Ignitor doesnt have power to it
Controller is a 50e47-843, i think controller is bad. can light furnace wwith lighter an runs fine
  • 1,268 Answers
Light the furnace with the lighter and allow it to cycle for a day, keeping it set for run. It should clear and the igniter work properly after that. If it doesn't, then is in the controller. But most likely will reset and clear within a 24 hour period or much less. It just has to keep cycling until it clears and resets.
Posted on Nov 15, 2014
Furnace was working fine and just stopped working...it reacts to raising the thermostat but doesnt actually flame on
This is probably a ignitor.
1. Thermostat calls for heat. 2. Draft inducer motor starts. 3. Pressure switch attached by a small plastic or rubber tube senses the negative pressure produced by the draft inducer and closes. 4. Draft inducer runs for 30 seconds to a minute before you hear a gas hissing sound. The ignitor did not glow, the flame sensor (a small metal probe about 1/8" in diameter, with a white porcelain base) does not sense the flame, so after 8 to 10 seconds the hissing sounds stops with no ignition of gas to heat your home. Your furnace shuts down and goes into a lock out condition until you turn your power switch back off and on again. Then the sequence starts all over again with no ignition of the gas. Solution:You probably need to purchase and install a new ignitor. I would suggest that you inspect your ignitor closely for cracks.Make sure you do not touch the ignitor with your bare hands. If you do not visually see a crack, then you could have a furnace control board problem or a limit, rollout switch problem. Please see "limits, rollout switches & furnace control boards" further down on this page. The furnace's control board might not be supplying the voltage to the ignitor. If your furnace lights and the gas stays on for 8 to 10 seconds, then shuts right back off, then you need to clean your flame sensor with light sand paper or steel wool. You might need a new flame sensor, but most of the time they can be cleaned an will work well after cleaning.
Please leave feedback... Thanks...
Jan 28, 2011 | Goodman GMS90703BXA Heater
Doesnt blow any heat we checked all connections furnace clicks on but never gets warm we think maybe its the heating element but we are not sure how to get to it to check
Problem: Your furnace will not ignite the gas to produce heat for your home. When a furnace has a bad ignitor what I see most of the time is the following sequence of operation:
1. Thermostat calls for heat. 2. Draft inducer motor starts. 3. Pressure switch attached by a small plastic or rubber tube senses the negative pressure produced by the draft inducer and closes. 4. Draft inducer runs for 30 seconds to a minute before you hear a gas hissing sound. The ignitor did not glow, the flame sensor (a small metal probe about 1/8" in diameter, with a white porcelain base) does not sense the flame, so after 8 to 10 seconds the hissing sounds stops with no ignition of gas to heat your home. Your furnace shuts down and goes into a lock out condition until you turn your power switch back off and on again. Then the sequence starts all over again with no ignition of the gas. Solution:You probably need to purchase and install a new ignitor. I would suggest that you inspect your ignitor closely for cracks. Make sure you do not touch the ignitor with your bare hands. If you do not visually see a crack, then you could have a furnace control board problem or a limit, rollout switch problem.The furnace's control board might not be supplying the voltage to the ignitor. If your furnace lights and the gas stays on for 8 to 10 seconds, then shuts right back off, then you need to clean your flame sensor with light sand paper or steel wool. You might need a new flame sensor, but most of the time they can be cleaned an will work well after cleaning.
Dec 19, 2010 | Heating & Cooling
I have an 8 year od York furnace model P1XUC20N09501C 90%. The problem is the ignitor comes on, the left burner lights, but the other burners won't light. I can light the other burners manually with a...
Its not crosslighting Clean them all use a air line if you have one or a vac , must be blocked or not in line . Not much else I can think of .
Apr 24, 2017 | Heating & Cooling
Furnace shuts down intermittently when calling for heat
The flame sensor is not working properly, it is not allowing the ignitor to ignite, and this is making the system shut down, the flame sensor has obtain a build up of carbon, you will need to remove the flame sensor, and take a little piece of sand paper to remove the black carbon from the flame sensor stem, clean until the stem is shinning, replace the flame sensor and turn the furnance back on this will correct the problem.
Dec 10, 2009 | Heating & Cooling
It's not lighting it's not working I see motor is running and I think gas coming out but it's not lighting I turn off the funance
Turn the power off to the furnace, turn the thermostat to the highest heat setting then turn the power on. The fan may start for a brief period, then the combustion blower will start, after approx 90 seconds, the ignitor will light and heat up. You should be able to see a glowing in the burner lens. If you do not see a red glowing, similiar to a car lighter, that would indicate the ignitor may have failed. If after 3 attempts, the systems fails to light, there is a light on the circuit board that will flash, the number of flashes will indicate the reason for the fault.
Nov 13, 2009 | Goodman GMS90703BXA Heater
My problem is with the central heat. The thermostat will click, but the heater doesnt come on. What will cause that?
On a call for heat, the 24 volt thermostat2.gif sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the ignitor. The ignitor will glow and you will be able to see it if viewed thru the small inspection port. Once the ignitor gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the ignitor does not energize (bad control, bad ignitor), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not lite (dirty pilot), the burner does not lite (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
Most newer furnaces will have a diagnostic center or control built into the control module. You may be able to view it as it is running thru a small viewing port. Some models will require the removal of an access panel prior to finding it. On the reverse of the access panel, there will be a diagnostic chart that will aide you in understanding any error code recorded (usually a blinking light).
Oct 18, 2009 | Heating & Cooling
Ruud heater will not light consistently
Your furnace is going into a lockout condition, cycling the power resets the circuit board and it starts over. I will need to know approximate age and model of your furnace, it sounds like you have need to clean the flame sensor rod. However i need to know what i am working with.
Dec 18, 2008 | Ruud UBHC Air Conditioner
Goodman furnace blinked 1 time
Furnace attempted to start but failed after so manay tries. This may help you.
Sequence of operation, Gas Furnace.
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the ignitor. The ignitor will glow and you will be able to see it if viewed thru the small inspection port. Once the ignitor gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
This is why we technicians earn the big bucks!
Dec 05, 2008 | Goodman GMS90703BXA Heater
No heat
knowing the sequence of operation on your gas furnace may help you diagnose your condition.
Dec 03, 2008 | Goodman GMS90703BXA Heater
Heating & Cooling Logo
60 people viewed this question
Top Heating & Cooling Experts
Paul Carew