I recently switched some breaker around in my fuse box. There were a few 110's and 220's not being used. I deleted those to make some room to put a larger amp breaker for my hot tub that been sitting
Don't know what to try from here.
Try for what ?
You removed breakers not needed or ones with little
on them, to make room for a larger 50 amp Hot Tub
Breaker,so you got your hot tub powered up
What is the question,seems you solved the issue
by making room for the new breaker !
Posted on Nov 21, 2014
  • 744 Answers
SOURCE: Intermittent Power fading on all electrical circuits
This sounds like a bad connection somewhere. If you are comfortable working on electrical equipment, remove the main circuit breaker panel cover and sometimes an inner cover depending on the panel make.
Turn off the breakers one at a time - Check the wiring connections on ALL circuit breakers after they have been turned off. It's not unusual for wiring to loosen up on breakers after several years. Tighten all the screws where the wires are attached, usually with a flat-blade screwdriver. Then tighten all the white wires attached to the neutral buss. If you see any green wires, tighten them too.
Look for any burned or discolored wires, indicating that something is loose or overloaded. Do not place your other hand on anything metal while you tighten the wiring and use an insulated screwdriver. The best bet is to put your free hand in your pocket so you don't lean on something grounded accidentally.
You should also check the wiring on the main breaker to the home, but this can be dangerous and should only be done by trained personnel. This task may require removing the electric meter outside your house. It's even possible that the wiring on the primary side of the meter is loose - if it looks burnt, call the utility company - they will usually respond to this issue.
Hopefully, tightening all the wiring on the breakers will solve the problem. Residential circuit breakers are usually "stab" type, meaning they ""stab" onto the phase busses.
Above all, please be careful. If you aren't sure, it's usually best to call a licensed electrician.
Ask again if you need more help.
Posted on Mar 31, 2009
  • 3600 Answers
SOURCE: 240 w/60 a outside breaker with test switch wont'
Inside the controller box is a red button to reset it but most likely the heater element is shorted out so replace the heater element first. Cost $100.00 at any pool or spa shop. Post here if you need more help.
Posted on Sep 28, 2009
  • 66 Answers
SOURCE: 20 amp breaker pops with only a light (60watts)
I have been an electrician for 11 years and when these breakers came out in 2005 what a nightmare. These circuit breakers are extremely sensitive. They are designed to sense loose connections and to protect your house from fires caused by them. By increasing the load (ie. more lights or tv) it increases the size of the "arc" created by the loose connection and the circuit breaker trips before the 20 amp maximum. What I normally find as the cause is a loose connection in one of the receptacles or switches on the circuit. A lot of times, installers will use the "quick stab" inserts on the back of the outlets or switches instead of the side screws. Usually, if you "side screw" all of the receptacles and switches it will resolve the nuisance tripping. One other item that can cause them to trip is too many dimmers on the arc circuit but it doesn't sound like that is the problem you're having.
Posted on Nov 16, 2009
  • 454 Answers
SOURCE: Circuit breaker only half working - reddish flag?
A red indicator means a circuit overload has tripped the breaker. You mentioned a heater? Does the circuit tripping coincide with the heater running? There may be too much load on that circuit.
Contact the original electrician to see if he will come check it out ( licensed, reputable electrician should have no problem with this). If he gives you the run around, find another. Was any aluminum wiring found in the home inspection?
Posted on May 01, 2010
SOURCE: why is my 50 amp GFIC breaker tripping out? I have
There might be a few things here:
1) Big problem >> the #8 wire is a fire hazard connected to a 50Amp breaker
#8 is a 40 amp breaker
#6 is a 55 amp breaker
We put #6 on a 60 amp breaker
Are you saying you hooked the #8 wire to the new 50 amp breaker, and the hot tub called for #6 wire?
Upsize your wire and breaker to meet code
http://waterheatertimer.org/pdf/Wire-size-amp-rating.pdf
2) After putting the correct wire and breaker, you can still have a short in the circuit somewhere
We used to set equipment out in the field in early morning >> the grass was wet >> our equipment was fine, but the tiniest short would cause the GFCI to trip
I don't know where the problem is without a thorough checkout of every possible grounded surface. You need a good multi-meter
3) You better get an electrician over there to have a look before the place burns down or somebody wakes up dead in the hot water.
