Furnace fan What does a fan limiter switch do? When they fail can the fan run continuously?
  • 1 more comment
  • Jim Beyer
    Jim Beyer Nov 05, 2007
    It's a Carrier and the thermostat is an electronic programmable I installed about 12 years ago.
  • Jim Beyer
    It's a gas furnace with a separate a/c unit (outside.) The fan will continue running after the heat cycles off and will blow cool air (obviously) until the heat comes on again. The only way to stop the fan is to kill the power at the furnace. The thermostat won't control the fan.
    I was thinking maybe the tstat crapped out on me because when you switch to "auto" and there is no call for heat the fan should switch off. The limit switch got my attention because I see a thermal device on it that I assume keeps the fan off until warm air is detected.
  • Jim Beyer
    Jim Beyer Nov 06, 2007
    OK-Looks like the tstat isn't causing a problem-disconnecting the green wire and restarting the system didn't help. The fan runs as soon as you power the unit up. Turning the system off at the tstat doesn't turn the fan off.
    I looked at the limiter wondering if the thermal device could be the cause.Is this a normally open switch that closes when the heat heats it up?
    Sergeant:
  • 288 Answers
What type of system do you have? The auto/on switch on the thermostat will cause the fan to run continuously.
Posted on Nov 04, 2007
  • 1 more comment
  • Rob Luna
    Rob Luna Nov 05, 2007
    O.K. assuming you programed the thermostat that shouldn't be the problem unless its defective. The fan limiter you are referring to is I believe the time delay relay. When you turn the thermostat off does it continue to run? Or does it come on instantly when heat is selected? Also is it a gas furnace, heat pump, electric or what?
  • Rob Luna
    Remove the furnace panel. You should find 4 small wires coming from the thermostat and connecting to the furnace somewhere. They will be red, white, green, and blue (yellow is sometimes used for blue). unplug the cord. Disconnect the green wire from the furnace, make sure its not touching anything. Its only 24 volts, but it will short the transformer out if it touches something. turn the power back on. If the fan does not come on, set the thermostat as you would for heat, if the unit functions correctly now, its either the thermostat or the low voltage wires are jumping across somewhere.
  • Rob Luna
    Rob Luna Nov 06, 2007
    Yes, some are time delayed, yours sounds heat activated. Try removing one of the wires in the same fashion as the thermostat and see what happens.
I have new blower motor. it dosen't stop running
Could be a bad blower motor resistor,mounted by the blower.
Sep 28, 2016 | 2002 Dodge Ram Pickup 1500
Blower fan continually runs
It may be but the fan control may be set to turn off at to high a temp, or theres a short between ;r; and g at the stat or furnace or sequencer, IF it runs through it. A limit or rollout switch may have failed but this will keep the unit from firering. Check for a manual blower switch that may be on. At stat it should be at auto and alsso at the fan control. A stuck relay is always possible,
Mar 08, 2015 | Coleman Home Electric Furnace Eb15b/Eb15d
Hi, I have Starling QVX heater. The air flow space where the limit switch is located heats up to around 210 Degrees after the furnace runs for awhile then the switch cuts off the gas and the fan...
The should be a temp stamped right on the limit switch telling you it's limit. It is very possible it is going bad. I know they make adjustable limits but would not go too much higher than what is in there now. Good Luck!!
Apr 27, 2017 | Sterling RF30 Natural Gas Garage Heater
We have a White-Rodgers 1F80-51. The fan blows
Usually when the furnace blower motor runs all the time
The limit switch or rollout switch is usually open or bad.
The furnace board is seeing that one of those switches is open, so it brings the blower on to try to get the heat out of the combustion chamber area, so the switch will close. But if the switch is bad and won’t close, the furnace board will keep the blower running continuously.
May 31, 2010 | Heating & Cooling
When furnace runs blower won't run.as soon as furnace stops blower runs. They never both run.
Sounds like fan limit switch/fan timer
This will cause the main burner to run untill the over tempreture switch is tripped therefore shuting gas supply and running fan on high till over heat condition is resolved then it will restart burner and repeat
continuing to run heater like this will cause heat exchanger split.
May 13, 2010 | Heating & Cooling
Goodman GS9 propane furnace inducer motor runs continuously
it sounds like the low temp limit switch, the one that cools the furnace down with the burner off and the thermostat open, when it cools to a point the fan stops, the other switch in burner area turns burner off/on, hope this helps
Jan 31, 2010 | Goodman GMS90703BXA Heater
I have a dyno glo rmc-fa100dlx forced air heater. It will light and work for a few minutes, up to about 5, then it will stop heating and the fan will keep blowing. any ideas? thanks!
If the unit comes on and runs but then shuts down, that sounds like an indication of a high limit trip.
Most, if not all, furnaces have high limit switches that keep a constant check on the temp inside the furnace or air handler. On most systems, once this high limit switch has been made (got to hot), the limit switch breaks control voltage to the heating device (strips, gas, fuel, etc.etc..). The blower motor continues to run until the high limit has dropped in temp and reset itself.
On some models, the high limit is a manual reset, meaning you need to reset the switch yourself or shut the unit off and then back on to reset it.
Check all filters and replace as necessary. Check the coils and fan blades for dirt build-up and cleanliness. Check motor belt (if applicable). If all these fail to solve the problem, then your issue either lies within the blower motor itself not moving enough air for proper heat transfer. Or the high limit switch itself is failing.
Jan 09, 2010 | Heating & Cooling
Fan continues to run after heating
That's the fan switch. It's a thermostat that controls the fan coming on and off, it's probably failed and needs to be replaced. You can see it if you take the front off the furnace, the wires come off it and go to the fan motor.
Jul 13, 2009 | Dayton Gas Furnace Heater
Goodman a/c blower fan will not shut off
Unhook the thermostat wires on the furnace. If the blower shuts off then your problem is either the thermostat or the thermostat wires. If it contiues to run check you high limit switches next. If all else fails you most likely have a bad blower relay. On most modern furnaces the blower relay is part of the circuit board.
Good luck
Mar 29, 2009 | Goodman CLQ36AR49 Air Conditioner
Air conditioner/furnace squirrel cage fan remains running when th
Ensure you don't have a short in your therm wires. Disconnect them, if the furnace continues to run, you have a lockout problem at your furnace. When the motor on the fan fails, it wont run. Check for led codes on the control board. If you don't have led codes, turn off the power to the furnace at the breaker, and watch the unit. If nothing happens, connect the thermostat. If nothing happens still call for heat. Let the therm run through it's cycle, and if the bower runs continuous again, let me know we can walk through that situation.
Dec 05, 2008 | Ruud Central System Air Conditioner
Heating & Cooling Logo
262 people viewed this question
Top Heating & Cooling Experts
Paul Carew
Dan Webster
Dan Webster
Tim Whalen