I have a riello burner 40 it will fire and come to temp but wont refire, goes into lockout
  • 4 Answers
My first guess would be that it sounds like a clogged oil filter, air in your fuel line, is piping overhead, or leak in a fitting or connection causing it to loose it's prime when running.
I have also seen primary controls that are faulty do this, watching the complete cycle of the run time will give you more clues as to when the control actually locks out. Does it lock out during the run cycle as the boiler reaches temp.? If so,check for oil line and suction issues as stated above.
If it locks out on start up after reaching boiler set temperature, if hitting reset right away burner doesn't start and lock out occurs with no motor engaging, check motor (Note: Some motors when HOT will not kick in when powered, but after they cool down naturally they start, motor shaft may also be bound up tight, replacement is necessary) if burner motor spins but does not fire, check for fuel flow to the nozzle, be sure oil is pumping to the nozzle, if it is, clean cad cell eye, and check transformer for spark, if all is good.. replace primary control.
Disclaimer:
Of course all this information is technical troubleshooting information and should be performed by a Licensed Technician, not knowing how to properly test for flame failure can cause injury, fire or worse! Consult a technician in your area if you are not proficient at oil burner repair!
Posted on Dec 13, 2014
2 Suggested Answers
  • 3287 Answers
SOURCE: i have a riello 40 burner it fires for 2 seconds then cuts out what could be the problem
If it actually fires up and you have a flame for 2 seconds and then it shuts off, I'd bet that the photo cell is either dirty or has failed. If it is dirty, it suggests that the burner has been neglected for some time and probably is in desperate need of a tune up. The photo cell is located under the ignition transformer and is aimed into the combustion chamber to see the light created by the flame from the burning oil.
If it is clean, the photocell has likely failed and will need to be replaced. If it still runs the same way after photocell replacement, it is probably related to the primary controller or one of the other safety devices. Is this a forced hot air or hot water system?
Posted on Oct 06, 2012
Riello burner
You need to measure the manifold pressures before and after the gas valve and adjust accordingly to fuel used, 3.5" NG or 11" Propane.
Nov 06, 2013 | Honeywell Biasi B10-3 Boiler ,riello...
I have riello oil burner put oil into a empty tank tried to bleed it now it won't fire up can you help
is the filter clean u might of picked up sludge in bottom tank also blow out the supply lines and re fitt try again
Sep 23, 2013 | Honeywell Biasi B10-3 Boiler ,riello...
GX90-715A wont stay fired
1) Product manual has burner info page 11, maintenance 12, and troubleshoot flow charts starting page 17
Otherwise, Rheem does not post service manuals.
http://bostonheatingsupply.com/Rheem/Rheem%20Commerical%20Gas/Rheem_CommGas_Extreme_Use%20and%20Care%20Manual.pdf
2) Post question on pro water heater forum.
http://www.thetankatwaterheaterrescue.com/forums/forum3/
3) Is air intake clear? Is the burner sooted? Is the flame large and clear blue? Is the vent obstructed? Does air draft when blower activates?
Feb 14, 2013 | Rheem RUUD GX90-715A Water Heater,gas,90...
I have a halstead finest gold combi when I turn the boiler on the boiler goes into its ignition sequence when it comes to ignite the boiler fires but after the igniter stops the boiler cuts out completely...
Difficult to get too specific without knowing if you have gas or oil. Also, I am going under the assumption you mean the burner shuts down, not the whole heating system. That being said, all heating appliances have whats called a safety curcuit. Each control has the ability to shut down if certain critera are not met. There is a sensor that senses light down the blast tube. If no light is sensed in a predetermined time period, then the sensor cuts power to the burner. This stops delivery of fuel so if it does ignite you wont blow up.
(I suspect that the ignitor and burner shut down simultainously.)
It may be the sensor (cad cell eye) is doing its job, however why is the question. Could be a number of things including the fuel delivery, ignition, improper air adjustment, etc.
No qualified professional should diagnose a problem unless they are in front of the appliance. I recommend you find a licensed qualified heating techician. Hope this helps.
