How to regas a goldair air con unit
Split air con. i have vacuum pump, gas and gauges. pipes are red, yellow and blue. which pipes go were.
    New Friend:
    Problem Solver:
  • 5 Answers
Ok first the blue hose onto the suction line(the thicker of the two pipes)of the ac unit,the yellow onto the vacuum pump.the red hose not necessary.After vacuum is completed remove yellow hose from pump and put it on gas bottle now you ready to charge the unit
Posted on Dec 13, 2014
bobotfel
  • 236 Answers
SOURCE: Samsung split system air conditioner model as24bpa
Suction-5/8"
Liq. line-1/4"
Max pipe length-50'
Max vertical hight bet. accu and fcu-25'
Posted on Jan 11, 2008
bobotfel
  • 236 Answers
SOURCE: I have a Fujitsu Split
Try to disconnect the supply from circuit breaker for 10sec. and "on" again, if it doesn't work you need at qualified technician for that problem.
Posted on Apr 16, 2008
koolbreezes
  • 540 Answers
SOURCE: KELVINATOR KSR20C
One might think so, YES! look on one of the door panels that you can remove! Thank-you-very-much!
Posted on Aug 23, 2008
notsomot
  • 67 Answers
SOURCE: my split air con unit is leaking water from the unit in house
The things that you can check yourself are
is the indoor unit level?
Are the filters clean?
The area the water is draining to free of obstruction?
Is the drain actually draining?
----Get a cup of water and pour it over the indoor coil (please make sure the power is off first please) If the water does drain then it is prolly a bigger problem.
Prolly your unit is short of gas and need a refrigeration tech out to check. That it isnt ice-ing up but you would notice the performance drop.
Hope this helps
Posted on Jan 08, 2009
meBNme
  • 334 Answers
SOURCE: I am trying to regas a Panasonic CU-A24BKP5 split
OK, now we need to let the comopressor cool down if it is hot. Once it is cool, (that could take a while if it is so hot it tripped out on internal overload.) check for continuity between the compressor leads. If they show continuity between them hook the wires back up and turn it on, Check the amp draw at start up, and check the voltage to the compressor.
The compressor is bad If....
1) there is no continuity between the compressor leads.
2) if you have an amp draw but the compressor is still not pumping refridgerant.
If you do niot have voltage going to the compressor, then we will need to trace down the cuase for loss of power.
Posted on Oct 17, 2009
Where can I buy a regas kit for my split unit airconditioner I live on the Gold Coast
I've never heard of a regas kit for a split a/c system. You need a declaimer, a vacuum pump, the designated refrigerant, gauges, and a digital scale. Evacuate the system, when system holds a vacuum, look up amount of refrigerant and type from mfg. tag on unit of spec book. Add specified amout of refrigerant and your done. If noy familiar with pressure on gauges you can use an amp meter to ensure unit is not over charged or has a restriction which would cause higher discharge pressure and therefore high amperage. Best to call a tech. Cheaper and safer.,
Jan 01, 2015 | Sanyo 33,000 Btu Ductless Airconditioner
How do I replace a outside central air conditioner
First you need to determine if it is a heat pump or straight cool condenser. The reason is the low voltage wiring is different. This is the correct way to install an outside unit.
1.Pad must be level and unit should be secured to withstand 140 mile uplift wind with tie down straps.
2. Make sure breaker size does not exceed max per data sticker on unit. The electrical whip should also be correct wiring size for breaker AMPS.
3. Remove the shard er core valve to prevent damage to it, protect king valve with wet cloth or thermal trap paste to avoid damage. Connect the liquid line small cooper pipe to unit by brazing. Then run through gauges Nitrogen at low psi to prevent shoot build up in line set, now start brazing the suction line large cooper pipe, once finished help cool with water cloth.Check visually for any missed spots and re braze. Once you are comfortable that braze is a good seal now it it pressure test time.
4. (The above procedure is assuming that the inside unit has already been installed correctly, including the line set to unit.)
Through gauges connect Nitrogen compressed gas tank and increase psi in the line set to 350 psi and let stand ten minutes. If pressure is still 350 on both gauges you have a good seal, release the nitrogen into the air and remove tank from hose. Once gauges read 0 psi on both sides high and low you can start the vacuum process. These pressures can differ per refrigerant ( R410A example).
5. Hook up the Vacuum pump to the middle hose from gauges making sure you have replaced the shard er core valve back into the ports.tighten all hoses to any connection on machine, gauges, and pump open gauges and turn on pump allow to run at lest 20 minutes or until you reach 100 microns in a vacuum.Shut, close gauges and shut off pump remove the hose from pump.connect this hose to refrigerant tank and purge to center hose at gauges ( minus) amount of purge.
6. Now you can open the king valve and let refrigerant flow out of the condenser into the line set and air handler otherwise you have to add the refrigerant, newer refrigerant has to be charged into unit in the liquid state not gas state. R410A older refrigerant can be charged in gas state R22.
7. Hook up electrical,breaker off check with volt meter, follow diagram on unit. Then hook up low voltage, for straight cool depends on t-stat and unit witch colors they use follow schematics. I have found that Goodman use blue as common and yellow for cool, make sure that the same colors are used in the air handler to provide the 24 volts to outside contact coil.
