I'm having a problem with my boiler with a Honeywell L8124A,C aquastat. The temperature gauge is always showing around 170f. The HI limit is set to 180f and the LO limit is set to 160f. With a differe
More about my system. I have a Burnham RSA85TH-TB boiler, Homeywell L8124A,C Aquastat, 2 circulator pumps, one handles three floors with three zone valves. The other circulator pump handles a Buderus indirect water heater. I also have a Taco zone valve controller.
  • 1 more comment
  • Cliff Caron
    Cliff Caron Nov 12, 2014
    forgot to add Beckett burner
  • Cliff Caron
    I might have figured it out. It looks like a bad upper limit. It will only get as hot as the lower limit plus the 10 degree differential no matter what I set the upper limit to.
  • Cliff Caron
    Can someone please move thisquestion to Furnace and Boilers, I don't know how it got placed under Water Heaters. Thanks
    Master:
  • 876 Answers
It looks like you're not having a problem. 170 is right between the HI and LO limits. Not sure what the problem could possibly be??
Posted on Nov 15, 2014
2 Suggested Answers
  • 659 Answers
SOURCE: hot water boiler will not ignite
Check all your limit switches on this unit. One of them is either tripped or bad.
Posted on Apr 07, 2009
What temperature is it when boiler is on no 4?
Boiler temperature is usually controlled by a thermostat or aquastat. Maybe number 4 is firing rate?
Jan 23, 2015 | Water Heaters
Why will my boiler not fire up for heating but works fine on hot water
you have a triple aquastat that maintains a temperature level needed to provide hot water. but you are not getting the thermostat to operate the central heating. The thermostat is a switch that operates by temperature. if you have tried raising the thermostat and the system did nor kick in try jumping the thermostat terminals in the aquastat . if that works then the problem is either in the thermostat or the wiring to the thermostat. also with a electrical tester." while the thermostat is jumped" test the c1 and c2 terminals to see if power is going to the circulator. If not then you need a new aquastat. if you have power and the pump is not moving water replace it.
Oct 11, 2014 | Water Heaters
How do I disable low limit
WHY???????????????????
Only common sense option is to remove the Aquastat as you can adjust the lower limit down but NOT disable it. Bigger question may be What are you trying to do and do you know what you are doing???
Aquastats are made to START and STOP Pumps in Recirculation systems at settable limits not run them 24/7.
Running a pump 24/7 voids the heater warranty.
Sep 11, 2014 | Honeywell L8124a 1007 Triple Aquastat...
Which contacts do I connect the boiler to? I thought it was the TT, but I am not getting any voltage on them.
Here is a link, that includes the wiring diagram:
http://www.forwardthinking.honeywell.com/related_links/water/aq2000/install/69_1974.pdf
It looks like the 'T-T' terminals match up with 'T-T' terminals on the Boiler Aquastat-- Do you see that control?-- and do you have wires between those controls.
Power to this Control Module is all the way to the left on the connector terminal board-- the ones that say:
R (1) C (2) - Power In
Also: Did you realize that this control is a modulating control-- Not just an 'On-Off' control?
This control has outdoor sensors, that modulate the temperature of the water temperature-- The warmer it is outside, the lower it sets the Hot Water Temperature-- thus saving fuel-- yet assuring that on very cold days, you still get Hot enough water to be comfortable in your occupied space.
Oct 12, 2013 | Honeywell AQ25142B Aquatrol Boiler Reset...
Wickes 102 combi boiler constantly loosing water pressure
It sounds like your thermostat could be the problem. Have you noticed the boiler cutting off at all, or does it run continuously until it goes out on low water?
You stated, "when boiler is on", so I am wondering how you get the boiler on. If your boiler is controlled by a thermostat, you need to check it for a cold draft possibly from behind the thermostat in the wall where the wires come through. The thermostat should never be on an outside wall. The thermostat could be defective.
An aquastat can also control your boiler. If you have an aquastat, check the setting, typically 175 - 180 degrees. You should also have a "high limit" which should be set at 210 - 220. Some people run that high side limit higher; not a good idea - defeats the purpose. If the aquastat is set too high, the boiler will operate too hot and the problem you have will occur.
