Question about Powerware 9120 UPS System
Overtemp Condition on LCD
Alarm sounds, UPS is in Bypass mode, and noticed both fans were not on. After sticking a piece of paper into both fan slots to check, the top one started working. UPS is located in tight quarters and machine computer it feeds is running. This is why a person can't easily visually inspect the back without shutting machine down and disconnecting UPS. This problem occurred about 24 hours after battery replacement and I suspect may have helped the old batteries fail.
    Scholar:
  • 64 Answers
You're absolutely right, overtemp on batteries can greatly escalate the failure of batteries, particularly older or heavily loaded ones. The fans are a fairly easy replace, if we can assist in any way, please do not hesistate to contact us.
http://www.gowithon.com
Posted on Jun 30, 2009
I have a 2003 artic cat 400 2x4.The cooling fan will no longer come on. What do I check
Hey Mark, make sure you haven't accidentally pulled a wire loose..the temperature sensor wire or the fan wire (s).- rare.. You probably have a temperature sensor going bad and that is what triggers the overtemp switch ("alarm") to start the fan. Could also be the fan switch.
Jun 07, 2017 | ATVs
Liebert gxt2-10000rt208 fault indicator and A + E LEDs on. Did anyone know this alarm?
I'm going to go on a limb and say the unit also has the bypass indicator on as well, is that correct? A=On bypass due to overtemperature condition & E=On bypass due to inverter failure.
I can't see in the picture or hear it but is it beeping also? 1 second beep every 2 seconds? Thats on internal bypass. If none of this is true then you have a tricky problem.
Dec 09, 2014 | Liebert Computers & Internet
UPS Bypass mode failure
it looks like you have a faulty static switch
Apr 11, 2014 | Eaton Powerware 9355 UPS System
I have an Eaton 9355 20kva system. Theres an alarm #188 Bypass Failure and notice#105 Bypass Not available. The batteries are also not charging or the battery current is reading 0 amps. When the power goes...
Bypass failure is the same as your input unless you have a dual input. You lost power and the UPS did not hold the load because the batteries are bad. Replace the batteries and you will be ok.
Feb 18, 2013 | Eaton Powerware 9355 UPS System
Error light in my apc smart ups sc 1500va ups
1. Four beeps every 30seconds (On Battery LED will be illuminated)
This alarm indicates that the Battery PowerSupplied outlets are now supplying battery power as opposed to power from theutility. If the UPS determines that the input utility power is unsafe for yourcomputer equipment, the UPS will switch to battery power.
Note: Ifthe power disturbance is brief, you may only hear one or two beeps.
2. Continuous Beeping (On Battery LED will beilluminated)
This alarm indicates that a Low Batterycondition has been reached and that the UPS will soon shutdown. Once the UPStransfers to On Battery operation, it can only stay on battery for a limitedamount of time. The UPS will sound this alarm about two minutes before thebatteries are totally exhausted. Once exhausted, the UPS will shutdown and turnoff its output power to your equipment. If you hear this tone you shouldimmediately shutdown your computer to prevent data loss or corruption.
3. Continuous Beeps for 30 seconds (BackUPS OFFICE 250 and 280 ONLY)
This alarm indicates the unit has detected anOverload condition after it has performed a self-test during start-up.
4. Continuous Two-Tone Beep
This alarm indicates a severe Overload wasdetected while the unit was on-battery operation. This tone will continue tosound until the unit shuts down.
5. Continuous Tone (On Battery LED will beflashing)
This alarm indicates that the battery-poweredoutlets are overloaded.
6. Continuous Tone (On Line and On BatteryLEDs flashing) Back UPS OFFICE 350,400, and 500 ONLY
This alarm indicates that an internal UPS faulthas occurred.
