Panasonic Air Conditionner will not work It will cool for 30 secs then the louver will close and the timer light will flash On heat mode it will work fine except the air is not as hot as it used to be
    Scholar:
  • 101 Answers
Sounds like the air filter is dirty. Air flow is restricted and the compressor will shutdown if it gets too cold because the available air cannot warm up the evaporator enough. That could also be the reason it does not heat as well either. Since you do not mention that the air flow is lower than it use to be.
Posted on Apr 22, 2014
  • 1 more comment
  • Martin Lafleur
    Martin Lafleur Apr 22, 2014
    Ok thanks I will clean the air filter but you mean the air filter inside?
  • Martin Lafleur
    Martin Lafleur Apr 23, 2014
    I cleaned the air filters no difference I cleaned them not too long ago
  • Martin Lafleur
    Martin Lafleur Apr 28, 2014
    Thank you for the potential help! The fan motor is probably broken because ice formed all around the A/C and all around the fan inside
2 Suggested Answers
  • 14 Answers
SOURCE: fijutsui air conditoner
We had a similar problem. The timer light would blink 3 times, pause, then blink 3 times again, pause, and so on. The fan was blowing lots of air out, but the air was not cold. The operation light was off.
The technician came and fixed it for free, since it's actually easy to fix. He went to our circuit-breaker box, and cut power (from the box) to the air conditioners for 30 seconds. Then, he restored power - problem fixed!
It's apparently because the air con goes into a "safety" mode when there's a power surge.
Posted on Dec 16, 2008
How do I get the fault codes up on a Panasonic split air conditioning system CUE24FKR
14.2.2 To Make a Diagnosis1 Timer LED starts to blink and the unit automatically stops the operation.
2 Press the CHECK button on the remote control continuously for 5 seconds.
3 "- -" will be displayed on the remote control display.
Note: Display only for "- -" (No signal transmission, no receiving sound and no Power LED blinking)
4 Press the TIMER ? or ? button on the remote control. The code "H00" (no abnormality) will be displayed
and signal will be transmit to the main unit.
5 Each press of the button (? or ?) will increase error code
number and transmit error code signal to the main unit.
6 When the latest abnormality code on the main unit and
code transmitted from the remote control are matched,
Power LED will light up for 30 seconds and a "beep" sound
(continuously for 4 seconds) will be heard. If no codes are
matched, Power LED will light up for 0.5 seconds and no
sound will be heard.
7 The breakdown diagnosis mode will be canceled unless
pressing the CHECK button continuously for 5 seconds or
operating the unit for 30 seconds.
8 The LED will be off if the unit is turned off or the RESET
button on the main unit is pressed.
Diagnosis
display Abnormality / Protection control Abnormality
Judgement Emergency operation Primary location to verify H00 No abnormality detected - Normal operation H11 Indoor / Outdoor abnormal communica
tion > 1 min after starting
operation Indoor fan operation
only • Internal / external cable connections
• Indoor / Outdoor PCB H14 Indoor intake air temperature sensor
abnormality Continue for 5 sec. - • Intake air temperature sensor (detec
tive or disconnected) H15 Outdoor compressor temperature sensor
abnormality Continue for 5 sec. - • Compressor temperature sensor
(detective or disconnected) H16 Outdoor Current Transformer open cir
cuit - - • Outdoor PCB
• IPM (Power transistor) module H19 Indoor fan motor mechanism locked 7 times occurance
continuously - • Indoor PCB
• Fan motor H23 Indoor heat exchanger temperature sen
sor abnormality Continue for 5 sec. O
(Cooling only) • Heat exchanger temperature sensor
(detective or disconnected) H24 Indoor heat exchanger temperature sen
sor 2 abnormality Continue for 5 sec. - • Heat exchanger temperature sensor
(detective or disconnected) H27 Outdoor intake air temperature sensor
abnormality Continue for 5 sec. O • Outdoor temperature sensor (detec
tive or disconnected) H28 Outdoor heat exchanger temperature