If I sound a bit scary here, it's because something doesn't sound right with your installation.
Posted on Oct 19, 2010
Machine is not getting any power it is not the fuse
it could be a few things the door catch,or the fuse take the lid off unplug first see if theres anything wrong where the cable comes in if the fuse and the cable has nothing wrong then it's more than likely the door catch or Probably a bad "on" switch or dial. It will need replacing. If the washer is more than 10 years old, you may have a hard time finding parts. You will then need a new washer or resort to finding used parts from and junk yard or used appliance dealer. Source(s): Been there, done that. or The on-off switches are circuit breakers. No there should be nothing behind the breaker box panel except wiring. Do you have any GFCI outlets in the house? They are typically put in bathrooms and kitchens. Go around and make sure they are all reset. Your three living room outlets could be wired through a GFCI outlet.
May 17, 2011 | Washing Machines
Cant find the fuse box. The headlights have stopped working, but we cant find where the fuse box is located.
Headlights aren't fused, per se...they are protected by a circuit breaker. If I were you, I'd first check the actual headlight switch. They're relatively inexpensive (I recently put one on a '92 Silverado and it was under $15.
Jan 02, 2011 | 1994 Chevrolet C/K 2500
No power to the receptacles on a circuit, the breaker isn't tripped. there are no GFI's
No breakers are tripped and a circuit is dead.
There is a loose wire.
Let me explain how it works. Each 120V breaker has a black wire that leaves breaker box. The black wire is accompanied by a white neutral wire and a bare ground wire. These wires are sheathed in plastic, and altogether they make up a romex cable.
The cable leaves the circuit breaker box and travels to the first junction box. The junction box is a ceiling box that holds light or fan -or- a wall box containing switch or plug. As a general rule, the romex leaves the breaker box and travels all the way to a junction box located right in the area where lights and plugs are located. The romex does not stop at a junction boxes located in other room.
Inside the junction box, the romex splits and goes to the next junction box, and then to the next box, and the next.
So the plugs in one room are all connected together by a single romex cable that started back at the breaker box. And a single romex wire from the breaker box arrived at one of the junction boxes located in immediate vicinity of dead receptacle.
Here's what happened. A wire came loose somewhere between the breaker and the dead receptacles.
The loose wire is probably in a receptacle.
Here's what to do.
1) Breaker first: You can isolate the suspect breaker by identifying all other breakers. Then tighten screw on suspect breaker. Look for white wire and ground wire associated with the romex cable that connects to breaker >> tighten those screws on neutral busbar. Look for burning around suspect breaker. Is there a burning smell indicating breaker is bad?
2) Receptacles Next. Use ordinary tester. Test each receptacle. Receptacle has two rectangular prong holes and one round hole located below other two. The round hole is the ground. Breaker is turned on. Test each rectangular hole to ground. You have to test both prongs to ground.
The loose wire is right there in the vicinity of dead receptacles.
Test one receptacle and then move to next receptacle. At some point the tester will light up. Now click suspect circuit breaker to see if that receptacle is on breaker. Test receptacle with breaker off and breaker on. If that receptacle is on the suspect breaker, then a loose wire is inside that receptacle box >> or inside the next box. Many times, the wires are pushed into 'quick-connects' located on back of receptacle ... wires get loose ... you need a small screwdrive to release quick-connect, and then wrap wire around screw -or- replace receptacle
If none of receptacles show electricity, then loose wire is inside a switch box, or it is inside a ceiling box located in same general area. Check your switches first. Look for quick-connects, or signs of burning. Look for loose wire nut. Plug light into dead receptacle. Pull switch out with wires attaches. Power is on. Move switch around to see if dead receptacles shows electricity. Move to next switch. The loose wire is there somewhere.
Finally the ceiling box. Take down light and see if there is a loose wire inside. Look for signs of heat or burning.
Oct 11, 2010 | Connecticut Electric Square D Packaged...
