It sound like your first stage sequencer is stuck in the 'on' position Shad. Usually the first stage is responsible for turning on the blower on low speed while energizing the first 5 kw of electric heat.
The problem you describe is typical of 'stuck' contacts within the sequencer.
No field service to the sequencer, replacement is necessary. Of course without actually seeing your furnace, this is just a resonably educated guess.
Posted on Oct 01, 2015
Therinnaiguy
  • 1420 Answers
SOURCE: Coleman furnace blower runs continuously
You should be seeing 120 volts to the igniter. Anything less requires either a replacement of the transformer, start relay or control module.
Posted on May 30, 2008
  • 6 Answers
SOURCE: coleman evcon Dgato7obdc
Small blower motor? Are you talking about the combustion blower if so then check your vents for blockage.. if the vents are blocked won't work... if it has a control board init it will give you a diagnostic code. Flashing light on the board... count the flashes and look up the fault on the chart in your owners manual ot on the furnace door..
Posted on Jan 15, 2009
  • 3 Answers
SOURCE: coleman evcon dgat090bdd. New ignitor won't heat up.
Looks like 4 flashes might be high limit fault on this furnace. (I don't have a manual for this furnace, just searched online for the code meaning) Is the unit running flame at all? Is the unit running flame for a while then shutting flame off before desired temp is reached? Does the main air fan turn on to circulate air through your diffusers? Does it feel like the unit has much air flow out of the diffusers if the fan is running? Is your air filter clean? If it is infact your high limit switch, it is usually caused by not having enough airflow through the furnace and overheating occurs.
Hope this helped, let me know if I can assist you further :)
Posted on Jan 16, 2009
  • 8 Answers
SOURCE: wiring from thermostat to furnace
Typically you normally will have five wires controlling your furnace and airconditioning. R Y W G C. If you get some thermostat wire. Connect them like this---- red wire will go to R(this is your 24V to thermostat)----yellow wire will go Y(Y is your cooling)----white wire will go W(W is for heating)---green wire to G(green is your fan)---black can go to C(this is your common to supply 24Vto thermostat)
Posted on Jan 19, 2009
  • 221 Answers
SOURCE: Coleman Evcon..... Inducer Adjustment
Just wanted to make sure you knew this model is on a recall list:
http://www.dgatprogram.com/
Posted on Jan 02, 2010
Coleman Evcon EB15B heat doesnt stop when it reaches the temp set on the themostat just gets hotter and hotter until I shut it of at the circuit breaker
Thermostat not doing it's job.
Probably the contacts on the thermostat are stuck together, Caused by arcing each time it opens.
If you are up to it.... clean the contacts or replace thermostat,
Cheers
Mar 03, 2015 | Heating & Cooling
Coleman/ Evcon central electric furnace Eb15b thermostat on auto will not blow air out i hear a click u see and feel it heating up then i hear Another click dont see nor feel heat then but put thermostat...
check the thermostat setting on back for electric heat. sounds like it is on gas heat. the fan should turn on right away if it is electric or heat pump.
Nov 15, 2014 | Heating & Cooling
Evcon eb15b
thermostat, heat sequencer or contactor, no 240 volt power no 34 volt power
Nov 23, 2013 | Coleman Heating & Cooling
I have a coleman evcon model eb15a furnace. it does not work with the therostat, if you turn the main breakers on the fan and one elament come on the fan auto/continuious run switch doest work either any...
Hello, have you tried jumping the R and W wires on the thermostat sub base? If this turns on you furnace than the thermostat is bad, however if there is no display on the thermostat and does not power up by jumping the R and W Wires then most likely the transformer is bad and must be replaced.
Mar 16, 2011 | Coleman Heating & Cooling
My Coleman Evcon heating and air unit will not blow air
bad blower motor. recommend a new blower motor and capacitor.
May 28, 2010 | Coleman Heating & Cooling
I have a coleman/evcon heat pump. When the thermostat kicks on the contacts kick in and hum but the compressor nor the fan run. Is this probably my capacitor has gone bad?
I would check the hig voltage power supply to the unit. Check the main breaker and make sure it is on. Check the disconnect and make sure there is power at that point to the condensing unit. The contactor will kick in from the low voltage in the control circuit.
Jul 11, 2008 | Coleman Heating & Cooling
Dec 19, 2007 | Coleman Propane Forced Air Heater...
Heating & Cooling Logo
87 people viewed this question
Top Coleman Heating & Cooling Experts
Bill Long
paulcarew
Dan Webster
Dan Webster
Are you a Coleman Heating and Cooling Expert? Answer questions, earn points and help others