Dec 08, 2011 | APC Smart-UPS SC 1500VA UPS System
Symmetra LX "Intelligence Module Fault". Does
First calculate the total load of the UPS and then calculate the total load. One of the Intel Module is Primary and one is Secondary. I can't remember exactly which one is primary. Q1. There will be a LED on the INTELI MODULE flashing RED. That identifies the bad MODULE. Q2. You can remove the MODULE, but I recommend you place the UPS in Static Bypass first through the Display Menu. Also make sure the UPS is in NORMAL MODE or already in STATIC BYPASS, the LED's on the Display should indicate what mode its in. Q3. You can remove the display from the Inteli Module with out harming the load. You just can't do anything with the UPS, as to tell it to Go to Bypass (Static Bypass) or get out of Bypass, check voltages, etc. So order the part first by getting part number on the sticker off the Module, then schedule your shutdown and perform the you maintenance after hours this way you don't affect anything during business. Also don't do the repair on a Friday due to the fact its weekend and APC/Third party UPS companies will charge you a lot to come out in the weekends. FIRST DO THIS PLEASE- GET THE MANUAL FOR THIS UNIT!!!! And READ IT FIRST!! Find in the manual where it walks you through putting the UPS In bypass (Static Bypass). Follow the manual, My way of doing is to READ TWICE, OPERATE UPS ONCE!! This has help me not dump any loads. My suggestion to you is to check if unit is in Bypass (static Bypass due to the faulty module. If it is on Bypass then all you need to do is follow the procedures to place UPS in External Maintenance Bypass. If UPS is in Normal mode but with Alarms and Beeping, then Navigate through the display and find the BYPASS Mode. Then hit enter Yes on the BYPASS MODE, it will ask you again if you want to "Place UPS INTO BYPASS. Hit YES. You will hear it click. Your LED on the display should Light UPS Solid "BYPASS LED ON" AGAIN Please keep referring to the MANUAL. Once your in bypass mode (Static Bypass) then you can operate the External Bypass Switch on the bottom of the UPS. That is the Maintenance Bypass Switch. This isolate the UPS completely and your load never see's the transfer from Static Bypass to External Bypass, Because its a MAKE BEFORE BREAK System. (Make the power before Breaking the Power) Sorry to get down to simple terms, but when I work on a UPS its personal due to the fact you are responsible for the all that is on the OUTPUT of that UPS. Once on External Bypass, You can now do you module swap. Turning the UPS back on, Please follow place UPS back On Line in the UPS Manual. Also in the Diagnostics, off the display of the unit, it also identifies what module is bad including the Power Modules to the Battery Modules.
Nov 03, 2010 | APC Symmetra Tune-UPS technical support -...
Overtemp
The cooling fan is probably not working. Unit will overheat. Check the fan to see if it run continuously with no scraping noise with the UPS turned "ON". If the fan does not run, open the case and replace the fan.
Jan 19, 2010 | Powerware 9120 UPS System
How to take ups in manual bypass mode.
You definitely want to follow the manual procedure to avoid a possible load loss:
http://powerquality.eaton.com/Products-services/Backup-Power-UPS/9390.aspx?cx=3
9.1.4 Transfer from Normal to Bypass Mode
To transfer the critical load to Bypass mode:
C A U T I O N
In Bypass mode, the critical load is not protected from commercial power interruptions and abnormalities.
1. Press the CONTROLS pushbutton on the main menu bar. The System Controls
screen appears.
2. Press the BYPASS pushbutton on the System Controls menu bar.
The UPS transfers to Bypass mode and the critical load is immediately supplied
by the bypass source. If the bypass source is not available, the power processor
remains on and an alarm sounds.
3. The UPS is now operating in Bypass mode and the BYPASS status indicator is
illuminated.
The power module (PM) status indicates READY. The system is now on bypass
and the UPS power processor remains on.
At this point, you can operate an external bypass switch to get to maintenance bypass if needed.
Oct 14, 2009 | Eaton PW9390 UPS System
Bypass LED on the ups is on
This an excerpt from the UPS's manual:
The Bypass LED illuminates indicating that the UPS is in bypass mode. Utility power is sent directly to connected equipment during bypass mode operation. Bypass mode operation is the result of an internal UPS fault, an overload condition, or a user initiated command through an accessory. Battery operation is not available when the UPS is in bypass mode.
Jul 19, 2009 | APC Smart-UPS 1000VA UPS System