Furnace blower runs for a minute then shutdowns- no heat
Their must be an interlock that shuts down the blower if it doesn't see a flame. Does this model have a pilot light or electric spark. It was working fine.
  • Edward Ventura
    Edward Ventura Apr 17, 2015
    Where is the ignitor located on a 600315.321and how do you replace it.
  • 2,533 Answers
If the flame does not come on it could be the igniter needs replacing. Some times if everything is set to go but if the flame does not light up then it automatically shuts down again. It is common to have to replace igniters.
Posted on Apr 17, 2015
Heil nulk075dg05
You have a dirty or bad heat sensor. When you remove the front panel on you furnace you will see a probe that is 2 or 3 inches long that is in the flame when the furnace fires up. If it doesn't detect a certain temperature within the first 30 or 40 seconds it shuts down the furnace. You can either clean the probe off with sandpaper, or purchase a new one. They aren't very expensive and are easy to replace. In my experience it is usually a build up of carbon on the sensor and a good cleaning with sandpaper and alcohol usually takes care of the problem.
Feb 04, 2014 | Heating & Cooling
Furnace stops before house warms up
This could be due to a fault in the temperature limit switch
Jan 26, 2013 | Gibson Tappan Frigidaire Furnace Control...
My furnace blower shuts off after 20 seconds of running
Could be a defective flame sensor and/or thermostat
Feb 23, 2018 | Heating & Cooling
Ruud 90+ Model UGRA 10EZAJS Trips Out
Check for condensation buildup in the Induction Blower housing. The condensate tubes or canister may be blocked and causing the diaphragm switch to trip the unit out causing the burners to shut down.
Feb 11, 2012 | Ruud Heating & Cooling
Ruud furnace Model URKA A030jK08 Code opt 589
Flip the lower panel over and look for a wiring diagram. On that diagram there will be a diagnostic chart. Let me know what 5 blinks represent. Then I want you to read on.
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
Nov 23, 2009 | Heating & Cooling
Weatherking furnace is starting and stopping
This just sounds like a couple of problems. First, your blower is designed to only turn on once the heat exchanger heats up, so the flame will be on for a minute or two before the blower starts. it sounds like your blower is cooling down the heat exchanger too fast and causing it to shut off so it can warm up again...check blower speed for heat, it should be the lowest speed (black wire). Blue=medium speed, red= high speed. second problem could be your flame sensor rod is calcified, you just need to locate this and clean it off with some fine sand paper.it is located in the flames near the burners. Also change your filters, for proper air flow through your heat exchanger.
Oct 28, 2009 | Heating & Cooling