Question about Ingersoll Rand Electrical Supplies
Won't stay running
I can heat fuel and turn key and the gen will start and then go dead I can crank again and it will go dead. I can have someone hold the fuel shut off up and it will stay running none of the system check lights come on when you push the button to check the system this is a g25000 kw diesel
CarlGehrke
  • 169 Answers
SOURCE: Gen. set won't auto start.
This sounds a little like a bad wiring problem between the transfer switch and the generator. But before I leap to any unfounded conclusions let's make sure I understand just which Guardian generator and transfer switch you have. The generator I think you have is an air conditioner sized box that has a 2 cyl air cooled Generac GT990 engine in it. The control panel has a 15 amp fuse, and maybe a 7 amp one, some LED indicators, a 3 position rocker switch (manual,off,auto), and a momentary set exercise switch. If you look inside your transfer switch there is the transfer mechanism, a single relay, either 2 or 4 fuses, and a terminal board where 4 small control wires connect to the generator. The control wires will be labeled N1, N2, 193, and 23.
If all of that is true then I'll also assume that the generator is blinking all of the LEDs and as soon as you put the rocker switch in the manual position the generator starts and the transfer switch moves to the "generator" position. It shouldn't do that, manual means switch the switch manually too. :-)
Let's take care of the exercise setting first. Switch the main output breaker of the generator to the "off" position, this prevents the transfer switch from activating even if the generator runs. Next put the generators rocker switch into the "Auto" position and wait at least 1 minute, if the generator starts we have to fix the wiring between the N1 and N2 terminals in the transfer switch and the matching terminals in the generator before we can proceede. If luck was with us and the generator is just blinking its LEDs at you, press and hold the set exercise switch for 30 seconds, you're reseting a "watchdog" type circut so it has to be for the whole 30 seconds. When you let go of the set exercise switch the LEDs should blink another 10 times or so, then the generator should start and run its exercise for 12 minutes more or less and then it'll shut down. At that time the only LED that should be lit is the green "system ready" one and it should be steadily lit. Remember to close the output breaker again.
Next let's address the transfer switch issue. If I've understood you correctly, the transfer switch moves anytime you turn the generator on. The only reason a regular old RTS type transfer switch could do this is that it's being commanded to transfer. It works like this, the 2 coils that move the transfer mechanism get powered by the source we're trying to switch to, once the switch gets into the position it's going a pair of limit switches disconnect it from the power supply so that the coil is only "live" during a transition. Spring loaded contacts hold the switch in either position once it's more than halfway towards either one. The relay inside the box is also in line with the limit switches so that if the relay is deenergised the switch will try to get to the utility position and stay there, it can't if there is no utility power to drive the transfer coil. On the other hand if the relay is energised, the switch will try to get to the generator position and stay there, if there is no power from the generator it can't because the generator is what drives that bottom transfer coil. So I think that for whatever reason the relay in your transfer switch is staying energized when we don't want it to be.
On the terminal board inside the transfer switch you should see terminals labeled 194 and 23, these are the power to the relay coil (194), and the ground to transfer signal (23). With the generator set to off, and a fairly quiet room, disconnect the wire from terminal 23, if you can hear the relay coil click on and off when you touch the wire to terminal 23 there is something wrong with the wiring at the generator end of things. You should also see 12 volts DC between terminal 194 and ground, this comes from the generator too.
If the relay didn't click back and forth above check it by using a short piece of wire to connect terminal 23 to ground, if the relay isn't energised when terminal 23 is grounded and deenergized when terminal 23 is open you either have a bad relay or a problem in the grounding of your system. To get a bad relay fixed for free call up Guardian, register the generator (you'll need proof of purchase), and get them to tell you where your nearest warrenty service person is. If you tell him about this post he'll bring a relay with him when he comes to you.
If you're satisfied that the relay in the switch is working properly, we're on the trail of a wiring problem at the generator end of things. If the generator has just been installed you should carefully check that wire 23 hasn't been connected to terminal 0 at the generator terminal block. It's easy to get this connection wrong when doing th e install. The other thing that can go wrong is that the wire can get pinched inside the conduit and short to ground. To check this disconnect both ends of wire 23 and measure between either one and ground, you should get nearly infinite resistance.