Switch stuck in trip mode
The reason why the breaker stays tripped is a result of a direct short. Unplug every electrical device plugged into an outlet in both rooms and try the breaker. If it stays on, individually start plugging in each device until the breaker trips, that is the defective device. If the breaker stays tripped, start checking wall outlets for short circuits with an ohm meter. If you did not find a short, check your hard wired lamps and appliances for shorts. If you did not find any shorts the only other problem is a shorted pair of wires in the wall or ceiling. You will need to disconnect any hard wired lamps and appliances and check for shorts between individual pairs of hot (black) and neutral (white) then hot and ground. I have a short circuit finder, but you do not need one because the technology is not perfect and you may have to manually check for shorts with a meter anyway which never lies.
Jun 25, 2010 | Square D Co. HOM130 Circuit Breaker
I'm putting a new adition on and am wiring it. I have two rooms with ceiling fixtures and seperate switches and will put them on the same circuit. The first room will be powered from the fuse box to the...
Hello There,
I would put the Switch's Independently for each fixture, thought wired together through the same wiring to the fusebox.
If one Switch is wired to another, they could both alternate for the same fixture, however, use them independently:
with the wires connected from the fuse box, to independent switches, but the switches are hooked up towards the fuse box. And then from the fuse box, to switches, and then to fixtures. :)
Apr 01, 2010 | Atlas Hammering
I live in a home where we had a switch go bad in our boys room. When we replaced the switch my daugters switch would not work. We have three wires coming out of both wall outlets plus a ground. I got a...
If the problem arose after you replaced the switch in your boys room, that is where I would go to first in my attempt to troubleshoot the problem. After you pull the switch out, I would leave the switch in the off position, and check that 2 of the three wires in that box are receiving power.
If there is only a single with power then that is the power coming into the switch box, and it is very likely that one of the other wires is intended to feed beyond. A good way to check this would be to turn the switch on and see if your daughter's switch is getting power when that switch is on. If this is the case, the next part becomes a little tricky.
1. turn the switch in your boys room off
2. disconnect only one wire from the 2 that do not have constant power.
3. turn on switch, if light for the room turns on, then attached wire is switch leg for the light, and disconnected wire is power out of rest of the circuit.
CAUTION: turn off power at breaker before continuing
4. once you know which is the switch leg, and which is the out for the rest of the circuit, junction the in wire with the out wire, and attach a single wire to this junction twisting all three together, put a wirenut on the junction, and re-attach to switch.
once this is done, you should be able to turn the breaker back on.
If the above instructions are not needed, it is possible that the switch is fed from a plug in the room, and that a connection on the plug could have gone bad. In this case, you should once again, turn the breaker for the room off first.
1. pull out the plug
2. ensure that all wires are wrapped around the screws, not pushed into the holes in the back of the device. Black to brass, White to silver, Ground to green
3. put the outlet back and turn the breaker back on
4. test the switch
I hope that this proves helpfull and resolves your problem. please let me know if you have any questions
Feb 09, 2010 | Leviton COMBINATION SINGLE POLE TOGGLE...
Dryer wont work
I'm assuming that the dryer is gas, since both the washer and dryer are on the "same" breaker. I'd try replacing the wall plug before replacing the dryer. If you have a voltage tester, you should see if you are getting an honest 110 volts coming off the circuit. Since the circuit was a problem before, I would test it first and then more on.
Jun 08, 2009 | Maytag Atlantis MDE7400AY Electric Dryer
Our tub's pump won't start. we haven't used it in
Begin by checking the circuit breaker or fuse box. You may find that someone turned the breaker off or removed the fuse. Next the pump most likely has a reset button on it which is evident if you remove the panel covering the mechanical area and look around.
Apr 26, 2009 | Home
Microwave causes all appliances to shut off
A surge protector will not help. The circuit that you have the microwave plugged too is overloaded or the breaker is weak.
You need to find out which breakers in your switch box operate which outlets. Then you may be able to move some of the appliances to different recepticles that are on different circuits.
Turn the lights on in all the rooms.
Got to your switch box and turn off one of the single switches(not the ones that are two switches hooked together).
Then go to each room and check to see which lights have went out. Take a lamp or small appliance to each wall plug-in and see if it has power.
When you find out everything that switch controls, write it on a piece of paper so you will know in the future what that circuit has on it.
Turn that switch back on and repeat the process with the next switch and so on and so forth until you have written down what each breaker controls.
Now you will have some idea which circuits have the most load and which ones you can move something to.
You also need to call your landlord or building super to check to make sure the breakers in the switch box are in good condition.
Hope this helps.