Pilot on boiler will not light. What are the troubleshooting steps. How do i know the valve or board are good?

Posted by on

  • 3 more comments 
  • btandpt Jul 03, 2009

    New thermopile and continuity in the heat circuit. Is there a way to test the valve and board?

  • btandpt Jul 03, 2009

    ? JUmp

  • btandpt Jul 03, 2009

    how do i jump out thr heat circuit

  • btandpt Jul 04, 2009

    IT IS A NEW GENERATOR , HOW DO I JUMP OUT THE VALVE TO CALL FOR HEAT

  • btandpt Jul 04, 2009

    Im sorry i was not clear the pilot is on... the themopile is new... i have 600mv at valve .... any other suggestions... can you tell me how to jump out the heat circuit to test valve?

×

3 Answers

  • Level 2:

    An expert who has achieved level 2 by getting 100 points

    All-Star:

    An expert that got 10 achievements.

    MVP:

    An expert that got 5 achievements.

    Vice President:

    An expert whose answer got voted for 100 times.

  • Expert
  • 294 Answers

Hello Btandpt
let me tell you that the possible reasons for the problem you are currently facing are..

  • If you can get in, clean out the jet with a pin. Likelihood is the flame is only a fraction of what it should be, and isn't keeping the little safety valve open. call service engineer.
  • dirty pilot symptom yellow flame (lower temperature soot on thermocouple)
  • worn thermocouple symptom blueflame will not hold
  • faulty gas valve symptom as above more expensive to fix
  • faulty case seal goes out on windy day
  • vitiation lack of air, sooting, (boiler needs servicing gas boilers shoudn't ever soot).
  • lose t\c connection on gas valve
  • some boilers have a over heat swich in the t\c cuircut it may have tripped. why? maybe the pump or the thermostat etc etc as you say that thermocouple is new it does not mean that a new one is always Ok.. please do check it again.

Posted on Jul 04, 2009

  • Level 3:

    An expert who has achieved level 3 by getting 1000 points

    Superstar:

    An expert that got 20 achievements.

    All-Star:

    An expert that got 10 achievements.

    MVP:

    An expert that got 5 achievements.

  • Master
  • 2,071 Answers

Normal 0 false false false MicrosoftInternetExplorer4 /* Style Definitions */ table.MsoNormalTable {mso-style-name:"Table Normal"; mso-tstyle-rowband-size:0; mso-tstyle-colband-size:0; mso-style-noshow:yes; mso-style-parent:""; mso-padding-alt:0in 5.4pt 0in 5.4pt; mso-para-margin:0in; mso-para-margin-bottom:.0001pt; mso-pagination:widow-orphan; font-size:10.0pt; font-family:"Times New Roman"; mso-ansi-language:#0400; mso-fareast-language:#0400; mso-bidi-language:#0400;} Its better you replace the pilot lamp generator which is in the pilot assembly. It is the piece with a silver cable coming out of it and that cable splits open into a red and white wire at the gas valve, That piece holds the valve open once it is hot enough and is likely not putting out enough voltage to do its job. Millivolt models have a thermocouple or pilot generator that may be faulty or weak. Loose or rusty connections of the thermocouple to the gas valve or loose coil connection, or short in these wires can shut off a pilot

Good luck;

Regards;
VOTIT

Posted on Jul 04, 2009

  • LORETO LACARON
    LORETO LACARON Jul 04, 2009

    Sorry for error in connecting i'm only input again my sollution ;



    Its better you replace the pilot lamp generator
    which is in the pilot assembly. It is the piece with a silver cable coming out
    of it and that cable splits open into a red and white wire at the gas valve,
    That piece holds the valve open once it is hot enough and is likely not putting
    out enough voltage to do its job. Millivolt models have a thermocouple or pilot
    generator that may be faulty or weak. Loose or rusty connections of the
    thermocouple to the gas valve or loose coil connection, or short in these wires
    can shut off a pilot

    Good luck;






×

  • Level 3:

    An expert who has achieved level 3 by getting 1000 points

    All-Star:

    An expert that got 10 achievements.

    MVP:

    An expert that got 5 achievements.

    Genius:

    An expert who has answered 1,000 questions.

  • Master
  • 1,847 Answers

posible causes
1.dirty pilot symptom yellow flame (lower temperature soot on thermocouple)
2. worn thermocouple symptom blueflame will not hold
3. faulty gas valve symptom as above more expensive to fix
4. faulty case seal goes out on windy day
5. vitiation lack of air, sooting, (boiler needs servicing gas boilers shoudn't ever soot).
6. lose t\c connection on gas valve
7. some boilers have a over heat swich in the t\c cuircut it may have tripped. why? maybe the pump or the thermostat etc etc


Also check ..

http://www.letsfixit.co.uk/html/boiler_hints.html

Thanks
Kindly rate the answer
Kevin

Posted on Jul 03, 2009

1 Suggested Answer

6ya6ya
  • 2 Answers

SOURCE: I have freestanding Series 8 dishwasher. Lately during the filling cycle water hammer is occurring. How can this be resolved

Hi,
a 6ya expert can help you resolve that issue over the phone in a minute or two.
best thing about this new service is that you are never placed on hold and get to talk to real repairmen in the US.
the service is completely free and covers almost anything you can think of (from cars to computers, handyman, and even drones).
click here to download the app (for users in the US for now) and get all the help you need.
goodluck!

Posted on Jan 02, 2017

Add Your Answer

Uploading: 0%

my-video-file.mp4

Complete. Click "Add" to insert your video. Add

×

Loading...
Loading...