If this seams difficult, well it is unless you have the correct training incorrectly done can cause damage to unit and to personal health ..
8. Or call a professional HVAC tech.
Sep 20, 2014 | Goodman Heating & Cooling
Daikin split system air con dead
Split system Air conditioners are very often on two or more separate breakers, with a control voltage (24vac commonly) connecting their operation. the condensor unit and out-door fan generally on a 220 vc 'paired' breaker, possibly a quick disconnect near the unit with fuses inside, or an independant breaker pair, and the evaporator unit with INDOOR fan on a 110 or 220 vac breaker.
switch the fan to 'ON' at the thermostat... this is the midpoint of the system electrically. If the fan comes on check for voltage at the condensor unit. a check to see if the thermostat is the problem... remove the thermostat and connect the red, green and either the white or yellow wires (not both) if you chose white you should have heat...yellow AC...
most split system AC have a small buss fuse on the control circuit board of the indoor unit. looks like a glass tube with metal caps held by metal clips. In 40+ yrs experience I have found it is more likely one or both of the 30 amp buss fuses near the outdoor unit (replace both even if one is still ok) or a 30 amp breaker in the quick disconnect box.
In many systems the control voltage to the thermostat derives from a transformer in the outdoor unit... it could be as simple as a broken wire. Without a full diagnostic, a complete description of the unit ( AC or heat pump, etc) this is all speculation
Nov 19, 2013 | Heating & Cooling
GoldAir Airconditioner F9 Error
Is the power supplie dedicated to just the ac because it should be check power needs in manual
Feb 20, 2013 | Heating & Cooling
Help me please have a R410a 12000 btu mini split airconditioner heat pump that lost gas how do l regas it have closed all the leaks and have the R410a refregerant with the adapter.i have not charged a...
Mini splits need to have the refrigerant weighed in. First, ( if the system is already empty ) pull a vacuum down to 500 microns. Second, add the amount of refrigerant listed on the mfg. tag. Hope this helps!
Jun 07, 2012 | Heating & Cooling
Hi, how to you add more freon to 9,000 btu fugitronic portable a/c? Thanks
From the condensing unit you can see two valves. Connect the blue hose to the bigger pipe sometimes marked "S" to the suction manifold gauge with the blue dial.The discharge valve "D" is the smaller pipe and connect it to the red hose going to the red dial gauge. After connecting the hoses respectively, open the blue handle of the manifold to release air from the blue hose and close it. The same thing should be done to the red handle valve of the manifold. Connect the yellow hose to your freon cylinder and slightly open the cylinder valve while connecting it to the middle of the gauge manifold. Now, there is no air from all hoses and you can start charging freon when the unit start running. Check suction pressure and the Rated Load Ampere of the unit
Sep 03, 2011 | Fujitronic FA-9000 9,000 BTU Manual...
I have a Samsung AQV12JA. Fault code (Gas leak) have replace the outdoor and indoor thermistor per tech line. They said replace outdoor computer board. Board was back ordered for over a month, this is a...
As per the error code there should be gas leak from the Air Conditioner. Please visit the link below for a complete service manual with diagrams for more details, I hope it should help:
http://tinyurl.com/23ufvr2
Thanks and regards,
Anil.B.R
Sep 07, 2010 | Samsung AS18A6RB Air Conditioner
I need wiring manual for goodman mini split.
outside unit L1 and L2 are load (input 240vac)
then you have control voltage, usually yellow and blue (24vac) this connects to some 18/2 thermostat wire which goes inside as white and red.
note: this unit may only need 24v control which is 2 wires from the inside unit and also 3 wires 2 hot 1 ground for line voltage.
STANDARD WIRING
on the inside unit you have green, white, blue and red control wires.
on your thermostat you have white, red, yellow and green
you run the wire from the outside unit to the inside unit. then run a 18/4 wire to the thermostat if wired and join the following wires.
inside unit thermostat outside unit
green------------------------green
white-------------------------white
red----------------------------red
blue-------------------------------------------------------blue
yellow--------------------yellow
Oct 08, 2009 | Heating & Cooling
Remove and relocate split air conditioner
The simplest way of explaining this is as per the following. On your outdoor compressor unit there should be two pipes, one smaller diameter [high pressure] and a larger diameter pipe [low pressure]. Turn your A/C on inside the house and then shut off the smaller diameter pipe. Run the unit for a around 3 to 4 minutes and then check if the cooling is reducing from the unit inside the house. When you feel room temperature air [not cool] being emitted from the indoor unit shut off the larger diameter pipe and turn off unit. Isolate electrics, disconnect A/C piping and immediately seal the piping with good quality tape to prevent egress of dirt. When re-installing a quick purge of gas is usually only required to clear the lines if they were sealed properly and kept clean. Ideally running a vacuum pump is recommended but if care was taken then it may not be needed, as in many of my installations.
Jan 09, 2009 | Heating & Cooling
Heating & Cooling Logo
109 people viewed this question
Top Heating & Cooling Experts
Paul Carew