Heat stripe and compressor on at the same time
I have a similiar problem with my Duo Therm. When I select the cool position on the t-stat both the heat strip and the compressor try to kick on. This is overloading the 20amp circuit. I am still struggling to find out why this is happening. I have replace both the t-stat and the relay board and still haven,t found the problem.
  • mark_roge357 Jul 09, 2009
    Jeff, thanks for your help. With further investigation the problem was this: I needed a new t-stat so I went to the supply store and showed them my old one and he gave me a new one. The problem is one is for a heat strip and the other is for a heat pump. If you look carefully at the circuit board you will notice a difference at to where the diodes are placed. I unsoldered the diodes in the new t-stat and positioned them like the old t-stat and the unit is working fine. Thanks again
    An expert whose answer gotĀ voted for 100 times.
    Novelist:
  • 127 Answers
Is this a wall mount thermostat or manual control unit? What is the model of the air conditioner? The only way that this is going to happen is that power is jumping somewhere to the heater coil from the cool side.
If it is a wall mount thermostat, the yellow wire is the cool mode (compressor on) and both the tan and blue wires are the fan mode. The orange wire is for the heat strip. So if you set the thermostat on High/Cool, then you should have power at the yellow and blue wires, not the orange. If the orange wire is energized, then there is a problem.
Remove the orange wire from the thermostat, try it again. If the breaker trips, then remove the wire from the connection at the relay board. Once again, try the unit. If the breaker trips due to the same problem, then it has to be a bad relay board. If the breaker does not trip this time, then you have problem with your wiring between your thermostat and the control unit.
Sounds like you don't have manual controls since it has a relay board.
Hope this helps,
Jeff
Posted on Jul 03, 2009
Ac compressor runs but will not cool
check thermostat, replace capacitors amp compressor to be sure its running if not relay module issue.
Aug 08, 2015 | Dometic 651815 Duo Therm 13,500 BTU...
Duo therm heat pump blowing hot air only
relay module or communication cable from t-stat issue.
Apr 02, 2014 | Dometic 459186 Duo-Therm Brisk Air...
I have a Duo Therm rooftop AC inb my 2004 General Coach park model trailer. It has a heat/cool thermostat with a slider for t-stat control and hi/low on/auto fan switches. On heat it works fine. ON cool...
Got to be a relay/ contactor that is bad. Tstat is not energizing the relay to bring the compressor on. If you can understand the schematics you need to find where your high voltage stops. If you give direct power to the compressor and it runs then obviously power is not going through relay. Either bad relay or that the relay is not being energized at all by the tstat with low voltage. Good Luck
If you need further help, reach me via phone at https://www.6ya.com/expert/thomas_092728000e6acb79
Mar 11, 2017 | Heating & Cooling
SWITCHING A DUO THERM THERMOSTAT TO A WHITE RODGERS 300 HEATING AND COOLING THE NEW ONE WE HAVE Y,W,B,RH,O,RC,G,A. TERMINALS OLD ONE HS, 7.5,COOL,FUR,HI FAN,FAN, GND,
FUR - OLD T'STAT - (W) NEW T'STAT
COOL- OLD T'STAT - (Y) NEW T'STAT
HI FAN - OLD T'STAT - (G) NEW T'STAT
7.5 - OLD T'STAT - (RC) ON NEW JUMPER WIRE - (RH)
need full model number of w/r thermostat for other wires
Jul 02, 2011 | Heating & Cooling
Duo Therm Fan Blows, No cool air. Worked yesterday, not today?
most likely compressor running could be capacitor, breaker,relay,or compressor it self start by checking power to unit
Aug 22, 2009 | Heating & Cooling
Dometic Rooftop RV Air Conditioner Logo
125 people viewed this question
Top Dometic Heating & Cooling Experts
Bill Long
Tim Whalen
Are you a Dometic Heating and Cooling Expert? Answer questions, earn points and help others