Thermostat starts furnace, burner goes on, comes up to temperature and the fan keeps trying to start and shuts off. The motor just keeps bumping over, will run for a few seconds then stop.
  • mdaly86885 Jun 26, 2009
    Are you sure the problem is with the motor?
    Doesn't the fan/limit switch control the motor-
    couldn't the switch be bad? The motor will wind up a little each time it tries to start, then shuts down.
    Top Expert:
  • Honeywell Master
  • 79,865 Answers
The fan is turned on by a relay, replace that relay, the contacts are most likely burned in the relay, also check all the connectors to the fan and it's controls for poor connections or signs of overheasting, the motor may also be going ouut and drawing excessive current.
Posted on Jun 26, 2009
  • 749 Answers
Seems like there is a problem with the motor, it will need replacing for it to correctly work.
Furnace reaches temperature set then shuts down and restarts 8 times before final shutdown.
When you say the the furnace re-starts 8 times before shut down, what is cycling 8 times? just the indoor blower or is the main burner re-firing 8 times? If it's only the fan it sounds like the fan control.
Mar 07, 2018 | Coleman Heating & Cooling
My good man furnace model gmh80903bnca will not get to temp fan shuts off and burners keep burning then kicks off on high limit then starts process over but never gets to temp set at 655
If you have a switch that can manually turn on the fan, try it to verify the fan works. This is what I think is happening. The normal operation should be thermostat calls for heat, inducer fan comes on, pressure switch closes, igniter glows, main burner ignites and then in 30 or so seconds the fan comes on and stays on until the thermostat is satisfied. Once the thermostat is satisfied the burner shuts off and the fan runs for approx 120 seconds then shuts off. I think the control board that automatically turns your fan on is faulty. On most modern furnaces if the auto fan control fails and the furnace gets to hot and limits, when the limit opens and shuts off the burner it also energizes the fan motor to cool the heat exchanger.
Jan 13, 2018 | Heating & Cooling
1999 Goodman down draft natural gas furnace. It starts as normal, the burners fire and it warms up, but the blower doesn't start, after a couple minutes the burners shut down and the blower immediently...
IT SOUNDS LIKE THE FAN CYCLE RELAY OR BOARD IS NOT MAKING THE FAN COME ON WHEN IT SHOULD THE BURNER SHUTS OFF PROBABLY BECAUSE IT REACHES THE HIGH LIMIT.
Feb 03, 2015 | Heating & Cooling
Heil nulk075dg05
You have a dirty or bad heat sensor. When you remove the front panel on you furnace you will see a probe that is 2 or 3 inches long that is in the flame when the furnace fires up. If it doesn't detect a certain temperature within the first 30 or 40 seconds it shuts down the furnace. You can either clean the probe off with sandpaper, or purchase a new one. They aren't very expensive and are easy to replace. In my experience it is usually a build up of carbon on the sensor and a good cleaning with sandpaper and alcohol usually takes care of the problem.
Feb 04, 2014 | Heating & Cooling
Goodman furnace Model GDS80703AXBB -fan comes on then igniter light comes on, then burners turn on but shut off right away and wont stay lit. Now igniter light wont come on so burners not coming on at...
Sounds like either the flame sensor is not working.
The sequence for starting the furnace is:
1. extraction fan on
2. pressure sensor (for fan)
3. ignitor (spark or glow plug) comes on
4. gas valve opens up
5. ignition of flame
6. flame sensor (or temperature sensor)
7. plenum temp. sensor
8. main fan starts
It is most likely that the flame sensor is dirty or gone,
or (and I hope not), the module is gone and needs to
be replaced.
Sep 10, 2017 | Heating & Cooling
We have a tempstar down draft furnace. 2 years ago the heat exchangers where replace because we were told they were cracked. This year the downdraft motor was makikg a lot of noise & we were told the...
Sounds like the low limit or high limit is out these control the fan motor.They are usually set to kick on around 150 degrees and set to go off around 95 to 100 degrees. Over heating does happen with cracked heat exchangers and it can possibly take these two items out. Normally your furnace should run approximately five minutes or a little less then your fan motor comes on and then for cooling down burners should drop and the fan motor should run again roughly five minutes or so then shut down. Times may vary as to your settings.
Dec 20, 2010 | Heating & Cooling
Furnace cuts off before reaching set temp.
You can make sure it is not the thermostat by crossing or jumping the R and W terminals (or associated wires) together. This will keep the furnace calling for heat. As it is approaching set temperature, get in front of the furnace and inspect the air filter to make sure it is clean, watch the control module for any error codes that may be turning off the system prematurely.
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
Mar 07, 2010 | Honeywell Programmable Thermostat Heater
Honeywell thermostat TH6110D1021. Blower comes on
Hi, You are right, fan is on a time delay in the heating cycle, and after burners fire that is when this delay comes into play. You have a preset factory temperature that determines the cycle on time for the fan, and the off time after the burners shut down also. This will not be in the thermostat, but in the fan/limit control the is mounted on the face of the furnace, with a probe inserted into the fire box.Depending on how old or new this unit is, will depend on the type control you have.It may be just a high limit switch, or the 1st I mentioned.If so, It rotates in the burner as the temperature rises, to turn the fan on and off.Disconnect power, remove cover, and 2 screws.Slowly remove the control and gently clean the probe. Turn the dial if this one has it and you will be able to hear it click. This click is contacts closing to start fan operation.Reinsert and try again. If problem continues, you will have to replace it.They do tend to stick closed/on, in the heat cycle from time to time and a cleaning sometimes will solve this problem. Not knowing how old this furnace is and type, make it difficult to give you a correct diagnosis, so check this fan control as I have explained, and if your system is of a different type, please let me no so I can correct this problem. Sincerely,
Shastalaker7
Dec 11, 2009 | Honeywell Programmable Thermostat Heater
New honeywell thermostat on new gas furnace not working
sometimes there's a differential setting anywhere from 1-3 degrees, see if you can make sure it's down to 1