"pressure rises and pressure relief valve opens" This could mean that your pressure switch is prematurely venting. Check boiler temperature to see exactly at what temperature the T&P valve purges. If it blows off below the high side setting, either adjust or replace. The T&P valves are usually not adjustable. That blow off temperature is stamped on the head of the valve. So, if it discharges too soon, replace it.
Have you actually seen evidence thgat the T&P valve is opening? You may have a bad bladder in your expansion tank and your system may have air in it. Your boiler should have 12 psi when cold and 20 - 22 psi when operating. Check your boiler pressure guage.
this eventually drops below the minimum operating pressure" Technically, there is set point for a NO MINIMUM OPERATING PRESSURE. That is a function of the amount of water in the boiler. If the T&P is blowing off, it will vent water from the boiler and the boiler pressure will go down. There is a minimum operating TEMPERATURE.
Your boiler could be low on water. You will have to manually fill the boiler. Be careful of thermal shock to the boiler. Feel the piping, and fill only when the circulator is running. Make sure the water is not going directly into the boiler. The supply water should go into the circulating supply side which feeds the radiators, radiant floor, or base board circuits.
All this will adversely affect your hot water. The heat exchanger for the potable hot water may have scale build up in it. Using the hot water keeps the boiler running, and a scaled heat exchanger will give you cooler hot water and the boiler keeps running. If this is a problem, you will need to replace the heat exchanger. A better idea is to not use the boiler for your domestic hot water. Why run the boiler in the summer?
Feb 02, 2013 | Water Heaters
Want to raise the water temp
Stand alone water heaters have temperature controls in different locations.
Most residential electric water heaters operate on 240 volts. Please, shut off power first whenever you need open or remove panels for adjustments or servicing.
"Traditional" electric water heaters have them behind removable panels - like the top and bottom gray panel on the water heaters on the right side of the photo. Both panels have adjustable controls behind them and both should be adjusted to the same setting.
Some newer electric water heaters use electronic controls. These may be accessible without removing panels and even have digital displays. Others have controls that are located on the top of the heater - behind a panel. Electronically controlled water heaters may or may not need to be powered on when making adjustments. Check your manual if in doubt.
Gas (propane & natural gas) type water heaters have the temperature control on the gas valve. There are often two controls on the valve, one for the pilot (off, light and on positions) and a second for temperature adjustment.
A tankless water heater built into your home's furnace is controlled by an "aquastat". An aquastat is a fancy term for a thermostat to control water temperature. A typical aquastat is mounted directly on or very near the furnace and looks like this:
Inside, are several temperature settings. Here's a photo of the interior of the Honeywell aquastat:
The Hi dial should never be set to a value lower than the Lo dial. "Safe" settings are Hi = 180, Lo = 160 and Diferential (above "Lo") = 10. You'll need to tweak these up a bit to make water hotter. You should read more about settings for these aquastats here. Skip down to the section titled "What Settings To Use on a Heating Boiler Aquastat Combination Control"
I hope this helps & good luck!
Nov 22, 2012 | General Electric GE SmartWater Household...
Is it possible to lower the top temperature on the thermostate. I can change the lower temp but not the max which I wish to set below the 180 level. Thanks
there is a high and a low limit on these units, the two control knobs are actually the reverse of what you are trying to accomblish,first lower the bottom or low cut off temp first then the high temp ,it must cycle a couple times for it to adjust
Jun 06, 2011 | Honeywell L4103A1019 combination aquastat....
I want to increase the boiler temp by using the your aquastat
Warning! Can cause electrical shock! Here is the instruction manual
for L7248c
http://customer.honeywell.com/techlit/pdf/PackedLit/68-0281.pdf
Jan 12, 2009 | Water Heaters
Boiler overheating
the problem there a relay stuck or thermostat bring on the pump & you can lower your high limit aquastat!! also the flow valves can bypass hot hot water risers time to put in a seperate water heater domestic coil are not energy efficient !!!! aquastat high limit set @ 180f deg low limit set @ 140f deg!!!
good luck!!! tim
Oct 08, 2008 | Water Heaters
Water Heaters Logo
127 people viewed this question