Tests with a multimeter show that on mains power the output voltage is steady at around 230v but reduces to around 170v when using the battery. Is this normal?
    New Friend:
    Cheetah:
    An expert who has answered 20 or more questions within one hour.
  • 124 Answers
1. check either it is overloaded or the batteries are weak . check battery voltage to
Posted on May 10, 2014
3 Suggested Answers
fotomohamed
  • 321 Answers
SOURCE: dead appearing ups/inverter
keep on your main switch. off all the lights fan and other electrical items, let that inverter get charge first
Posted on Jun 18, 2009
jvpacoin
  • 91 Answers
SOURCE: I need to adjust the output voltage higher in the
you need to open the unit and get a palstic screw driver and look for the output adjust variable resistor and turn the variable resistor. make sure you have a true rms voltmeter when your doin it. Good luck
Posted on Aug 14, 2009
My gilera seems to have voltage drop and cause my engine to cut off when i press my brake.
Hi, Herman the following is a comprehensive charging system test that is guaranteed to the find issue with your system.
1. Battery Test: The battery needs to be a fully charged and load tested to ensure proper readings, connections need to be clean and tight. If you are not working with a fully charged and functional battery, all other voltage tests will be incorrect. Standing battery Voltage should be 12.5-13.2 DCV.
2. Charging System Voltage Test: Start motorcycle, measure DC volts across the battery terminals you should have a reading of approximately 13.2-15 DC Volts.
3. Check Connections/Wires: Inspect the regulator/stator plug, and check the battery terminals for connection/corrosion. If everything seems to be in order, move on to number 4 below to determine if there's a failed component.
4. Stator Checks/Rotor Check: Each of the following tests isolates the Stator & Rotor. If AC Output test Fails and Resistance Check, and Stator IB Test Pass then Rotor is at fault (Pull Primary covers and inspect rotor for damage).
5. AC Output Check:
Unplug the regulator plug from the stator
Start motorcycle and change Voltmeter to AC volts.
Probe both stator wires with your meter lead.
The motorcycle should be putting out approximately 18-20 ACV per 1,000 rpm. Reading will vary depending on system, check service manual specification
Generic Specs:
22 amp system produces about 19-26 VAC per 1,000 rpm
32 amp system produces about 16-20 VAC per 1,000 rpm
45 amp system produces about 19-26 VAC per 1,000 rpm
Stator Resistance Check:
Switch your multimeter to Ohm x 1 scale.
Probe each stator wires with meter leads and check resistance on the meter.
Resistance should be in the range of 0.1-0.5 Ohms. Reading will vary depending on system, check service manual for specification
Generic Specs:
22 amp system produces about 0.2 to 0.4 ohms
32 amp system produces about 0.1 to 0.2 ohms
45 amp system produces about 0.1 to 0.2 ohms
Stator IB test or Ground Check:
Probe each stator wire with your positive lead on the multimeter and the negative to ground.
There should be no continuity to ground on either wire.
If there is continuity to ground your stator is shorted to ground.
5. Regulator Test: Each of the following tests isolates the regulator only, so if any of these tests fail, the regulator is at fault.
Identifying Wires:
Battery Charge Lead- Wire going from regulator to battery positive.
AC output leads- Wires coming from the Stator to the regulator.
Ground- Wire from Regulator to ground or regulator may be grounded via the physical bolting to chassis.
Regulator Ground Test: Ensure the regulator body is grounded or grounding wire is fastened tightly to a good ground (you should verify this by checking continuity from regulator body to chassis ground).
Fwd/Reverse Bias Test/Diode Test: This check is testing the Diode function to ensure it is regulating the AC current for the stator into DC Current.
Switch multimeter to Diode Scale.
Place your Multimeter positive lead on each AC output wire.
Place your multimeter negative lead on the battery Charge wire.
The meter should read voltage typically around .5 volts.
Next, switch your multimeter leads putting the negative lead on the AC output wires and the Positive lead on the Battery Charge Wire.
The reading should be Infinite.
With your meter on the same setting, place your multimeter positive lead on the regulator ground wire or to the regulator directly, and then place your meter negative lead on the AC output leads.
Next, switch your multimeter leads putting the negative lead on the regulator ground and the Positive lead on the AC output wires.
Note: Below is a table to show the readings:
Positive Lead Negative Lead Reading
AC output 1 Battery charge lead Voltage
AC output 2 Battery Charge Lead Voltage
Battery charge lead AC output 1 ?
Battery charge lead AC output 2 ?
Ground AC output 1 Voltage
Ground AC output 2 Voltage
AC output 1 Ground ?