Related Questions:

1 Answer

How to relight pilot on boiler


Every boiler will have manufacturer lighting instructions on the unit, so be sure to read it thoroughly and turn off the gas for 5 min to make sure there is no gas build-up around the boiler. Some have electronic ignition and some require a manual lighting of the pilot. If the control knob has only ON-OFF, it has electronic ignition. Simply turn off the power (at the electric switch on the boiler or at the breaker box) and then turn it back on and it will relight itself when heat is needed) If it has ON-OFF-PILOT, you will have to light it manually. You will have to turn the gas valve knob so the arrow is pointing at the word "pilot" and depress the knob, while lighting the pilot with a lighter or match. Continue to hold the knob down after the pilot is lit for about 30-45 seconds to allow the thermocouple to heat up. If you release the pilot knob and the pilot stays lit, you can turn the knob to the "ON" position and the burner will light. Please be careful. if you are not sure what you are doing, call a professional.

Mar 01, 2015 | Heating & Cooling

1 Answer

Why wont furnace light past the thermol coupler


There is really not enough information here to go on. If this furnace has a thermocoupling, the pilot will need to be lit manually. Follow the manufacturers lighting instructions carefully. If it still will not light you may have a dirty pilot assembly or a defective gas valve. Modern furnaces do not use a thermocoupling. There is no standing pilot light. Each time the furnace needs to be lit it will be done electronically. Many reasons why it wont light in this case. Safety control could be preventing it from lighting for safety reasons. A bad ignitor, ignition module, circuit board, gas valve, pressure switch, gas supply, induced draft motor, blocked or restricted flue pipe, cracked heat exchanger, dirty flame sensor, ect. ect. ect.

Oct 07, 2014 | Coleman 7990-319p Evcon Gas Furnace...

1 Answer

Light the pilot light on weil mclain gas boiler


Joanne If there is a standing pilot on the boiler. Put the gas valve to the pilot setting and push in on the valve while holding a long match or BBQ lighter @ the pilot assembly that is behind the small access port at the top of the gas train assembly. Dont hold the pilot knob doun without having a flane @ the gas outlet of the pilot assembly or gas will build up and could blow out of the port and hold the gas valve in for about a minute or two and let it go it should stay light when you let it go .If it does not sta lit and it IS a standing pilot there- is a thermo-coupling that may be bad If the pilot does not stay lit.
If there is an electronic ignition rather than a standing pilot then you do not need to light it will light itself if the electronic ignition is bad or if the flame sensor is dirty. If you remove the pilot assembly from the gas train and clean the flame sensor rod with a piece of .0000 steel wool it could help. If not you may want to call a licensed pipe-pitter ( OR plumber depending where you live and the local codes).
If you don't thing you could do it yourself then call a licensed pipi-fitter or plumber. (Gas only has to leak once for there to be a problem so please do call someone licensed if you don't think you could do it your self.), http://www.weil-mclain.com/en/weil-mclain/products-services/
Here is a link to the manufacturer you should be ale to fing your equipment and the install instructions, if you look around .You can download a PDF and print it
Good luck and stay warm

Feb 08, 2014 | Weil-McLain CGa-25-SPDN, NG, Gas Fired...

1 Answer

I HAVE A 20+ BRYANT BOILER THE PILOT LIGHT IS OFF HOW DO I TURN IT BACK ON PLEASE HELP THANKING YOU IN ADVANCE MS I


Turn the gas valve to pilot. Push knob down & hold. While holding, light pilot & keep knob held down for one minute. Let go of knob & see if pilot stays lit. then turn knob to on position. Boiler should then turn on.

Oct 18, 2010 | Bryant Heating & Cooling

1 Answer

Got a ravenheat ls 1oot combi boiler not working red light on timer on not making any noise works every now and then for short periods


Hi,
I have a ravenheat 820/20(t) boiler and the pilot will not say alight, I have 20mV from the thermocouple(through the safety switch) and its had a new gas valve fitted(good earth continuity).The heating system is holding pressure at 1.2 bar.
Has anyone got any ideas what could be holding the pilot 'OFF'.
I CANNOT SEE ANYTHING ELSE IN THE PILOT CIRCUIT.
PLEASE HELP !

Dec 20, 2009 | Water Heaters

1 Answer

How do you light a ravenheat pilot light


push in the yellow or grey button on the gas valve and click the piezo ignighter repeatedly keep the gasvalve button depressed for 20 seconds and the boiler should light if it does not you have a fault come back for more advice if this happens

Sep 30, 2009 | Calvin Klein The Field Controls Company...

1 Answer

I have an old ideal elan 2 boiler. The pilot light has gone out and wont re-ignite. I have pressed the ignition switch in but there is not even a spark. Does anybody know where the re-set button is on...


Hi, to light the pilot you must first ensure the gas valve button (Grey with 3 symbols on it) is placed in the ignition position, then, while holding the button in towards the gas valve depress the orange ignitor button several times, hold the gas valve button in for about 30 seconds once the pilot lights. If it fails to light and you cannot see a spark when you depress the ignition button the cable could be faulty, the ignitor corroded or damaged or the pilot could be blocked or the gas turned off. If it is an Elan 2 CF boiler there is no reset button.

Apr 26, 2009 | Kitchen Appliances - Others

Not finding what you are looking for?
Teledyne Laars Laars Lite 2 Pool Heater 250,000 Btu / Natural Gas  Logo

Related Topics:

131 people viewed this question

Ask a Question

Usually answered in minutes!

Top Teledyne Laars Pool & Spa Experts

paulcarew

Level 3 Expert

2464 Answers

Jay Finke
Jay Finke

Level 3 Expert

1338 Answers

Bill Jordan

Level 2 Expert

372 Answers

Are you a Teledyne Laars Pool and Spa Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...