I have a heil dx 1300. the fan doesn't work with ac. can i run heat?
    Master:
  • 602 Answers
You can run heat if the blower motor that blows air into the house is working.
Posted on Dec 14, 2014
Heil heat pump heat won't work changed defrost board ac works
Reversing valve may be bad or stuck. U can pull the fan, then turn the unit on. The reversing valve is just a small unit with a 110 V. cable going to it. Sometimes taping the valve will make it change to heat.if so it will need to be replaced.
Feb 28, 2014 | Heating & Cooling
I have a Heil furnace (Temp star 9000 I believe) model number NUGS075BG03 that is not working properly. The inducer motor runs fine and I can see a blue flame through the sight glass but the circulating...
you need to check to see if blower motor runs in ac mode, if not then the first thing you want to check is the capaciter for that motor. if capaciter is good, motor may be locked up, you can check the amps of the motor by putting an amp clamp around wires going to blower motor, all ratings should be listed on motor
Oct 17, 2013 | Carrier Icp Heil Tempstar Furnace Blower...
Heil epm36f19a1 runs but no heat
Fan relay is stuck among other things. The thermostat turns on the combustion air fan and puts power to the spark unit. If the burner comes on after the temperature in the heat exchanger rises the indoor fan will then come on. After the thermostat comes to temperature the power to the gas valve which shuts off the burner. Then after the heat exchanger cools a bit the indoor fan will stop. That's the sequence of events. look at the switches that control the fans. There is a wiring diagram somewhere on one of the panels that access the unit for service.
Mar 06, 2013 | Electronics - Others
HEIL HVAC, fan blows but no heat or AC
Your airconditioning system may be out of cooling gas, and if it has sufficient gas, the compressor might not pick when you put on the AC, and if the compressor did not pick ie start, you cant experience cooling effect, the fan will only be blowing.
Jan 18, 2013 | Cars & Trucks
I have a heil furnace ac is working heat wont come on?
Check the white wire is making contact well in the t-stat.
Is it gas heat or electric/heatpump
If gas then check your flame ignition system to determine if it is lighting a pilot or has a hot surface type glow element. If it does not sense the flame it will refuse to run gas for heat and or check that the electric enducer fan is comeing on before the pilot even attempts to light. It must run to prove a draft induction exist for the furnace baffles before it will attempt to start heat.
If it is a heat pump then it should fail to heat side on the reversing valve and not really need to be checked since your AC works. The call for AC has reversed the valve to even get cooling. So it is going to be heat strips failing or sequensers failing maybe even low refrigerant on a heat pump system. I know this is all a bunch to digest remember it is usually electrical and just a loose wire! So start from there and T-stats do go bad just because they can!
Oct 08, 2010 | Heating & Cooling
My 2 ton ac with air won't run even the fan on
Hi; Does Your air handler have a small fuse on the circuit board. CHECK IT. What kind of heat do You have / heatpump/gas/total electric/. Need more info...alpharome416
Jan 22, 2010 | Heating & Cooling
Heil Max Performance 10 Heat Pump not working
First check to see if you have afloat switch inside the air handler ar underneath the air handler. Its purpose is to shut the outside ac off if the drain stops up. Very common. If this is OK take cover off unit and with screw driver push in the contactor. It is located about the middle of the panel. It has main power at the bottom. If unit comes on you cave a control voltage problem. Meaning something is not allowing 24 volts to the contactor. If your out of Refrigerant the low pressure swich will have it off. Call a service tech. Rusty
Jun 09, 2009 | Heating & Cooling