AC output 2 Ground ?
For more information about your issue and valuable "FREE" downloads that you will need please click on the blue links below. Good luck and have a wonderful day.
http://www.jetav8r.com/Vision/Stator/fault_finding_by_www.electrosport.com.pdf
Feb 21, 2017 | Gilera Motorcycles
1993 Honda shadow vt 1100 drove it to work today park it for about 2 hours went out to crank it the bike started for a second then died hit starter button again and lost all electrics no electrical power...
Hi, Bobby the following is a comprehensive charging system test that is guaranteed to the find issue with your system.
5. AC Output Check:
Generic Specs:
Generic Specs:
Identifying Wires:
VT1100C No power just went dead Honda Shadow Forums Shadow Motorcycle Forum
Honda SHADOW VT1100 Owners Workshop Manual
http://www.partsfish.com/page/oem-parts-for-honda
Honda VT1100C2 Owner Manual
Feb 19, 2017 | 1994 Honda VT 1100 C Shadow
2005 vl 1500 charging system system not charging checked generator 3 wires giving pluss 80v at 5000rpm instaled new rectifier voltage across battery under 13 volts could faulty battery be problem
Hi, Anonymous the following is a comprehensive charging system test that I found on a Rider Groups website
1. Battery Test: The battery needs to be a fully charged battery that has been load tested to ensure proper readings. If you are not working with a fully charged and functional battery, all other voltage tests will be incorrect. Most places like Auto Zone, Advance Auto, and Pep Boys will charge and test motorcycle batteries for free. Standing battery Voltage should be 12.5-13.2 DCV.
2. Charging System Voltage Test: Start motorcycle, Measure DC Volts across the battery terminals (you should have a reading of approximately 13.2-15 DC Volts).
4. Stator Checks/Rotor Check: Each of the following tests isolate the stator & Rotor, If AC Output test Fails and Resistance Check, and Stator IB Test Pass then Rotor is at fault (Pull Primary covers and inspect rotor for damage).
AC Output Check:
Probe both stator wires with your meter leads.
The motorcycle should be putting out approximately 18-20 ACV per 1,000 rpm. (Reading will vary depending on system, check service manual specification)
Generic Specs:
Resistance should be in the range of 0.1-0.5 Ohms. (Reading will vary depending on system, check service manual for specification)
Generic Specs:
Identifying Wires:
For more information about your issue and valuable "FREE" downloads that you will need please click on the links below. Good luck and have a nice day.
http://www.crowitis.com/images/VL1500_Charging_System_Wiring_Upgrades.pdf
stator output voltage
Suzuki VL1500 Service Manual
OEM parts for Suzuki
Suzuki VZ1500 Owner Manual
Jan 16, 2017 | Motorcycles
2002 Honda VT 1100 C2 Shadow Sabre how to check if your getting power from alternator
Hi, Anonymous before testing any electrical component in the Charging System it is "IMPERATIVE" that you have a fully charged battery of 12.5 volts or more and be able to pass a proper "LOAD" test because your battery may have 12.5 volts or more but little or zero amperage and must be replaced AGM types more so than lead acid batteries.
1. Battery Test:
3. Connections and wires:
Inspect the regulator stator plug, and check the battery terminals for connection corrosion. If everything seems to be in order, move on to number 4 below to determine if there's a failed component.
4. Stator Checks/Rotor Check: Each of the following tests isolates the Stator & Rotor. If AC output and resistance test fail and stator test passes then the rotor is at fault (Pull Primary covers and inspect rotor for damage).
5. AC Output Check:
Unplug the regulator plug from the stator start motorcycle and change Voltmeter to AC volts. Probe both stator wires with your meter lead. The motorcycle should be putting out approximately 18-20 ACV per 1,000 rpm. Reading will vary depending on system, check service manual specification
Generic Specs:
Switch your multimeter to Ohm x 1 scale. Probe each stator wires with meter leads and check resistance on the meter.
Resistance should be in the range of 0.1-0.5 Ohms. Reading will vary depending on the system, check the service manual for specifications.
Generic Specs:
Stator Ground Check:
If there is continuity your stator is shorted to ground and must be replaced.
5. Regulator Test:
Identifying Wires:
Next, switch your multimeter leads putting the negative lead on the AC output wires and the Positive lead on the Battery Charge Wire. The reading should be Infinite. With your meter on the same setting, place your multimeter positive lead on the regulator ground wire or to the regulator directly, and then place your meter negative lead on the AC output leads.
