Hi The system was fine after I replaced a capacitor for the out side start up worked fine until yesterday 90 degrees not cooling well noticed fan ran all night on low unless you turn off circuit breaker,thanks Joe
    Genius:
  • Goodman Master
  • 1,363 Answers
If the thermostat is calling for cooling the fan will run 24-7
Posted on Aug 11, 2015
watugot
  • 290 Answers
SOURCE: Ruud heat pump outside unit trips circuit breaker
Check your wiring between the contactor and compressor for a short to ground, or check the compressor windings for short to ground.
With the Tstat off, the contactor should be open so the only way for the compressor to be trying to do anything is if the 110 volts from the unbroken side are traveling through the compressor to ground. Since 110v is not enough to run it, the overload is kicking it out, cooling off, and repeating the cycle. When you kick on the Tstat, the contactor is supplying voltage directly to ground without going through the resistence of the compressor windings and kicking the breaker.
Post back and let me know what you find.
Posted on Nov 20, 2007
koolbreezes
  • 540 Answers
SOURCE: AC breaker trips after 10 minutes
Whats the amp breaker? Is this for the inside unit or the outside condenser? If the inside and gas heat you have a bad fan motor, If its an electric furnace , the same, but if its the outside unit, the fan could be going bad, locking up and the compressor still runs and pulls high ampsand tripps breaker or the compressor is just pulling too many amps due to plugged coils with dirt , grass or weeds blocking airflow.(koolbreezes74401@yahoo.com)
Posted on Jun 09, 2008
koolbreezes
  • 540 Answers
SOURCE: Goodman CKL60-1 Condenser Fan Runs OK, then stops
Bad bearings on the motor or check the fan rotations . Air should always blow out the top and **** in through the sides or coils.!... Thank-you-very-much!
Posted on Aug 25, 2008
muttandjeff
  • 359 Answers
SOURCE: Blower in Attic not running
inside unit has fan control relay , either on control board or can be separate ,except for the 24 volt transformer and the t-stat the units operate separately concentrate totally on the inside unit this is where the problem lies
Posted on Nov 08, 2008
motor1258
  • 6674 Answers
SOURCE: Hello , this is Bobby
Here's a link to a service manual, with step by step tests to determine whats wrong. I'm thinking compressor shot, but this should confirm, and or help you determine for yourself. Be careful with those capacitors eh !! Read warning in service manual.
http://www.rvcomfort.com/pdf_documents/1976141_copy.pdf
Posted on Oct 19, 2010
2002 4 ton Bryant air conditioner shuts off, fan still runs but not cooling is problem in the controls in the attic or in the AC unit or both?
With a non heat pump it is a simple 24 volt AC control circuit. In the attic there is a relay that is actuated via the fan control wire directly from the thermostat. On the thermostat there is an auto/man switch that controls the fan. Manual the fan runs all the time. Auto fan turns on and off with the outside compressor.
If the system is not calling for cool and the fan continues to run the fan relay is sticking. common problem. Sometimes after running for several days the relay will stop sticking if not, replace relay.
If the system is calling for cool and the compressor stops I would still expect the fan to run until thermostat tells the A/C to off. Some compressor units include a safety switch or high-pressure cut-out switch A blocked internal valve bad control board or external fan in outside unit defective no air flow in outside unit.
High pressure cut out not good,
Suggest turning temp max cool and observe. If acceptable cool and the compressor runs without interruption all is good, except for the blower in the attic. Safely check relay in attic blower circuit.
Hope this helps.
Jun 28, 2017 | Bryant Heating & Cooling
Condenser fan replaced one year ago, fan not turning but can hear motor
the answer to your problem is most likely the motor start capacitor. A AC motor can run in both directions. The start capacitor is used to cause the current to lag behined the voltage which determines the direction the motor will turn. Its posible the start and run capacitors are in one can. so changing one will change the other. However look for a wiring diagram. Do not asume that both capacitors are wired in properly. They may be fighting one another causeing premature failure.
Sep 18, 2012 | Carrier 38CKC036 Air Conditioner
I have a RUDD Achiever 11. The outside fan only intermittently runs and seems to quit in the evening (overtime for the air condo techs). It won't start again until the morning but when it runs, it blows...
Two possible problems here.
1. you have a bad condenser fan motor. average cost $140.00 for the part plus installation if you can't do it. just buy the motor you most likely will be able to use the existing fan blades.
2. you have a bad run capacitor on that fan. avg cost $5.00 - $35.00 plus installation
In my opinion if you're handy and safe with electicity save some money, if not have it done.
check out grainger.com for the parts they're very reasonable. for the fan you'll need to get specs from the defective unit like amp. voltage rpm. its all on the unit itself. for the run capacitor you'll need the same. all the info u need is on the parts. search the site for run capacitor or condenser fan motor.
good luck hope this helps
Jul 15, 2010 | Ruud UBHC Air Conditioner
Freezer works Refrigerator will not cool down
The compressor should be OK this time because you caught it in time. But if the condenser fan stops you need to consider replacing the fan. I have had refrigerators do fine until the fan motor warms up and you are away, it stops. Don't think you should use the refrigerator until the fan is fixed. Sea Breeze
Apr 22, 2009 | Kenmore Refrigerators
Aug 25, 2008 | Goodman CKL60AR60 Air Conditioner
Fan does not work.
I'm working on one right now and I believe it's the capacitor. It's hard to find this capacitor. So far I've tryed 3 HVAC suppliers and none have this rare capacitor. First UNPLUG THE UNIT. Take the phillips screws out of each side in the front. Then take the 3 screws out of the face of the control. There are 3 white common wires and a dark brown compressor wire and a light brown fan wire. Take the 1/4 inch screw out and unplug the wires and find another one.
Aug 05, 2008 | Whirlpool ACQ158XP Wall/Window Air...
Oct 23, 2007 | Ruud UAMB Air Conditioner
Airconditioner problem
This unit has a bad Start/Run Capacitor or a bad Fan Motor! Replace the $10 Cap...An then the $90 fan motor if the Cap dont solve it!
Oct 01, 2007 | Heating & Cooling
Heating & Cooling Logo
61 people viewed this question
Top Goodman Heating & Cooling Experts
Paul Carew
Tim Whalen
christian nielsen
Are you a Goodman Heating and Cooling Expert? Answer questions, earn points and help others