Tempstar DC90 pilot light or burner keeps going out. The furnace will run continuously. Even if I turn heat off at the thermostat. I have to kill power at the panel box to get it to shut off. Then I've been pushing the reset button near the ignitor and when I turn everything back on it runs fine for a while until some point where the burner in the Oval window at the top doesn't light again and the furnace runs contouring again.
    Legend:
    An expert who has written 200 answers of more than 400 characters.
  • 484 Answers
The reset button near the ignitor is a high temperature limit safety switch. When the furnace gets too hot and the manual reset limit switch is tripped, it most likely goes into a 'safe' mode where the gas control is locked out electronically and the blower is made to run continuously to rid the heat exchanger of the excessive heat. This will continue until the reset is pushed and the power is cycled off. It will remain an endless cycle unless the reason for the overtemperature condition is not corrected.
Your furnace 'temperature rise' is getting too high due to a lack of air across the heat exchanger for whatever reason. Some of those reasons could be a restricted air filter or a blower motor that's cycling improperly on its internal winding thermostat. You could also have a dirty air conditioner 'A' coil (evaporator) on top of the furnace restricting the air flow. Nevertheless, you are going to have to have it serviced by a reputable service company's technician to correct what's wrong.
Posted on Nov 30, 2014
4 Suggested Answers
SOURCE: Goodman Furnace Lights But Won't Continue to Run
The flame sensor is dirty. You can not see the build up on the sensor but enough build up will change the resistance and the furnace thinks there is no flame.
To clean the sensor, first you need to locate it. it will be a sensor located in the path of one of the flames. Once you locate the sensor, open the bottom panel to turn"off" the furnce. After the panel is removed, unscrew the sensor from the frame above the jets. Use a clean rag and gently wipe the sensor several times. Place back in the cut out and close the lower panel.
The furnace should cycle on and the flame stay on for the normal cycle.
Posted on Jan 18, 2009
SOURCE: tempstar dc90 furnace will not light
Possible solution would be to push the reset button if you haven't already. I have had to do it twice on my dc90 in the last week.
If you look at the glass where you can see the combustion chamber, the glass is oval, follow the long axis of the oval toward the 'top' of the ignition chamber (my unit is laying down, with the blower on the west end and the combustion chamber on the east, as I am facing south). On top of the chamber are two protected spade clips. In between them is the reset. Make sure that the unit is off, press the button, and fire it back up.
Posted on Feb 20, 2009
  • 767 Answers
SOURCE: carrier super saver furnace keeps going on and off
Sounds like the flame sensor is dirty or bad. This sits in the burner flame when the burners are running. This usually has a single white wire connected to the back of it.
Posted on Jan 03, 2010
Pilot light won't light the burner
Clean the flame sensor with 0000 steel wool , the Ignition control module is typically at fault.
Mar 31, 2015 | Heating & Cooling
Tempstar DC90 willnot shut off
I can't stand the tempstar smart valve! Now I'm not sure what a dc90, but if you have a gas fire residential furnace I know what it is. The smart valve controls gas and flame proving only. The blower issue is probably one of the high temp safeties that has stuck. During a call for heat, your system verifies that all safeties are closed. If this sequence is not correct, then the unit assumes that the unit has overheated due to a high temperature safety issue, and brings the blower on to cool it down, normally for 90secs. Also if the unit is calling for heat when the power is turned off, still calling for heat when power is turned back on(like you said by throwing the switch), this will also bring the blower on for 90sec, then blower will/should turn off, and the heat cycle will start. So if your tstat is calling for heat(heat on and set temp higher than accrual temp), and you turn off power then turn power(main voltage) back on, this will bring blower on for 90secs. Now, the burners staying on is a different issue. I've not seen that in 15 yrs of service on a smart valve. There is probably 24volts feeding the "W" circuit, for some reason. On the control board there is a terminal block with R W G Y C. The W is your heat. This W receives a 24v signal from your tstat. Turn off power, remove W from the board, then turn power back on. If no heat then you've isolated your problem to the control wire coming from your tstat, or the tstat itself. If it continues to heat with W disconnected then its something in the furnace, circuit board? Hope this helps!
Mar 04, 2017 | Null Heating & Cooling
Unit does not stay lit
A few questions for you. If the thermostat is satisfied as in turned below room temp, does the blower shut off. Are the filters clean? Furnaces have a limit control that governs how hot the heat exchanger runs. If the limit switch opens for some reason the fan or blower will continue to run until the limit switch closes. So dirty filters? A very dirty blower wheel? A blower motor that is not coming up to speed, Could just be a bad limit switch that is opening up at a lower temperature than it should. I would also check the pressure switch sensing tube. The end could be blocked with deposits
Sep 06, 2017 | Heating & Cooling
Furnace cuts off before reaching set temp.
You can make sure it is not the thermostat by crossing or jumping the R and W terminals (or associated wires) together. This will keep the furnace calling for heat. As it is approaching set temperature, get in front of the furnace and inspect the air filter to make sure it is clean, watch the control module for any error codes that may be turning off the system prematurely.
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
Mar 07, 2010 | Honeywell Programmable Thermostat Heater
Furnace tries to light but misfires
Check the air filter.
Feb 26, 2010 | Goodman Heating & Cooling
Hi i hope you can help. I have a high effeciency furnace and the burners keep turning off.
Feb 16, 2010 | Dayton Gas Furnace Heater
My furnace will not shut off on auto. the fan will not run when switched to on. what should I check?
Some new furnaces have a feature that when it has an issue, it starts the room air blower until you reset the thermostat or kill power to the furnace. Not knowing what you have for a system I can offer you only how a furnace works and what you could look for "generically".
Jan 18, 2010 | Honeywell Heating & Cooling
Tempstar dc90 dual fuel system seems dead. the
Look for flashing light in bottom door and count flashes after furnace locks out. Read code or flashes with sticker on furnace panels.
Jan 10, 2010 | Goodman GMS90703BXA Heater
Amana furnace main burner intermitent
Sounds like dirty flame sensor. You can either clean it orreplace it.
Apr 21, 2009 | Honeywell Power Humidifier: Furnace...
Heating & Cooling Logo
265 people viewed this question
Top Heating & Cooling Experts
Paul Carew
Dan Webster
Dan Webster
Donni Steen