Feb 04, 2013 | Water Heaters
Rheem Intelli-vent intermittently goes in lockout mode
However AO Smith has posted relevant service manual:
http://waterheatertimer.org/How-to-troubleshoot-gas-water-heater.html#intellivent
Have you cleaned the air intake located under combustion chamber, and inspected for broken glass vial?
Rheem FVIR system uses glass vial that breaks if combustion air is slowed, and resulting combustion causes slow-moving venting of hot gasses, causing overheating that breaks glass vial.
http://waterheatertimer.org/How-to-repair-Rheem-FVIR.html
Check gas pressure.
Replace gas control valve:
http://waterheatertimer.org/pdf/How-to-replace-water-heater-gas-valve.pdf
Oct 09, 2012 | Water Heaters
I have a riello 40 burner it fires for 2 seconds then cuts out what could be the problem
Oct 05, 2012 | Honeywell Biasi B10-3 Boiler ,riello...
I have a Richmond 40 gal water heater model# 6G40PVW-40PF manufactured 5/2010 and it wont't stay lit. I don't have the owners manual as we purchased our home in 12/2011 and it was a foreclosu
Well I you have the problem resolved by now, but I will answer anyhow. This just happened to me yesterday with the same water heater that you have. My problem was that the flame sensor was dirty and not picking up that the burner was lit, so it shuts everything down and goes into lockout mode. I had a similar problem with my furnace lighting system. It is called flame rectification. What actually happens is the flame itself allows a small current to flow through it, so the flame sensor actuall makes electrical contact with the burner. The control senses this connection and knows then, that the flame is on. If it doesn't sense this connection, it thinks the flame is out, so it must shut off the gas valve to prevent a possible explosion. Take your burner out and clean up everything in there, being careful not to break the small glass bulb inside, which is another safety device. Fine emery cloth of a wire brush will clean up the flame sensor good. Also wire brush the burner itself, since this is the other end of the rectification circuit.
Apr 01, 2012 | Audiovox Richmond 6G40-36F 6-Year Tall Gas...
Heats up the rapidly decreases within in minutes.
Problem new or old? How long you have unit? Sounds like not enough flow to keep burner on. Tankless need at least .6 gpm to keep hot water flowing or else the burner fires then shuts fires then shuts and you get a sandwich effect...hot cold hot cold. If you have new diverter valve in shower -vs- old two handle type try turning hot water ALL the way ON and see if hot stays hot. If it does stay hot then slowly adjust to cool and see if you maintain a good MIX for proper temp. If it goes cold again try this......LOWER control pad setting to a comfortable 105 degrees (ladies) 100 degrees(men) and turn shower valve all the way to HOT. See if your temp remains consistant now and if it does then problem solved. Tankless mindset...set temp on control pad and stop trying to MIX at shower valve. Thats how these things work. Thats why I install a control pad in each bath and one in the kitchen for adjusting ash temp during dishwasher on time. ditto for wash machine. You should never need to turn on cold water if your unit is set to proper temp at controller. Hope this helps
May 17, 2010 | Rheem Tankless Hot Water Heater...
Pilot light on water heater wont stay lit
The thermocouple has failed. It is the temp probe that goes from the pilot lite burner area to the control valve. Go to your local plumbng repair shop and buy one. Most appliance parts stores have them also. Take the old one with you and they will hook you up with an exact replacement. They are not that hard to change. Usually a nut or 2 screws in the temp bulb area at the burner end and a nut that threads into the control valve.
Make sure before you install the new one that the area where it mates to the gas valve is clean. Should be about a 20 min job including clean up with replacement parts in hand.
Jan 23, 2010 | Rheem 40 Gallon FVR NATGAS Low WATER...
Honeywell Biasi B10-3 Boiler ,riello Burner Logo
257 people viewed this question
Top Honeywell Water Heaters Experts
paulcarew
Lawrence Oravetz
Steve
Are you a Honeywell Water Heater Expert? Answer questions, earn points and help others