Question about AO Smith Miller / LSI / Home / Nordyne Replacement Furnace Motor 1/5hp 1050 RPM 115 volts OML64
Pressure valve closed, will not lite and stay burning?
Furnace will lite for only a moment and than shut off, flashes pressure valve closed.
Will not fire led light flashing 2 times
You didn't provide very much information, but I will try to help you. Here are some possibilities.
1. The pressure switch may not be closing, or is stuck closed all the time.
2. If this furnace has a hot surface ignitor, it may be faulty or not getting voltage.
3. If this furnace has spark ignition, the module could be faulty or the ignitor may not be positioned correctly.
4. The gas valve may be faulty, turned off, or may not have gas pressure to the valve.
There may be other issues, but I tried to cover the most likely causes. I hope this helps!
Dec 20, 2014 | Heating & Cooling
Furnace will not stay lite, flashes pressure valve closed
Too much or too little pressure. Check for air blockage or an ice blockage inside or outside the house. Were flames good color when lit?
Nov 12, 2014 | AO Smith Miller / LSI / Home / Nordyne...
Smart gas valve get 24v. but pilot will not spark or light
Do you have 24 volts at the gas valve terminals when the pressure switch closes?
Dec 17, 2013 | Honeywell Furnace Gas Valve Sv9501h2409
How to adjust pilot lite on a furnace
Select thermostat to off. Take front upper panel off of furnace. Looking at gas valve you should see a flat head or straight slot screw. This is the cap to access the adjustment. Look at the body of the gas valve real close. You may need to put on your glasses or use magnifying glass. It should say pilot in very small raised letters. Remove the cap. Look down into access hole and you will see the adjustment screw. It is a nylon screw so be careful not to strip it out. Place the correct screw driver, should be a small phillips or straight head. Turn gas valve to pilot and depress. Light pilot. While holding down, adjust nylon screw clockwise until flame envelopes 3/8 to 1/2 inch around thermocouple. Replace cap. Select heat and verify pilot stays lit. If the flame doesn't stay lit most likely your thermocouple is defective. You can purchase at your local hardware or Home Depot. Length doesn't matter.The thermocouple is heated and sends a DC signal back to the gas valve. There is another screw cap on the gas valve that adjusts gas pressure. Do not try to adjust the gas pressure to the gas valve because you need a special instrument (manometer) to adjust pressure. This device measures the water colume of the gas. A qualified technician would adjust this to 3.5" WC. for natural gas or 11" for propane.
Dec 09, 2013 | GPS
Bryant 345mav furnace shuts down early after one minute
Try to jump pressure switch as soon as the inducer come on and see if it stay longer. if it does you might have problem with draft or pressure switch itself defected.
Nov 28, 2013 | Heating & Cooling
Suddenly not working im not sure if there even is a pilot to be lit
Goodman have troubleshooting idiot lights on the board. Look for flashes and count em.
The flash explanations are printed on the backside of the blower cover on most models.
A sampling of various failure codes on a furnace:
Read one LED flash that stays on continuously to mean your furnace has no signal coming from the thermostat and will not operate. Turn the power off and check the thermostat for improper settings or connections.
Interpret one LED flash that blinks on and off to mean your furnace has locked out because it could not ignite after three tries, and must be reset. Interrupt power to your furnace for 20 seconds or lower the thermostat so your furnace does not try to heat, then reset the thermostat to the previous setting. After one hour of lockout, your furnace will automatically reset itself and try to operate as usual.
Decipher two LED flashes to mean the draft blower is not working, or your furnace has a short in the pressure switch circuit. Turn off the furnace power and repair a short or replace the pressure switch.
Read three LED flashes to mean your furnace has an open pressure switch circuit or it has an induced draft blower operating. Check the pressure switch hose of your furnace for blocks or an improper connection. Also, look for blockages in the flue, and tighten any loose wiring.
Translate four LED flashes to mean your furnace has a primary limit circuit open, possibly from loose wiring or blocked filters. Check and clean filters, tighten wiring and check the flue for blockages.
Interpret five LED flashes to mean your furnace senses a flame without a call for heat. This could be from a gas valve closing slowly or a burner flame lingering.
Read seven LED flashes as a warning of a low flame sense microamp signal. This could happen with a coated flame sensor or a lazy flame from poor gas pressure. Turn off the power and adjust the gas pressure according to the information on the rating plate.
See eight LED flashes as meaning an igniter circuit problem due to a bad igniter or an igniter connected improperly. Replace the bad igniter or check the ground wiring, making necessary corrections.
Decipher nine LED flashes to mean the high-stage pressure switch circuit will not close during a high-stage-induced draft blower operation. Your furnace may have a pinched or blocked pressure switch hose, a blocked flue or loose wiring.
Read continuous flashing on the LED to mean your furnace has a reversed polarity of 115 volts. Turn off the power and correct the wiring polarity after reviewing the wiring diagram.
Feb 03, 2011 | Goodman Heating & Cooling
Goodman 95 %furnace keeps saying low pressure is stuck. changed out low pressure switch and high pressure switch and still have same problem.
That thang might be sensing a lazy flame. In other words the flames took too long in the board's opinion to quit sensing the flame. Yall probably need to do pressure tap on the gas valve.
Here is a realistic look at goodman fault codes and what to check fer and I am assuming you are not a tech and don't know this already and am hoping it helps:
Now here is how it should all go down:
Bottom dollar: it all goes back to type of gas, the initial setup, the pressure tap. and how it is wired up to begin with.
This will give you an idea where to start I hope.
Dec 10, 2010 | Goodman GMS80903BNA Heater
My central heating is on lockout and the burner is with red light
A sampling of various codes on a furnace
Interpret five LED flashes to mean your Goodman furnace senses a flame without a call for heat. This could be from a gas valve closing slowly or a burner flame lingering.
Dec 02, 2010 | Heating & Cooling
Furnace won't stay running
1 FLASH
Furnace fails to operate.
• Integrated control module
diagnostic LED is
flashing ONE (1) flash.
• Furnace lockout due
to an excessive
number of ignition
“retries” (3 total)1.
• Failure to establish flame.
Cause may be no gas to
burners, front cover
pressure switch stuck open,
bad igniter or igniter
alignment, improper orifices,
or coated/oxidized or
improperly connected flame
sensor.
• Loss of flame after establishment.
Cause may be
interrupted gas supply, lazy
burner flames (improper gas
pressure or restriction in flue
and/or combustion air
piping), front cover pressure
switch opening, or improper
performance.
• Locate and correct gas
interruption.
• Check front cover
pressure switch
operation (hose, wiring,
contact operation).
Correct if necessary.
• Replace or realign
igniter.
• Check flame sense
signal. Sand sensor if
coated and/or oxidized.
• Check flue piping for
blockage, proper
length, elbows, and
termination.
• Verify proper induced
draft blower performance.
Nov 23, 2008 | Goodman GMS90703BXA Heater
Laars lite 2 LG or LD Pool Heater- Heater won't stay on
the control module is the problem it allows the heater to come on then turns off power to the gas valve.if you are not getting enough water flow the high limit is turning the heater off then your problem is flow.
Sep 20, 2007 | Lite On Laars Lite 2 Heaters: 250,000BTU...
AO Smith Miller / LSI / Home / Nordyne Replacement Furnace Motor 1/5hp 1050 RPM 115 volts OML64 Logo
46 people viewed this question
Top AO Smith Plumbing Experts
Lawrence Oravetz
Boyet Soriano
Boyet Soriano
Gil Shultz
Are you an AO Smith Plumbing Expert? Answer questions, earn points and help others