Heat pump units have check valves and/or flow restrictors, maybe an expansion valve in each, the condensor and evaporator, you cant find the expansion valve, then there should be some sort of distributor, small copper lines into the coils.
Posted on Apr 30, 2015
    Legend:
    An expert who has written 200 answers of more than 400 characters.
  • 484 Answers
The TXV (thermostatic expansion valve) is always at the end of the high pressure liquid line as it enters the evaporator. This is the small line. The outlet of the TXV will usually have 4, 6 or 8 smaller lines feeding proportional portions of the evaporator coil. You have to remove the cover of the evaporator to access it.
Some units do not use a TXV, so you may have a 'fixed restrictor' instead. It too is located where above described.
Posted on Apr 28, 2015
Trane 4TEE3F39A1. What is tonnage?
Your Trane air handler is capable of managing evaporative units up to 3 tons.
Mar 06, 2016 | Heating & Cooling
Why does my A/C condenser compressor turn on and off every 5 minutes?
You need good airflow across the indoor coil, the evaporator. Air warms the refrigerant. If there is no airflow, the refrigerant will come back out freezing cold (in liquid form) and can damage the compressor valves. Before charging any ac unit, good airflow must be checked for across both evaporator and condensor.
Too much, overcharging will cause freezing all the way back to the compressor in a capilary tube type of ac.
Where is it the refrigeration lines are freezing cold?
Apr 28, 2015 | Heating & Cooling
Why is my A/C condenser compressor overheating, causing compressor to turn on and off every 4 minutes?
THERMOSTATE SIGNAL SHOWING OVER HEATING AND NOT RUNNING NORMAL ,HENCE OVER HEATING TRY CLEANING MAY HAVE DUST OR IT COULD BE THERASTSATE TO CONTROL AIR TO COOL
Apr 27, 2015 | Heating & Cooling
What is the problem with running a 10 SEER condenser with a 13 SEER air handler other than efficiency? I had a 2 ton 13 SEER air handler installed last August to replace one about 27 years old. The...
as most ac units are capillary tube control not tx valve having matched units is critical. as for cost the condensing unit is much more complex and expensive than the evaporator.
Feb 14, 2015 | Amana Goodman R-410A Heat Pump Condenser 2...
Low to zero pressure on low side test port
150 is low for high side pressure. may have to add more r-22 to system. if you had a blockage high side pressure should be higher. have you turned both service valves at condensor ccw completely?
Apr 20, 2014 | Goodman CKL42AR42 Air Conditioner
Determining the age and size of a Trane evaporator Model # TXH054A4HPAF
The serial number on that evaporator will have the date code in it, the model will tell the capacity (size). It looks like it is a 4 and a half ton or 54,000 BTU coil and has a TXV valve to meter the refrigerant.
Jun 16, 2011 | Ruud UAKA037 Air Conditioner
I have a Ruud Model # UACC-036JAS. Any idea on
Hi, yes the number you are showing me 036 indicates its a 3 ton unit. For every ton of cooling, you will have 12,000 btu's of cooling. 36 divided by 12=3 ton unit. Its showing me also its a Ruud Handler 2.0 ton which would be a Model# UACC-024JAS? If your mobel number is the one you gave me, UACC-036JAS, this is a 3 ton unit, absolutely no questions. I hope I have been of help to you. I am a licensed air conditioning / Refrigeration /Heating Contractor. Let me know if I have been of help.
Sincerely,
Shastalaker7
PS If this is a split system with the indoor air handler and condenser outdoors, both coils must be the same tonnage for it to work for you properly. You can't have a 2 ton indoor evaporator coil with a 3 ton condensing unit.
Jun 28, 2010 | Ruud Handler Air Conditioner
Hello i want to conect a trane condensator 2twb0036a1000ba to a trane evaporator mww536k10raa i need a wiring diagram
Your wiring concerns may be more with the thermostat wiring connections than the condensor connections. if you look inside the cover of the evaporator unit (usually called air handler) there should be a wiring diagram glued to the panel cover. This diagram will show all 3 units (stat,cndsr, airhndlr) and the wiring needed between them. Trane and Lennox are notorious for having the most wiring between components. You also need to be sure the stat is the correct type for the system (i assume this is a heat pump system) and there can be as many as 9 wires from stat to system and 6 wires from inside to outside units. Also, the stat will have a wiring diagram with it that shows most typical system wiring including the wiring between in and out units. Your best bet (if you have no diagram on the unit or with the stat) is to call trane and have their tech division fax a diagram to you. Goodluck,Macgivor
Jan 27, 2010 | Heating & Cooling
3 ton condensor and 2.5 air handler
I hate to use rules of thumb but 500sqft per ton depending on your windows and insulation. you are probably ok with a 2.5 ton however it will not work with a 3 ton outdoor unit as you have figured out. depending on how long that ac has been in you may want to replace it with a 2.5 ton due to the damage to the compressor valves because of the mis match. or if the indoor is newer and the original system may have been a 3 ton then i would replace the A/H. and be prepared to replace the outdoor if the valves are to far gone. If the trane is a new high effiency 2 and the goodman is just a 10 SEER you may be able to have a txv installed on the trane unit and a kickstart device outside. but only if its a high effiency but their again if the A/C fails you couldnt have a high effiency 3 ton you would have to drop down to 2.5,
Sep 22, 2009 | Heating & Cooling
Btu's
That air handler can accamodate different size coils. Look for the coil model number. Also you can look at the outdoor unit model number they should be matched up. There is generally a set of 2-3 numbers in the model numbers that will tell you. xxx036xxx is 36,000 btu. tonnage is 12,000 btu per ton so 36,000 btu's would be 3 tons. xxx040xxx= 40,000btu's or 3.5 tons etc.