York gas furnace pilot lights and begins heat cycle but burner quickly goes out and system continues to run blowing cold air
  • Heating & Co... Master
  • 9,742 Answers
There is a flame sensor that holds the gas valve open when there is a flame present. Heat generates about 10 to 15 milivolts to do this. Make sure the side of the flame is touching the sensor. If it looks ok Tighten the fitting that holds the sensor to the gas valve. If it still won't stay lit after all that then replace the sensor. They do fail with time.
Posted on Mar 30, 2015
Tempstar DC90 pilot light or burner keeps going out. The furnace will run continuously. Even if I turn heat off at the thermostat. I have to kill power at the panel box to get it to shut off. Then I've...
The reset button near the ignitor is a high temperature limit safety switch. When the furnace gets too hot and the manual reset limit switch is tripped, it most likely goes into a 'safe' mode where the gas control is locked out electronically and the blower is made to run continuously to rid the heat exchanger of the excessive heat. This will continue until the reset is pushed and the power is cycled off. It will remain an endless cycle unless the reason for the overtemperature condition is not corrected.
Your furnace 'temperature rise' is getting too high due to a lack of air across the heat exchanger for whatever reason. Some of those reasons could be a restricted air filter or a blower motor that's cycling improperly on its internal winding thermostat. You could also have a dirty air conditioner 'A' coil (evaporator) on top of the furnace restricting the air flow. Nevertheless, you are going to have to have it serviced by a reputable service company's technician to correct what's wrong.
Nov 13, 2014 | Heating & Cooling
Old anthes gas furnace with pilot light. burners will not light.blows cold air
Have to think that the thermocouple has failed if the pilot is on but the furnace main burner doesn't ignite
Apr 05, 2014 | Cozy (W352E) Heater
Light pilot reset
If yours is a high-efficiency furnace, you should hear the stack blower start running when your thermostat calls for heat. Next, the igniter should start to glow and remain glowing until the thermocouple opens the gas valve and allows gas to flow to the main burner. The main burner lights and burns until sufficient heat is generated for the main blower to turn on and blow warm air through your house. If any action does not occur in the order described, repairs are in order.
Dec 08, 2013 | Kitchen Appliances - Others
I have an older Carrier furnace type 58ss. The main burner will not ignite. Operating look ~ thermostat set @ 78 deg, switch furnace on, inducer fan running, pilot light clicks and ignites, inducer still...
power to gas valve ok .. Replace gas valve after checking gas valve coil for continuity/resistance... with valve removed ...and power to valve ... try blowing thru valve from supply side ... stuck valve.... replace...
Nov 01, 2013 | Heating & Cooling
Amana furnace not blowing hot air
My heating system is running so well because I have Amana furnace.
Nov 09, 2012 | Heating & Cooling
York Diamond 90 furnace blows cold air
There maybe a few issues. They have multiple safeties on furnaces. With this in mind this process to find the problem would take a Technician to check these safeties. It could be a flame sensor or thermocoupler each senses a flame or heat to keep the gas going. Also the damper for the flue must open for the gas to stay on. There may be more safeties on this and each safety sends a 24 volt current back to control module in order for the gas valve to stay open. If these aren't being met it will try around three times and go into a lock out mode which will keep gas shut off entirely.
Feb 21, 2012 | Heating & Cooling
Lennox Model G12Q3-82-1 Gas Furnace pilot light extinguishes each time butrner cycles off afrer heat cycle
Hello,See if it is blowing out.Relite the pilot and run the fan(blower) with out the main burner running.A cracked heat extanger will be the cause if it blows out.
Oct 29, 2010 | Heating & Cooling
Having a problem with a goodman gas furnace, pilot starts and burners fire up, blower starts and burner goes out after like 5-10 seconds. Blower continues to run but only circulates cold air. burner does...
Sounds like the rollout is being tripped from the blower moving the falmes. i would have your heat exchanger checked for cracks or holes as this is usually the reason the blower moves the burner flames to tripp a rollout.
Feb 22, 2010 | Heating & Cooling
Having problems with Carrier 58RAV furnace. Goes through the motions, but gas never turns on. I think it is a problem with the LPGS. Please advise. Thanks
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
Dec 24, 2009 | Carrier Heating & Cooling
Furnace blowing cold air
Nordyne Furnace, pilot is lit, thermostat is reset, Heater is on but blowing cold air.
Mar 28, 2009 | York Furnace Draft Inducer Blower Fasco #...