If you've proved to yourself that all of the wiring is correct, and the generator is properly grounded, you probably have a broken control board in the generator. To get the control board replaced use the same procedure as the relay above.
If that doesn't get this resolved for you post a comment and we'll try a different approach.
Regards,
Carl
Posted on Mar 06, 2009
  • 905 Answers
SOURCE: Gen starts and runs with rocker start button pushed in..stops....
Cleaning the brushes is used to address an AC output problem. If the generator would run for a few seconds after letting go of the button, then this might apply.
But, since yours is dying as soon as you let go of the button, that tells me that you are probably looking at a low oil condition, or a sensor / sending unit failure for oil level.
Without spec number, hard to remember if the sending unit is for low oil pressure, or low oil level. Either way, the ignition is being grounded. First, double check your oil level, make sure generator is reasonably level. If still not resolved, then locate the sending unit, and remove the wire that is on the end of it. There should be a connector either a few inches from the sending unit, or a few inches from the control board (coming from big white plug). Disconnect at either place. Try starting again. If it starts this time, double check oil levels. If those are fine, then sending unit has failed, or oil pump (if pressure unit) has failed. In either case, don't run for very long until sending unit is replaced, just in case.
Posted on Aug 25, 2009
  • 5603 Answers
SOURCE: Starts, runs a few seconds then shuts down. Will
Check for a low lube oil sensor problem first. Could be low oil pressure or a failed sensor. The sensor is timed and if pressure doesn't come up, then unit is shutdown.
Check fuel filter and also air leaks in the fuel supply lines.
Check if the fuel shutoff solenoid is responsible for the shutdown. If it closes just before the engine quits, then it is being commanded to shutdown, probably as a safety interlock.
Posted on Oct 11, 2009
Testimonial: "Very good info. I don't think I have a fuel shutoff seloniod unless it's internal to the injector pump."
kel1guy2002
  • 3740 Answers
SOURCE: Colman Powermate Generator will not stay running
This overflow can be caused by:
1. The float sticking
2. Gas inside of the float air chambers
3. The needle and seat have debris in them or a r damaged.
It is not a difficult fix but it does mandate removal of the carburetor float bowl.
You could probably do this yourself. It is much easier if you place the generator on a high work area so you can see the float and needle once you have the float bowl removed. Just make sure you do not drop the float assy so far that the needle comes out of the seat unless you have to remove the hinge pin SCREW for the float to clear the debris near the needles' pointed rubber head.
Thanks for using FixYa
Kelly
Posted on Mar 22, 2010
  • 5603 Answers
SOURCE: Hi, My Kipor 6700TA wont start. Battery died or fuel issue?
It sounds like your unit may not be charging the battery properly.
Try charging the battery and see if it responds properly. If it does, then check the charging circuit. This OFTEN involves a rectifier module which is usually about 1 inch square with four leads. OFTEN there is a fuse, sometimes within the generator housing (stupid place) which protects the low voltage winding.
Here is a hint: Most of these engines have a compression release on the top that one can press then crank up to speed and release. This takes much less effort on the battery. Some have a panel held by bolts. I put hinges on mine for easy access.
REMEMBER the battery is being drained WHILE the unit is running to hold the fuel solenoid open... so if charging isn't working the battery will die.
Test: You should see about 13.75 to 14 volts across the battery when properly being charged while running.
Posted on Apr 06, 2010
There was lots of corrosion on fuel filter n now it has new filter,new fuel pump,new regulator n it won't start with out starting fluid once it starts it stays running,this is a 05,hino 338,
The pump should turn on for about 2 seconds with key in the on position, this to put pressure in the lines and to the engine for starting. Then when cranking, the pump should be on again. The engine computer should be signaling the fuel pump relay to turn on during these two times. If the new pump won't turn on, something is wrong in your fuel pump circuit. Check the fuse for the pump first. Then find the fuel pump relay. Hold your finger lightly on it while someone turns the key to on. You should feel a click. If it does, verify voltage is going to the pump: look for voltage on the pump wire when the engine is cranking. If no click, the circuit from the computer needs checked.
