Ruud furnace won't light
I have a ruud deluxe 90 nat. gas unit built '87. The furnace turns on and the igniter glows, but won't light. The relay to the gas valve comes on about 15 to 20 sec. after igniter but I don't fell the gas valve open. I measured the voltage at valve and get .02V then 10.47 volts for a few sec then drops to .02V. ( From my vom meter I have to ground the red wire or I get a Neg. voltage reading. ??? )
I pulled the yellow wires off the circut board that come from the transformer and I don't get 24V or any voltage for that matter when 110v is on.
I don't think it's the valve because I can get it to open from the power of a 9V battery.
Is it a bad transformer or circut board problem or what?
Any ideas?
  • 2 more comments
  • awtinting Nov 04, 2007
    I check the two wire comming out of the transformer, Both yellow, with my meter, one probe on one yellow wire the other brobe on the other and get 0 volts.
    The circut board has both ac and low voltage on it along with relays that might look like they are removable. There is a smaller curcut board mounted on top that holds the relay for the gas valve, a white resistor and some diodes.
    I will try the ac. I did not think of that.
    The ac works and the transformer voltage jumps between .08 to .15 volts. A far cry from 24V.
    What next?
  • awtinting Nov 05, 2007
    Thanks for staying with me.
    Yes, I connected a 9v dc battery to open the silenoid valve and and the main burner opened up. Just long enough to smell gas.
    I removed the pilot gas tube and it is clear of debris, however there is no gas that comes out of the tube while the coil is at glow.
    Think it's cloged inside the valve?
    How does it know when to turn pilot on?
    FYI I did replace transformer today.
    Now what? Thanks.
    I saw the orifice and it is clrear and the tube has no kinks and is tight at all jounts.
    The heater was working last week.
  • 288 Answers
First lets try the transformer. With your meter check for 24v on the output side. You cant check to ground on this, you have to check your meter with both wires to the transformer. If this is too complicated just try turning on the A/C, if it comes on, the transformer is good. The problem may be with the time delay relay. try by-passing it and then see what happens. since its an '87 when you say circuit board I assume its a board with all the low voltage wires attached to it right? Or does it have resistors, diodes, and relays molded into it?
Posted on Nov 04, 2007
  • Rob Luna
    Rob Luna Nov 04, 2007
    If the A/C is working with no problems, that means the contactor and fan relay are getting the correct low voltage, so the transformer can de eliminated as the problem. I am having a hard time understanding your readings for the low voltage. (make sure your meter is set for the correct type of current, ac/dc). Lets start from the begining. you have a glow coil right? it gets red but the the pilot is not lighting, right? So lets start with the pilot orifice, which is a very tiny hole that sometimes gets pluged up. so make sure there is gas coming out of it. Also, just to make sure I'm understanding you right, you connected a 9v D.C. battery to the valve and the main burner opened up?
  • Rob Luna
    Rob Luna Nov 05, 2007
    When the pilot flame ignites there is a sensor of some sort that tells the main gas valve that there is a pilot flame and its O.K. to open up. Its possible that the sensor or the coil in the gas valve that opens the pilot gas is bad. Also when you checked the pilot tube at the very end there is an orifice insert @ the flame end that has a VERY tiny hole in the tip. its easy to overlook. I know I mentioned this already, but its worth double checking. Also make sure the pilot tube is good and tight. a leak can cause the flame to not light.
Electric furnace won't light
tony this is a gas furnance do you seee a orange glow on the right hand side of unit
Jan 22, 2013 | Heating & Cooling
I have a Ruud UAKA-037JAZ central heat and air unit (Silhouette 11 gas furnace). When I turn the thermostat to heat the heat does not come on. I removed the front panel and there are 2 green lights lit up...
Need furnace model number. It sounds like you're looking for a standing pilot. Your furnace might not have one. Very likely to have a spark ignition type system or hot surface igniter.
Feb 01, 2018 | Ruud UAKA037 Air Conditioner
Have a ruud achiever 90 plus furnace. the flame goes out after the igniter quits. any ideas
Problem: Your furnace will not ignite the gas to produce heat for your home. When a furnace has a bad ignitor what I see most of the time is the following sequence of operation:
1. Thermostat calls for heat. 2. Draft inducer motor starts. 3. Pressure switch attached by a small plastic or rubber tube senses the negative pressure produced by the draft inducer and closes. 4. Draft inducer runs for 30 seconds to a minute before you hear a gas hissing sound. The ignitor did not glow, the flame sensor (a small metal probe about 1/8" in diameter, with a white porcelain base) does not sense the flame, so after 8 to 10 seconds the hissing sounds stops with no ignition of gas to heat your home. Your furnace shuts down and goes into a lock out condition until you turn your power switch back off and on again. Then the sequence starts all over again with no ignition of the gas. Solution: You probably need to purchase and install a new ignitor. I would suggest that you inspect your ignitor closely for cracks. Make sure you do not touch the ignitor with your bare hands. If you do not visually see a crack, then you could have a furnace control board problem or a limit, rollout switch problem. The furnace's control board might not be supplying the voltage to the ignitor. If your furnace lights and the gas stays on for 8 to 10 seconds, then shuts right back off, then you need to clean your flame sensor with light sand paper or steel wool. You might need a new flame sensor, but most of the time they can be cleaned an will work well after cleaning.
Nov 26, 2010 | Ruud UBHC Air Conditioner
Ruud Silhouette II Gas Furnace, the furnace lights but will only stay on for a few seconds?? What could be the problem??
Bad or dirty flame rod.
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
Jan 09, 2010 | Ruud Heating & Cooling
I have the same Ruud Achiever unit & it's not working.
It sounds like it will need a hot surface igniter. This is the part that glows when furnace is turned on, and tells gas valve to release gas for it to ignite. At that point funace is lit, it heats up flame sensor witch inturn tells fan to start.
Sep 30, 2009 | Ruud UBHC Air Conditioner
I have a Ruud Achiever 90 plus furnace that will not ignite
Again is this a spark or a glow coil? If it is a glow coil look at the coil and see if there is a crack or white spot on it. If so it needs to be replaced.
Jan 17, 2009 | Ruud UBHC Air Conditioner
Ruud achiever 90 plus blower not working
does the furnace ignite?? your system may not have been lighting and has gone into ignition lockout count the codes of the led lights then remove panel led diagnostic codes are listed there.
if led codes indicate no problem verify capacitor is good and that mtr is getting 115 volts.
Sep 15, 2008 | Ruud UBHC Air Conditioner
Ruud achiever 90 plus gas furnace
The door, you mean the metal cover on the front? if you have the door off and push the safety switch in with your hand everything works fine? I need more info here, but if what I said is right, then the "door" isn't making good contact with the switch.
Mar 05, 2008 | Ruud UBHC Air Conditioner
Heating & Cooling Logo
499 people viewed this question
Top Heating & Cooling Experts
Paul Carew
Dan Webster
Dan Webster
Tim Whalen