Anonymous Posted on Feb 10, 2015

Gas valve will onley open when I put ajumper wire on limit switch

1 Answer

Happy Valley Air Care LLC

Level 2:

An expert who has achieved level 2 by getting 100 points

All-Star:

An expert that got 10 achievements.

MVP:

An expert that got 5 achievements.

Novelist:

An expert who has written 50 answers of more than 400 characters.

  • Expert 199 Answers
  • Posted on Feb 15, 2015
Happy Valley Air Care LLC
Expert
Level 2:

An expert who has achieved level 2 by getting 100 points

All-Star:

An expert that got 10 achievements.

MVP:

An expert that got 5 achievements.

Novelist:

An expert who has written 50 answers of more than 400 characters.

Joined: Dec 24, 2012
Answers
199
Questions
0
Helped
61962
Points
316

You will need to replace the limit switch if it has stopped working. But if it is still working, it is protecting you against over temperature conditions and is part of a safety circuit. One the biggest causes for limit switches to open is the lack of air flow due to blocked coils, dirty filters or improperly operating fans. You should never operate a furnace with a safety circuit overridden.
You mentioned it started when jumpering a safety switch, if it is the flame rollout switch then most rollout switches have a reset button between the leads on the switch. Reset the switch is easy and should allow the furnace to restart. The rollout switch detects just that excess heat coming backward into the flame sword area. Some causes for this to occur is cracks in the heat exchanger, the induction fan deteriating so the flue gasses are not exhausted properly, or a blockage in the flue gas path. Blockage can be caused by excess rust buildup in the tubing, dirt dawber nests, and any number of other obstructions.
Any way you need a professional to determine the cause for the limit switch opening.
Hope this helps.

Add Your Answer

×

Uploading: 0%

my-video-file.mp4

Complete. Click "Add" to insert your video. Add

×

Loading...
Loading...

Related Questions:

0helpful
1answer

My Carrier WeatherMaker 8000 furnace is blinking a red light 2 times pauses then blinks red 4 times with a pause between the 4 times

They are listed inside the front panel of the main unit.
LED CODE
EACH OF THE FOLLOWING STATUS CODES IS A TWO DIGIT NUMBER WITH THE FIRST

DIGIT DETERMINED BY THE NUMBER OF SHORT FLASHES AND THE SECOND DIGIT BY
THE NUMBER OF LONG FLASHES.
STATUS

11 NO PREVIOUS CODE - Stored status code is erased automatically after 72
hours. On RED LED boards stored status codes can also be erased when power
(115 VAC or 24 VAC) to control is interrupted.
12 BLOWER ON AFTER POWER UP (115 VAC or 24 VAC) -Blower runs for 90
seconds, if unit is powered up during a call for heat (R-W closed) or R-W opens
during blower on-delay.
13 LIMIT CIRCUIT LOCKOUT - Lockout occurs if the limit or flame rollout switch is
open longer than 3 minutes.
- Control will auto reset after three hours. - Refer to #33.
14 IGNITION LOCKOUT - Control will auto-reset after three hours. Refer to #34.
21 GAS HEATING LOCKOUT - Control will NOT auto reset.
Check for: - Mis-wired gas valve -Defective control (valve relay)
22 ABNORMAL FLAME-PROVING SIGNAL - Flame is proved while gas valve is
de-energized. Inducer will run until fault is cleared. Check for:
- Leaky gas valve - Stuck-open gas valve
23 PRESSURE SWITCH DID NOT OPEN Check for:
- Obstructed pressure tubing. - Pressure switch stuck closed.
24 SECONDARY VOLTAGE FUSE IS OPEN Check for:
- Short circuit in secondary voltage (24VAC) wiring.
31 PRESSURE SWITCH DID NOT CLOSE OR REOPENED - If open longer than
five minutes, inducer shuts off for 15 minutes before retry. Check for:
- Excessive wind - Proper vent sizing - Defective inducer motor
- Low inducer voltage (115VAC) - Defective pressure switch
- Inadequate combustion air supply - Restricted vent
- Disconnected or obstructed pressure tubing
- Low inlet gas pressure (if LGPS used)
If it opens during blower on-delay period, blower will come on for the selected
blower off-delay.
33 LIMIT CIRCUIT FAULT - Indicates a limit, or flame rollout is open. Blower will
run for 4 minutes or until open switch remakes whichever is longer. If open
longer than 3 minutes, code changes to lockout #13. If open less than 3 minutes
status code #33 continues to flash until blower shuts off. Flame rollout switch
requires manual reset. Check for: - Restricted vent
- Proper vent sizing - Loose blower wheel - Excessive wind
- Dirty filter or restricted duct system.
- Defective blower motor or capacitor. - Defective switch or connections.
- Inadequate combustion air supply (Flame Roll-out Switch open).
34 IGNITION PROVING FAILURE - Control will try three more times before lockout
#14 occurs. If flame signal lost during blower on-delay period, blower will come
on for the selected blower off-delay. Check for: - Control ground continuity
- Flame sensor must not be grounded
- Oxide buildup on flame sensor (clean with fine steel wool).
- Proper flame sense microamps (.5 microamps D.C. min., 4.0 - 6.0 nominal).
- Gas valve defective or gas valve turned off - Manual valve shut-off
- Defective Hot Surface Ignitor
- Low inlet gas pressure
- Inadequate flame carryover or rough ignition
- Green/Yellow wire MUST be connected to furnace sheet metal
45 CONTROL CIRCUITRY LOCKOUT Auto-reset after one hour lockout due to;
- Gas valve relay stuck open - Flame sense circuit failure
- Software check error
Reset power to clear lockout. Replace control if status code repeats.
If status code recall is needed, briefly remove then reconnect one main limit wire to display
stored status code. On RED LED boards do not remove power or blower door before initiatingstatus code recall. After one status code recall is completed component test will occur.

