This is a 3-phase UPS. The Voltages for the three phases are 243V, 251V & 245V but the input inside is showing 299V.
It gives a beep and gives a message : "voltage out of range".
Please help
  • 1 more comment
  • mtac Nov 13, 2007
    Thanks. We actually foungd that the circuit breaker in the DB of the building was a 1ph CB; so we changed this and reset the memory of the UPS. So it worked.
  • pzooft Dec 08, 2007
    My BlackoutBuster won't stop beeping every ~10 seconds. I tried unplugging everything and turning it off, but it beeps again when I plug it back up. It never did this before, but the power went off today and now I can't stop the beep. Please tell me how to stop the beeping.
  • Anonymous Mar 20, 2014
    Please help
  • 46 Answers
A 3 ph ups normally can work upto 450 volts because the normally its the transmisson range of voltage
220 to 250 is the voltage range of normal 1 ph line so check for proper line voltage or load voltage
Posted on Nov 13, 2007
How i can change input configuration of APC SURT15KRMXLI from single phase to three phase Try page 6 of this document. It shows the connections and jumpers required. Make sure changes are made by a qualified electrician/technician who knows what they are doing so as not to damage UPS and not receive electric shock
Oct 14, 2015 | APC SMARTUPS RT 15KVA RM 230V...
what caused the UPS to transfer to Bypass? could be inverter fault, would you please check your battery set, maybe the input power is outside the tolerance and causing UPS to discharge the battery set , as well when battery set reaches the end of discharge it is causing the UPS to transfer to bypass and there is something missing on the input yellow Phase.
if the above is not true check the load type that is connected to the UPS output that is causing UPS to switch off in 10 minutes time.
Apr 17, 2014 | MGE UPS Galaxy 3000 UPS System
Mge galaxy 4000 bp ss supply failed
Make sure that Bypass Phase Rotation is A-B-C. Check that Bypass voltage is within a tolerance of 208 +/-5%. Frequency tolerance is 60hz +/- 1hz.
Any condition not met, and Bypass will not be available
Apr 01, 2014 | APC MGE GALAXY 4000 75KVA-3-PH OL UPS 208V...
Status : inverter overload - appear / MGE Galaxy 5000
maybe 1 of the three output phases is overloaded please check and distribute the load correctly on the output phases
Jan 23, 2014 | MGE Computers & Internet
Smart UPS VT 10KVA fault "Mains Not Available. Input Freq/Volt Out of Range". All phases input and output giving the expected voltages 240V and frequency OK at 50Hz.
Sounds like you hooked up the input to the UPS on the bypass. Either way either way your input is not there. Also make sure you configure the UPS prior to placing online.
Oct 04, 2013 | APC Smart-UPS VT 10kVA - SUVT10KH2B2S UPS...
Case 1: 220 V, 50Hz applied to s 3000 measuring the output as follows: 1- phase to ground 220 2- Phase to neutral 219 3- ground to neutral 1 volt Case 2 disconnct the input 220 V we have 1- phase...
Did you measure with a true RMS meter?
If yes,the results are normal,but your ground connection is not very good.
The case has 110v potential (exactly half of the input&output 220v) because of the input and output capacitor filters (a capacitor is conectet from phase to casis and an other from neutral to chasis,thus resulting a 1/2 voltage divider). Because of this,the earthing is necessary.
Jan 16, 2011 | MGE Evolution S 3000 VA RT2U Rack (68465)...
Mge ups making noise after applying coolant
If I knew the specific UPS model, I might be able to provide some better input. At this point, I would contact Eaton product support. Eaton acquired the MGE single-phase UPS line a couple of years ago and assumed support/service for these products:
Toll Free: 1 800 356 5737
Nov 03, 2010 | MGE Computers & Internet
How do you calculate low phase voltage of a three phase four wire system without useing voltmeter?
u can take three incadescent bulbs of same rating, connect them in 3 phase star connection, means 3 phase 4 wire connection..connect it across supply..the bulb connected across low voltage phase will glow dimmer than other two
Jun 19, 2010 | Zenith ZTG Nema-3R, 400 Amps Three Phase,...