Question about Panasonic Room Air Conditioner CWXC104HU

Open Question

H 11 h11 indoor outdoor ab normal

Posted by on

  •  ROHAN PIYATILAKE
    ROHAN PIYATILAKE May 09, 2014

    Hi anamulhasharif , I want to help you with your problem, but I need more information from you. Can you please add details in the comment box?

×

Add Your Answer

Uploading: 0%

my-video-file.mp4

Complete. Click "Add" to insert your video. Add

×

Loading...
Loading...

Related Questions:

1 Answer

Error message U4


Signal transmission error. Indoor and outdoor PCB's cannot communicate. Usually a faulty controller board in the outdoor unit. If the indoor unit otherwise functions normally (can control fan speed, louvres, beeps in replay to all remote buttons) then it is probably OK so check outdoor controller PCB.

Jul 21, 2014 | Daikin Mini Split Concealed Duct Units

1 Answer

It shuts off and blinks 11


AHX18MEV
4 - 12
[8] SELF-DIAGNOSIS FUNCTION
1. Indoor unit
(AH-X18MEV, AH-X18MEV-1, AH-X24MEV, AH-X24MEV-1)
To display the self-diagnosis, hold down the AUX button for over 5 seconds on the indoor unit when the indoor unit is not operating.
• The operation lamp (red), timer lamp (orange) and Super jet lamp lighter) flash to indicate the information of malfunction.
(Display of self-diagnosis result)
The operation lamp (red) and the Super jet lamp (green) flash in synchronization with the timer lamp (orange).
(AH-XP18MV, AH-XP18MV-1, AH-XP24MV, AH-XP24MV-1)
To display the self-diagnosis, hold down the AUX button for over 5 seconds on the indoor unit when the indoor unit is not operating.
• The POWER CONSUMPTION indicator indicates the information of malfunction by showing the main category error (number) and the sub-category
error (-number) alternately in 1-second intervals.
Example: Compressor high-temperature error
Remark

3. CHART
<INDOOR UNIT> ?:1-second ON / 1-second OFF
Problem
symptom
Outdoor
unit indication
(LED1)
Indoor unit Malfunction
No.
Content of diagnosis Check point Action
Lamp Main Sub Main Sub
Normal
condition
Normal
blinking
? ? ? ? ? Timer (Orange) 0 0 Normal
Operation (Red)
Super Jet (Green)
Indoor and
outdoor
units do not
operate.
1-time ? ? ? ? ? Timer (Orange) 1 0 Outdoor unit
thermistor
short-circuit
Heat exchanger
thermistor short
circuit error
(1) Measure the resistance
of the outdoor
unit
thermistors.
(1) Replace the outdoor
unit thermistor
assembly.
? Operation (Red)
Super Jet (Green)
? ? ? ? ? Timer (Orange) 1 Outdoor temperature
thermistor
short circuit error
(2) Check the lead wire
of the outdoor unit
thermistor for torn
sheath and shortcircuit.
(2) Replace the outdoor
unit thermistor
assembly.
? Operation (Red)
? Super Jet (Green)
? ? ? ? ? Timer (Orange) 2 Suction thermistor
short circuit
error
(3) No abnormality
found in above
inspections (1) and
(2).
(3) Replace the outdoor
unit control
PWB assembly.
? Operation (Red)
? Super Jet (Green)
? ? ? ? ? Timer (Orange) 3 2-way valve
thermistor short
circuit error
? Operation (Red)
? ? Super Jet (Green)
LED1
AU-X24MV, AU-X24MEV
AU-X18MV, AU-X18MEV
LED1

May 27, 2012 | Sharp Heating & Cooling

2 Answers

What does error code p8 mean


P8 means Abnormality in outdoor unit.
Check:
1) Wrong wiring of indoor/outdoor
connecting wire
2) Reversed phase
3) Protection device is working
4) Damaged outdoor coil thermistor

Solution:
1) Check the indoor/outdoor connecting wire.
2) Change the connection of electric wiring.
3) Check the protection device.
4) Measure the resistance of the outdoor coil thermistor.
If the resistance is normal, replace the
outdoor controller board

Hope, helpful.