sensor abnormality Continue for 5 sec. O • Outdoor heat exchanger temperature
sensor (detective or disconnected) H30 Outdoor discharge air temperature sen
sor abnormality Continue for 5 sec. - • Outdoor temperature sensor (detec
tive or disconnected) H33 Indoor / Outdoor wrong connection - - • Indoor / Outdoor supply voltage H38 Indoor / Outdoor mismatch (brand code) H50 Ventilation motor abnormality 7 times occurance
• Ventilation motor H51 Nozzle lock abnormality 2 times occurance
continuously - • Nozzle H52 Limit switch abnormality - - • Indoor PCB H97 Outdoor fan motor mechanism locked 2 times occurance
within 30 minutes - • Indoor PCB
• Fan motor H98 Indoor high pressure protection - - • Air filter dirty
• Air circulation short circuit H99 Indoor heat exchanger anti-freezing pro
tection - - • Insufficient refrigerant
• Air filter dirty F11 Cooling / Heating cycle changeover
abnormality 4 times occurance
within 30 minutes - • 4-way valve
• V-coil F90 PFC control 4 times occurance
within 10 minutes - • Voltage at PFC F91 Refrigerantion cycle abnormality 2 times occurance
within 20 minutes - • No refrigerant
(3-way valve is closed) F93 Compressor rotation failure 4 times occurance
within 20 minutes - • Compressor F95 Cool high pressure protection 4 times occurance
within 20 minutes - • Outdoor refrigerant circuit F96 IPM (power transistor) overheating pro
within 30 minutes - • Excess refrigerant
• Improper heat radiation
• IPM (Power transistor) F97 Outdoor compressor overheating protec
within 10 minutes - • Insufficient refrigerant
• Compressor F98 Total running current protection 3 times occurance
within 20 minutes - • Excess refrigerant
• Improper heat radiation F99 Outdoor Direct Current (DC) peak detec
tion 7 times occurance
continuously - • Outdoor PCB
• Compressor
Note:
"O" - Frequency measured and fan speed fixed.
The memory data of error code is erased when the power supply is cut off, or press the Auto Switch until "beep" sound heard following by pressing the "CHECK" button at remote controller.
Although operation forced to stop when abnormality detected, emergency operation is possible for certain errors (refer to Error Codes Table) by using remote controller or Auto Switch at indoor unit. However, the remote controller signal receiving sound is changed from one "beep" to four "beep" sounds.
Oct 13, 2017 | Panasonic Heating & Cooling
Fujitsu a/c outdoor model number AOTG12LVC indoor unit economy light flashing continuously, operation light single flash, timer light single flash this sequence repeats
Serial communication error. This means that the indoor unit is not communicating with the outdoor unit usually because the outdoor unit is faulty. You can check the indoor unit by switching it to 'fan' mode and seeing if all functions work normally (fan speed, louvers move as directed). If it responds normally, then it's probably ok so you can turn your attention to the outdoor unit. A common problem with the outdoor controllers is that they are susceptible to bugs, geckos, etc. shorting them out which will mean replacement of the board.
Mar 05, 2017 | Fujitsu Heating & Cooling
Panasonic air con - when you turn the air con on it runs for about 3 mins and then the timer light flashes. Air con will not work.
• Once abnormality has occurred during operation, the unit
will stop its operation, and Timer LEDs blink.
• Although Timer LED goes off when power supply is turned
off, if the unit is operated under a breakdown condition, the
LED will light up again.
• In operation after breakdown repair, the Timer LED will no
more blink. The last error code (abnormality) will be stored in
IC memory.
• To make a diagnosis:
1. Timer LED start to blink and the unit automatically
2. Press the CHECK button on the remote controller
3. "- -" will be displayed on the remote controller display.
Note: Display only for "- -". (No transmitting signal, no
receiving sound and no Power LED blinking.)
4. Press the "TIMER" or button on the remote
controller. The code "H00" (no abnormality) will be
displayed and signal will be transmitted to the main
unit.