here is a link copy and paste

https://www.fixya.com/support/t6287232-carrier_8000ts


.
0helpful
1answer

Furnace problems

On - OK
1 Blink - Ignition failure. Check Gas flow, gas pressure, gas valve, flame sensor.
2 Blinks - Closed pressure switch. Check pressure switch (stuck in closed position).
3 Blinks - Pressure switch - failre to close. Check venter, pressure switch, vent blockage.
4 Blinks - Open limit switch. Main limit or aux limit are open. (My comment - Means overheating in chamber. Often result of blocked intake air. Bad filter. In my case, plastic wrap had been sucked into the intake. )
6 Blinks - False flame sensed. Check sticking gas valve.
Rapid continuous blinking - Incorrect twinning, incorrect primary polarity. Reverse transformer secondary leads, reverse primary wires.

Closed pressure switch can be from dirty combustion vents, bad chamber pressure - like missing screws, maladjusted gas pressure, failing pressure switch, loose hoses, moisture in the hoses or fan blades The switch need to be closed to ge the unit to work
0helpful
1answer

I have a 15 year old York 80 diamnond unit and i have four flashes which tells me to open up limit? how do i do that? thanks.

A limit switch opens when the heat exchanger gets too hot. To check the switch with a meter turn the power to the furnace off, then disconnect the wires from the switch and set a meter to resistance, if the switch is open the meter will indicate infinite resisitance. There are several reasons why a limit switch opens and some of those reasons are
1) dirty air filter
2) the gas pressure on the gas valve is set too high
3) a problem with the blower motor
1helpful
1answer

I have a paragon 8145-20 defrost timer. do you wire the compressor to the timer? I cant seem to find a wiring diagram on how to wire this correctly

Link below has wiring diagrams and wiring manuals for 240V 8145-20
http://waterheatertimer.org/Paragon-timers-and-manuals.html#defrost

I am not expert installing defrost timers.
According to information from Paragon, 8145 is for hot gas defrosting. 8140 series are time initiated, and pressure-or-temperature terminated.
Wiring diagram does not show compressor wired to timer.

The cycle works like this:
Timer is running but defrost is not switched ON.
Fan is ON.
Timer switches ON and activates defrost cycle.
Fan turns OFF. Hot gas valve turns ON for defrosting.
Cycle limit switch is temperature or pressure sensitive.
Cycle limit switch reaches trip point, timer switches OFF.
Hot gas valve turns OFF. Fan turns ON.
So fan is off during defrost cycle.
Hot gas valve turns ON when timer switches ON.
Timer is switched OFF by pressure-or-temperature limit switch.
0helpful
1answer

Its won't light. The flame is there but won't light up.

Sounds like you have and open limit switch trace the wires from the gas valve one will go straight to the terminal board the other one will go through all the safety limits take an ohm meter (an ohm meter beeps or lights up when you touch the leads together showing a direct connection also called continuity) and check each limit switch by touching one of the meters leads to one wire on the switch and the other meters lead to the other wire on the switch if no continuity is there your switch is open some switch's have little reset buttons on them. Find the open switch and reset or replace.controlltech_9.jpg

0helpful
1answer

Heater exhaust blower comes on ignitor lights but it doesn't seem to get gas everything works but no flame and blower won't kick on the unit is brand new and was working this morning then stopped

This furnace should have a trobleshooting diagnostic led flashing light. Each blink (for example 3 blinks means open limit switch) has a particlur meaning. On the bottom panel has an explaination on what the blinks mean. But in the meantime check 24v at the gas right as the ignitors light. If you have 24v and the gas valve doesnt let the gas thru then the gas valve might be defective. I usually put 24v dircetly to the gas valve for 2-3 seconds to see if gas will come out. It is loud enogh to hear as well as smell. If you dont have 24v as the ignitor tries to light then check the air pressure switch. Also follow the wire off the gas valve. One is to ground. Make sure the gas valve is grounded. Follow not the grounded wire but the other one. Find out where the 24v power stops.
0helpful
2answers

Intertherm MGH-056ABFC-91 won't kick on. Just changed thermocouple, gas valve, and thermostat this week. Changed fan motor, blower wheel, and limit switch last winter. Pilot is lit, thermostat is set. The...

At the furnace, jump the R and W (or T and T) terminals on the circuit board or gas valve. Make sure the door switch is closed with some electrical tape. By doing this we are forcing the unit to start. If it does fire, you have either a bad thermostat or a broken wire to the thermostat. If it does nothing, look for a bad fuse, check for 24 volts going to the gas valve, an open limit switch or 120 volts at the transformer.
0helpful
1answer
0helpful
1answer

Code continous flashing

If your igniter comes on but no ignition, that eliminates the possibility of a bad or clogged pressure switch, high limit or flame rollout switch. Sounds to me like you have a control board, or a gas valve going bad. Could even be some loose, corroded, or faulty wiring. Before the igniter comes on the furnace does a self diagnostics to ensure everything is working, or the furnace will not make it to the igniter sequence. Inducer motor, pressure switch/s, limit controls are closed…then comes on the ignitier, gas valve opens, pilot runners and burners ignite, flame sensor detects the flame, blower comes on and all operations are working.

Hope this helps
Not finding what you are looking for?

122 views

Ask a Question

Usually answered in minutes!

Top Heating & Cooling Experts

Paul Carew

Level 3 Expert

3808 Answers

john h

Level 3 Expert

29494 Answers

Brad Brown

Level 3 Expert

19187 Answers

Are you a Heating and Cooling Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...