Next, switch your multimeter leads putting the negative lead on the regulator ground and the Positive lead on the AC output wires. The reading should be Infinite.
Stator test honda shadow
http://racetechelectric.com/files/pdf/rte_troubleshooting_flow_chart.pdf
Honda shadow vt1100 Owners Workshop Manual
Honda VT1100C2 Owner Manual Page 3
Jun 27, 2014 | 2002 Honda VT 1100 C2 Shadow Sabre
1994 Honda VF 750 C Magna no battery power
1. Battery Test:
5. AC Output Check:
Generic Specs:
Generic Specs:
5. Regulator Test:
Identifying Wires:
94 magna has no power to anything
Honda Magna VF750C Service Manual
Honda 1995 VF750C Magna Owner Manual
Apr 06, 2014 | 1994 Honda VF 750 C Magna
2011 Honda CBF Stunner not charging
Hi, Jithin before testing any electrical component in the Charging System it is "IMPERATIVE" that you have a fully charged battery of 12.5 volts or more and be able to pass a proper "LOAD" test if necessary, you may have a preliminary reading of 12.5 volts or more but little or zero amperage, the battery is faulty and must be replaced. AGM type batteries fall into this scenario more so than lead-acid batteries.
1. Battery Test:
5. AC Output Check:
Generic Specs:
Generic Specs:
5. Stator Ground Check:
6. Regulator Test:
Identifying Wires:
Battery Charge Lead- Wire going from the regulator to battery positive.
Regulator Ground Test: Ensure the regulator body is grounded or grounding wire is fastened tightly to a good ground (you should verify this by checking continuity from the regulator body to chassis ground).
For more information about your issue and valuable "FREE" downloads for viewing or printing that you will need please click on the blue links below. Good luck and have a wonderful day.
Honda cbf 125 battery not charging
HOW TO CHECK YOUR CHARGING SYSTEM and CHANGING the STATOR and REGULATOR...
https://haynes.com/en-gb/honda-cbf125-09-14-haynes-repair-manual
Honda CB Owners Manuals
Jan 22, 2013 | 2011 Honda CBF Stunner
Charging voltage to high, cooking batteries and head lights
Hi, Anonymous you may need a new voltage regulator the following is a comprehensive charging system test that I found on a Rider Groups website 1. Battery Test: The battery needs to be a fully charged battery that has been load tested to ensure proper readings. If you are not working with a fully charged and functional battery, all other voltage tests will be incorrect. Most places like Auto Zone, Advance Auto, and Pep Boys will charge and test motorcycle batteries for free. Standing battery Voltage should be 12.5-13.2 DCV.
AC Output Check:
Generic Specs:
Generic Specs:
Identifying Wires:
Electrical issue and fault finding chart
Yamaha zeal 250 service manual
Manuals Data Zealous
OEM parts for Yamaha
Dec 02, 2012 | 2000 Yamaha FZX 250 Zeal
My yamaha teo s 125 new battery fitted but still not charging
Hi, Birdy1995 the following is a comprehensive charging system test that is guaranteed to the find issue with your system.
5. AC Output Check:
Generic Specs:
Generic Specs:
Identifying Wires:
Yamaha YBR 125 not charging battery
Yamaha XN125 2000 Service Manual
Yamaha TEO XN125 Owner Manual
Sep 20, 2012 | Yamaha Motorcycles
My yamaha virago 1100 will not charge battery while running
Hi, Anonymous the following is a comprehensive charging system test that is guaranteed to the find issue with your system.
5. AC Output Check:
Generic Specs:
Generic Specs:
Identifying Wires:
ViragoTechForum com
http://www.sloneservices.com/SilverBack/Other-Stuff/VS-1100-chagre-syst.pdf
Yamaha Virago XV535 1100 1981 1994 Service Manual
Yamaha Virago XV1100K Owner Manual
Jun 16, 2012 | Yamaha Motorcycles
My battery drains while riding my 2005 wr450f. Have replaced stator and rectifier
Hi, Hans the following is a comprehensive charging system test that is guaranteed to the find issue with your system.
5. AC Output Check:
Generic Specs:
Generic Specs:
Identifying Wires:
Flat battery on WR450
YAMAHA WR450F Owner Service Manual
YAMAHA WR450F Owner Manual
Jun 11, 2012 | 2005 Yamaha WR 450 F
APC 620VA/390W Input 230V/Output 230V [apc-sc620i] (apc-sc620i) UPS System Logo
199 people viewed this question
Top APC Computers & Internet Experts
Jax Planet
Jax Planet
Are you an APC Computer and Internet Expert? Answer questions, earn points and help others