5. Every press of the button (up or down) will increase
abnormality numbers and transmit abnormality code
6. When the latest abnormality code on the main unit
and code transmitted from the remote controller are
matched, power LED will light up for 30 seconds and
a beep sound (continuously for 4 seconds) will be
heard. If no codes are matched, power LED will light
up for 0.5 seconds and no sound will be heard.
7. The breakdown diagnosis mode will be canceled by
pressing the CHECK button continuously for 5 sec-
onds or without any operation the remote control for
30 seconds.
8. The LED will be off if the unit is turned off or the
RESET button on the main unit is pressed.
When you have the error code, we can work out what to do next.
Mar 27, 2015 | Panasonic Heating & Cooling
I need to know what the voltage for this unit
Model: REG-123H
  • UPC: 855326002968
  • Product Type: 12,000 BTU Window Air Conditioner & Heater
  • Product Dimensions: L: 24.00" x W: 24.00" x H: 16.00"
  • Product Weight: 88.00 lbs.
  • Product Color: White
  • Application: Used to cool individual rooms
  • Type: Window Air Conditioner
  • Warranty: 1 year; 5 years sealed system
  • Coverage Area: 550 square feet
  • Voltage: 230 volts
  • Heater: Yes
  • Air Flow: 266 CFM
  • Amps: 5.5 amps
  • Heating Capacity: 11000 BTUs
  • Frequency: 60 Hz
  • Cooling Capacity: 12000 BTUs
  • Dehumidifying Capacity: 3.6 pints
  • EER: 9.8
  • Heat Pump: No
  • Number of Fan Speeds: 3
  • Programmable Timer: Yes
  • Timer Length: 24 hour
  • Refrigerant Type: R-410A
  • Air Conditioner Type: Cool/Heat
  • Energy Star Rated: No
  • Air Filter: Yes
  • Built-In Air Purification System: No
  • Display Type: Digital
  • Remote Control: Yes
  • Adjustable Louvers: Yes
  • Adjustable Side Panels: Yes
  • Compatible Window Size: Min. Window
  • May 31, 2014 | Comfort-Aire RED-123 Air Conditioner
    Fujitsu Inverter ASTA24LCC has flashing "Operation" and sometimes "Timer" lights. I have cleaned filters but the lights still flash. Does anyone know the issue here?
    You may need to open the louver and hold down the Manual/Auto button for 10 seconds to see if you can reset the machine. Additionally, unplug the unit for 30 seconds or so and then plug back in.
    Dec 09, 2012 | Heating & Cooling
    Timer light on fujitsu heat pump flashes not heating
    the light flashing indicates there is a problem. you can try reseting the system by turning the power supply off and back on again 30 sec later, if the same thing happens you need to count the number of light flashers and that relates to a fault code
    Jun 20, 2012 | Fujitsu Heating & Cooling
    FUJITSU Indoor Inverter ASTA09LCC/ASTA12LCC airconditioning - not cooling
    If the operation button is flashing 8 times, the timer light should also flash 4 times in each sequence. This indicates a failure of the PFC circuit in the outdoor unit which basically means a faulty outdoor board and will have to be replaced.
    If the operation light is flashing 8 times by itself, the indoor controller board may have a fault. You can normally test this by putting the mode on the remote to 'Fan' and checking that the controls otherwise work normally - louvers work as directed and fan speed changes correctly when selected on the remote.
    Most likely the fault lies in the outdoor board but you should contact a tech to diagnose correctly.
    Sep 24, 2017 | Fujitsu 18C1 Air Conditioner
    The timer light keeps flashing and unit does not respond to the on by cooling the room when the on button is pressed
    timer button keeps flashing and no heat coming from unit. cool air works, but absolutely no heat.
    Oct 13, 2009 | Daewoo DSA-122L Air Conditioner
    9000 btu maytag portable AIR CONDITIONNER Model M6PO9D2B-B
    Reasonalbe rule of thumb is a difference of 10 degrees Centigrade.
    Charlie
    Aug 18, 2009 | Maytag Electronic Portable Air Conditioner...
    Heating & Cooling Logo
    97 people viewed this question
    Top Heating & Cooling Experts
    Paul Carew
    Dan Webster
    Dan Webster
    Tim Whalen