Coleman Evcon Eb15b we replaced thermostat last night so that wasn't it when. Put in auto for heat u can hear a click. See where and feel it heating up tgen u hear. Another. Click and nothing even the heat stops but put it on on and the air blows constantly and its only air no heat
    Problem Solver:
  • 14 Answers
If you turn on heat and no fan comes on, the electric will over heat and trigger high limit switch. the switch either self resets after it cools for a while or needs manual reset. read directions on thermostat for electric heat. energizes fan at same time as heat on calling from stat.
Posted on Nov 20, 2014
  • 3 Answers
SOURCE: Gas Furnace is not heating anymore.
the fan you hear come on at a call for heat is most likely just the inducer motor. the click you hear is probably the relay for the hot surface ignitor which should glow red, then in turn ignite the main burners. your going to have to determine if the ignitor is coming on. if it isnt the ignitor is bad and will need to be replaced. if it comes on and than shuts off after a few seconds the ifc board is probably at fault
Posted on Apr 10, 2009
philbran
  • 242 Answers
SOURCE: Furnace runs constantly since blower motor was replaced
Sounds like they wired it direct to line voltage , it should run through a sequencer or fan relay to cycle on and off , your seq./relay could be stuck closed to but unlikely being it was just repaired , call the service company back before you do anything they are responsible.
Posted on Apr 11, 2009
  • 233 Answers
SOURCE: air conditioning runs all the time
I assume this is a manufactured home, this is probably a two transformer system, either your contactor is welded in the on positon or wyou have control wiring issues, (could be the thermostat)
Posted on Jul 12, 2009
  • 146 Answers
SOURCE: My Coleman Evcon heating and air unit will not blow air
bad blower motor. recommend a new blower motor and capacitor.
Posted on May 28, 2010
Coleman Evcon EB15B heat doesnt stop when it reaches the temp set on the themostat just gets hotter and hotter until I shut it of at the circuit breaker
Thermostat not doing it's job.
Probably the contacts on the thermostat are stuck together, Caused by arcing each time it opens.
If you are up to it.... clean the contacts or replace thermostat,
Cheers
Mar 03, 2015 | Heating & Cooling
Coleman/ Evcon central electric furnace Eb15b thermostat on auto will not blow air out i hear a click u see and feel it heating up then i hear Another click dont see nor feel heat then but put thermostat...
check the thermostat setting on back for electric heat. sounds like it is on gas heat. the fan should turn on right away if it is electric or heat pump.
Nov 15, 2014 | Heating & Cooling
No fan when ac kicks on Ihave a eb15b funace with a coleman ac
The heat will normally use a low speed on the fan, & the AC along with the fan switch on the thermostat will use the high speed. The thermostat turns that high speed on when there is a call for cooling & is the same switch if you were to manually turn the fan from auto to on. Try turning the fan on @ the thermostat. If it works, then replace your thermostat. If it doesn't, it could be a bad fan speed, a bad fan relay on a control board or external relay, or a loose or broken green thermostat wire.
Apr 14, 2014 | Coleman Home Electric Furnace Eb15b/Eb15d
Evcon eb15b
thermostat, heat sequencer or contactor, no 240 volt power no 34 volt power
Nov 23, 2013 | Coleman Heating & Cooling
Our coleman evcon furnace has started clicking over & over again before it starts up, we replaced the thermostat & the same thing happens.We are afraid that this is hard on the furnace & have resorted to...
Suspect that the igniter is causing the clicking (or could be a relay). Suggest having the furnace serviced. There is also a major recall for some models of the Coleman Evcon furnaces.
Oct 29, 2013 | Heating & Cooling
We have a Coleman Evcon BW-305150. Last night we
There should be one right above the burner tray. Look at the wiring diagram (pasted on one of the panels) and follow the wires Usually red orange or yellow) to the switch (may look like a rectangle plate with 2 prongs) and jump the switch with a jumper to test.
Feb 26, 2010 | Coleman Propane Forced Air Heater...
No heat at night
You have a poor low voltage connection from the thermostat or a bad contactor.The contactor is the main relay control inside the condensing unit. The incoming voltage wires connect to it.
Contactors are inexpensive. I would change that first.
Check all your low voltage wires in the condensing unit for loose connections.
Dec 11, 2009 | Coleman Heating & Cooling
Heating & Cooling Logo
155 people viewed this question
Top Heating & Cooling Experts
paulcarew
Dan Webster
Dan Webster
Donni Steen