I have a cple36-1...once the temp outside gets hot, it doesnt keep the house cool..thermostat is set at 76 and when i get home from work its 80+ inside. Weve had it checked freon is good and we keep the filters changed. Could it be the fan that was put on it is wrong? Or something else?
  • 3,287 Answers
There are many parts of a cooling system - any one of them could be failing and causing the problem you describe. Any qualified HVAC professional should be able to quickly assess the problem and make recommendations for you.
Some common problems include: poor power (low voltage), faulty condenser fan, faulty evaporator fan, dirty filters, dirty evaporator coil, dirty condenser coil, faulty expansion valve, contaminated refrigerant, over or under charged, undersized unit for the space to be cooled, wrong program in thermostat (times, days, temperature, heat or cooling mode, etc.) and more.
If you asked for a technician simply to "check the refrigerant" - that may be all he did. If you ask a tech to "determine what the problem is" - you allow him to do more than simply what you ask him to check. Let him do the all the work he needs to do to determine the source of the problem. Good luck!
Posted on May 07, 2014
  • 61 Answers
SOURCE: thermostat issue with comfort zone II.
Is this an electric or gass furnace - Eather of these can can have this problem its most recomendable that you call a seviceman .
in the case of electric furnace you may requier a new heat sequencer. And in the case of gass you may requier a new relay.
Posted on Feb 19, 2009
mastatech
  • 478 Answers
SOURCE: Amana 1 ton Residential AC / Outside unit comes on for a sec
open the service panel to check for control voltage of 24volts when tstat calling, The contactor should be pulled in, if contactor is down,and contacts appear to be clean, and the unit is still not running, it is a bad compressor. to test this unplug the black wire from the compressoror at contactor,w/ power off! Turn on power if fan works normally it's a bad compressor. However if you see a swollen split cap(5 wires to a soup can looking w/ the terminal C,F,and Comp), switch it first and start at square one.
You also need to consider the high pressure switch if its cycling on off on off.
Posted on Mar 12, 2009
  • 148 Answers
SOURCE: UNIT RUNS AN EXCESSIVE AMOUNT OF TIME AND AIR IS
DOES THE HOUSE FEEL DRIER IF IT IS 80 OUTSIDE WITH ALOT OF HUMIDITY THE UNIT WILL RUN FOR A LONG TIME TO REMOVE THE MOISTURE(HUMIDITY) OUT OF THE HOUSE BEFORE TEMP DROPS DRAMATICALLY IS THERE WATER COMING OUT OF THE DRAIN PIPE OUTSIDE
Posted on May 03, 2009
SOURCE: Thermostat unit not cooling house.
Okay. Here's what I suspect in order of probability:
- low refrigerant charge
- contactor not getting 24 volts from controller (controller problem)
- bad contactor
- bad capcitor
I'd start with the charge, as suggested by mastatech. But if it is low, you'll need a service call, anyway, so pressing the needle valve may not be necessary.
I'm assuming you're not going to be taking the unit apart and testing stuff, so you'd need a service call for that as well.
I guess bottom line is, call for service. At least, I think we've ruled out simple stuff which will avoid paying for a service tech to come out and flip a switch.
Maybe mastatech has some other recommendations.
Posted on May 10, 2009
james3751
  • 614 Answers
SOURCE: Not blowing cool air on my Ruud, 18 years old, outside unit.
If you have ice on the Line you are iced up. If coil is iced no air can get thru. Now First. Turn of ac and turn fan to on posotion. That will thaw unit. Let it run 45 minutes. That should do it. If the fan is not running you amy have a bad fan relay. One of the reason iced up unit is dirty evap, coil inside. Try to thaw it out first. You can clean the coil with a stool brush. Does not damage the coils. Good luck
Posted on Jun 09, 2009
Rheem split system condenser high pressure limit/safety needs resetting frequently before it reaches the set temp of 76 degrees faren. what's wrong and what do i need to check?
Is the outdoor fan running? The fan cools the coils and compressor, therefore keeping the high pressure low enough to run. Either the fan is not working or its not spinning fast enough. Check the capacitor, or just replace it.
Apr 18, 2017 | Heating & Cooling
One year old Amana ASZ 16 (replaced inside and outside units last year) - works fune until the last two weeks, now home at 5pm, reset the thermostat from 82 degrees to 76 or 77 to cool off house (which...
Sounds like the system is either over charged with freon or under sized. Call the same people back out ask for a supervisor to come out and check out the system any other company will charge you.
Jun 10, 2011 | Amana Heating & Cooling
We have a3 yr old Goodman CAPF3030B6AA Airconditioner and Furnace. The Air conditioner hasnt worked right all summer. Its 102 degrees outside and we can set the thermostat on 72 degrees and it will be...
A/C units have a design temperature of 90F. Now when the temperature is above 90F they start to have trouble keeping up. Depending on how well your unit is sized for the house, you will notice when the temp is over 90F. I don't know if who ever looked at your unit checked the refrigerant pressures since you said he checked the temps but I assume he did, however, it could possibly need charging.
Aug 05, 2010 | Heating & Cooling
My thermostat is set to 73 degrees when i get home at six it is set at 75 during the day when im not home the past couple of days it wont get to 73 it actually goes up to 76 77 it is working cool is on why...
may need charged a out of adjustment can cost lots is it old unit is outdoor temp. very hot may have trouble catching up to setpoint.on a 95 degree day good luck.
Jul 07, 2010 | Honeywell Electronic Programmable...
Air condition jsut 10 month old ... not keeping up whith cooling
If it's only 92° outside and the unit won't cool the house, then the unit is either to small or it's low on refrigerant. They are designed to cool a house with outdoor temperatures up to 115° to 120°.Usually you need one ton a/c for every 400 square feet of house, but, you have to take into account for average outdoor temperature and humidity, windows, doors, especially sliding glass or patio doors and which side of the house they are on, insulation in walls and attic.
The air leaving your duct work going into the rooms should be about 20° lower than the room temperature, if you have a 80° room then the air leaving the duct should be around 60°. if it is then the unit is probably to small if, everything is working properly.
Jun 07, 2010 | Goodman CLQ36AR49 Air Conditioner
Frigidaire 2001
check the thermostat setting and in cool mode
Sep 04, 2009 | Heating & Cooling
Carrier Air Conditioner- not reaching set temperature
if it is set to 76 degrees and its 78 in the house its working fine it is suppose to shut off once it reaches 76 but sometimes there is a 1 or 2 degree differential built ini would keep you filter clean and as long as it blows out cold air i wouldnt be to concerned most airconditioners need yearly cleanings though
Jul 14, 2009 | Carrier 38CKC036 Air Conditioner
Indoor temp doesnt go to my punched in setting of 68 on therm
if it is around 93-97 degrees outside,thats all the cool your going to get
Jun 23, 2009 | Honeywell Programmable Thermostat Heater
UNIT RUNS AN EXCESSIVE AMOUNT OF TIME AND AIR IS COOL NOT COLD COMING OUT OF VENTS CARRIER 58DLA / 58DLX CENTRAL AC FAN AND COMPRESSOR ARE OPERATING BLOWER IS WORKING UNIT IS TURNED ON TO AC TEMP SET AT 76...
May 03, 2009 | Carrier Heating & Cooling
Heating & Cooling Logo
29 people viewed this question
Top Heating & Cooling Experts
paulcarew
Dan Webster
Dan Webster
Donni Steen