Question about York Tools & Hardware - Others
York furnace tm9x060 need service manual-trouble shooter guide
Intermitten running code 7 or 8
3 Suggested Answers
SOURCE: York 92 % eff. furnace shuts down on # 3 error (pressure switch)
i have fixed almost every one of pc9 -----we have installed in our company,code three{flashes} at first new presure switches installed, same thing,york knows about this,induction motor bearings,could be bad.our local york dist, has boards,inducer, ***.motor, dual press.switch,free.as is known as the only way to fix.after all else is ruled out.one local competator called us if we wanted to join class action suit . good luck.furnaces work good at first, season or two then bam
Posted on Dec 04, 2009
Testimonial: "Believe have now pin pointed it to weak inducer motor.Removed outside exhaust vent apparatus with three elbows in it. Put one elbow back on .no more "
HVACjake
  • 22 Answers
SOURCE: york furnace model p2mpd12h06401f flashes 4 times
Check pressure switch for inducer motor. If switch closes, check for crack in ignitor. If gas valve opens and you can hear/smell gas, the ignitor is bad probably. If pressure switch isn't closed you need to check for blocked vent/chimney/heatexchangers.
Posted on Jan 21, 2010
York furnace code 7
The error 7 shows that the gas failed to ignite. That is because the sensor does not sense any flame. This can be because the sensor is dirty. You should look in the area of the jets for a wire that may be purple in color. It attaches to a bare metal probe that is shaped like the letter L This probe extends into the path of the flame from the jets. When it detects flame it tellls the controller that everything is good. When it gets sooty or dirty from use it cannot detect the small electric currents that are present. Clean it with scotchbrite. Error 7 means that the furnace is locked out and wont restart for an hour. You can shut the power off and turn it back on to reset it.
Feb 26, 2014 | Tools & Hardware - Others
York furnace 7 flashes
If the light flashes red 7 times, the furnace is not sensing flame. Check for a flame sensing rod (small steel rod in the path of the main burner flame). If you can see it, shut off the furnace, and clean the rod with a rag soaked in vinegar. Turn the furnace back on and see if this cures yyour fault. Make sure you turn the power off to the furnace and then back on as this will reset the circuit board.
Jan 05, 2013 | York Furnace Draft Inducer Blower Fasco #...
York diamond 80 fan starts running blowing cold air before furnace ignites..replaced thermostat
OK so you replaced the Thermostat huh? OK well then did you also replace the Thermistor Temperature Sensor? or whatever is used? As often it's BOTH, also check the wiring from the sensor to the host, in any event if it's NOT that then all it can be is the controller board, most likely the Micro? Check any and all sensors first though.. try to get a service manual too, it's hard without one?
Oct 20, 2011 | York Furnace Draft Inducer Blower Fasco #...
I HAVE A YORK FURNACE THAT HAS CODE 7 BUT THE LIST ONLY GOES TO FIVE. THE BOARD HAS BEEN CHANGED. WHERE DO I FIND THE NEW CODE LIST??
Contact York directly at their Consumer Relations Dept: 877-874-7378 Monday - Friday 8a - 5p CT
Hope this provides the answer you need.
Feb 15, 2011 | Heating & Cooling
York furnace model p2mpd12h06401f flashes 4 times for trouble code does'nt have code list inductor motor comes on but ignitor does'nt come on
Dec 18, 2009 | York Furnace Draft Inducer Blower Fasco #...
Nov 28, 2009 | York Furnace Draft Inducer Blower Fasco #...
INSTALLATION MANUAL FOR PV9C YORK FURNACE
I just replaced a thermostat on a york furnace model gy9s100c16up11h. During the process i connected the red and white wire and the unit came on after making the connections it will not come on even if I jump the red and white wires without the thermostat. Thanks Dan
Jun 10, 2009 | Heating & Cooling
Loud noise when furnace starts but furnace won't come on.
Your fan delay relay has failed and must be replaced.
Jan 16, 2009 | York Yankees Bedding MLB Comforter
York high effenciency furnace not firing all the time
has anyone worked on this furnace because the error would indicate that the positive 120 volt and the neg 120 volt is swapped , these units will also do this when the ground wire to the furnace or gas valve or furnace or @ the panel is lose , corroded , or missing , the gnd must be present to open valve , I am aware that ac is is not usually polarity sensitive but in this case it most certainly is ...have seen many time and know it to be true
Dec 27, 2008 | York Yankees Bedding MLB Comforter
Tools & Hardware - Others Logo
162 people viewed this question
Top York Tools & Hardware - Others Experts
vince
Paul Carew
Are you a York Tool and Hardware - Other Expert? Answer questions, earn points and help others