Feb 03, 2011 | Mitsubishi Heating & Cooling

2 Answers

We have a P8? CAN'T FIND MANAUL


P8-Abnormality in outdoor unit.
1.Wrong wiring of indoor/outdoor
connecting wire.......................Check the indoor/outdoor connecting wire.
2) Reversed phase......Change the connection of electric wiring.
3) Protection device is working........ Check the protection device.(LP,HP)
4) Damaged outdoor coil thermistor.....Measure the resistance of the outdoor coil thermistor.If the resistance is normal, replace the outdoor controller board.
5) Check out door coil is cleaned. If not do it.
thanks.

Jan 30, 2011 | Mitsubishi Mr. Slim MXZ30TN Air...

1 Answer

I have an LG split system air conditioner model number LSZ244VN-4 it is coming up with a fault code of CS after it has been running for approx 5 minutes


There is no CS code. Please read as C5.
Fault Code 05 and 53 (CH05 is displayed at indoor unit, 53 is displayed at outdoor unit)
This fault code indicates a communication error between the indoor and outdoor units; this is usually caused
by wiring errors or condensate pumps connected to the inter-connecting cable.
The communication between the units is a fluctuating DC voltage commonly called a serial signal, it can be
easily lost if the wiring is not done correctly. If there is a communication error fault CH05 will appear within 5
mins of powering up the system.
Testing
• Check Outdoor and Indoor Power Supply Voltages ( 230V ±10% ) and correct as necessary.
• Check for any mis-wiring or loose connections and correct as required.
• Check the resistance between communication line and GND. (Normal: Over 2M).
• If one Indoor unit operates normally Outdoor PCB is generally normal.
Turn on the power and start the indoor unit in cooling, set the temperature to 18ºC; the serial communication
signal will only be present for the first 3 mins of operation.
Set your meter to DC Volts, Test between terminals 5 (Red probe) and 2 or Earth (Black probe) of the outdoor
unit, you should see a fluctuating 0-72 Vdc.
If the Voltage is not present disconnect the terminal 5 cable, test the Voltage between this wire (Red probe)
and 2 or Earth (Black probe), you should see a steady voltage in the range of -0.1 to -10.0 Vdc. If No Voltage
is present either the cable or Indoor PCB must be faulty. This can be determined by checking the voltage
output on the Comms terminal of the Indoor unit, with the Comms wire disconnected. If No Voltage is present
the Indoor PCB must be faulty, if present, cable must be at fault.

Jan 19, 2011 | Heating & Cooling

1 Answer

Hi i have a panasonic cs28 cassett units both have F27 01 fault codes. have checked power at indoor and outdoor units can i do anything else


f27- indoor outdoor unit disconnected.
Check power in output of indoor and input of outdoor, if power variation, replace wire.

Normally in this fault code, one of the wire burnt or rat bitten.

Dec 27, 2010 | Heating & Cooling

1 Answer

Indoor fan slow to rotate in heat mode and no heat/compressor


The indoor fan will not run at normal fan speed untill the indoor coil reaches 32oC. This is done so that a cold draught is not felt when outdoor unit is not running. Check to make sure the outdoor unit is operating. If the outdoor fan is running but there is no indoor fan after 5 mins then you must likely have a gas issue or a fault compressor circuit.

May 31, 2010 | Fujitsu 24R1 Air Conditioner

2 Answers

Remote doesn't work on air con


Should be current detect pcb faulty, or compressor drawing too much current.
I don't have your model a/c, but panasonic fault codes stay pretty much the same
Normally panasonics have this info on the inside of the access panel.
Plus fault codes from the indoor unit make it easier to look up.

if the compressor is running, check the amps and refrig pressures.

Sep 19, 2009 | Heating & Cooling

1 Answer

Control cable wires crossed


I would not do anything just yet It might be more prudent to call Panasonic help line, and explain your findings I feel that the system will not have suffered any damage if the control cables have been simply wired incorrectly if that is the problem, try and find a call number from your installation paperwork, good luck.

Jun 08, 2009 | Heating & Cooling

Not finding what you are looking for?
Panasonic Room Air Conditioner CWXC104HU Logo

Related Topics:

24 people viewed this question

Ask a Question

Usually answered in minutes!

Top Panasonic Heating & Cooling Experts

Bill Long

Level 3 Expert

587 Answers

Fotis Papastamatiou

Level 2 Expert

96 Answers

Dennis Boxerman

Level 3 Expert

1037 Answers

Are you a Panasonic Heating and Cooling Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...