Jul 17, 2015 | Cars & Trucks
3006 chevy trailblazer turns over but wont start
That year has not been made yet and we wil be dead if and when it is. 2006 trailblazer could be fuel pump, do a fuel pressure test. CKP sensor scan for rpm, check for codes. Does it crank fast or slow? Try taking a hammer and hit the bottom of the fuel tank while someone turns th key and makes it crank. If it starts replace the fuel pump. See if it is getting spark at plugs by taking a screwdriver and insert in plug wire after you remove from plug and hold just enough away from a metal bracket and have someone turn the key to start and see if you have spark. Do not touch metal part of screwdriver.
Jul 06, 2014 | 2006 Chevrolet Trailblazer
Car won' start, battery is ok, antifreeze is low but not out could this be the problem?
No. it wouldn't keep it from starting. If the engine cranks but won't start, probably gas or spark (ignition) related. Do you hear the fuel pump in the tank turn on for a couple of seconds, when turning key to on, not start? If you cannot hear the pump, better check if you are getting gas up to the engine. Maybe the fuel pump quit, or the pump circuit needs looked at. The pump should briefly turn on with key on to pressurize the fuel system-the fuel line and the fuel rail where the injectors are. Then the pump will turn off, and only come back on again when the engine is cranking, and stay on when running.
Correct fuel pressure is important for easy starting, and good engine performance. Have the fuel pressure checked against the specification for your vehicle. If fuel pressure is good, check the ignition system-check for spark.
Dec 31, 2013 | Cars & Trucks
GMC 2000 sierra pick up 1500 sounds like it wants to start but won't turn over. Battery sounds good so I guess battery and alternator are ok. For several years fuel gauge doesn't work and...
It sure could be. But, first...by "won't turn over" you do mean it cranks at normal speed but won't start?
A simple test of the fuel pump is to stand by tank and listen as someone turns key to on. When first turned to on, your pump will activate for 2 or 3 seconds, pressurizing the fuel system, and then shut off if the engine computer doesn't get a cranking signal. Do you hear it come on? If not, then something's not turning your pump on. If you can hear it buzz on briefly, then maybe it's your filter. Another test: Spray a little starting fluid into your intake manifold (remove the big hose going into intake manifold) while someone tries starting it.If it doesn't fire and try to stay running, then it's probably an ignition problem. But if it does fire off, then you know it's a fuel problem-likely your pump or filter. good luck.
Nov 07, 2011 | 2000 GMC Sierra
1999 gmc sierra 2500 6 liter ran out of gas now won't start
If you are at or near the 100,000 mile mark then your fuel pump may have failed. If you remove the fuel filler cap and listen carefully at the filler neck while someone turns the ignition key to "run" [don't actually crank the engine] you should be able to hear the fuel pump buzz for about a second and a half as the key is turned On. If you don't hear the pump buzz then odds are your pump is dead. Your pump may have actually failed making it appear as though you ran out of fuel. Not to uncommon. Hope this helps and good luck!
Nov 01, 2011 | 1999 GMC Sierra
My suburban just stop while i was driving
And what does it do now? Does it crank over and not start, or just no power anywhere? If nothing, no power, recheck your battery connections, grounds, for something jarring loose, maybe a relay in the power distribution center (by your battery) jumped out of its socket. Gotta check around...But if it cranks over, but won't start, you need to review the basics for this condition: needs fuel and spark to run. Are you getting fuel up to the engine? Can you hear the fuel pump buzz on for 2 seconds when you turn key on? That 2 seconds is to pressurize the fuel line. When you start cranking, your pump will come on again, and stay on when engine is running. You can only HEAR the pump when someone turns key to on, and you stand or squat near the tank to listen for it, maybe with tank fill cap removed. If you cant hear the pump your FP relay would be the next place to look for a problem of no power to pump. If pump IS working, then back to engine: check if ignition (spark ) is working. Easiest way: pull spark plug wire, remove plug and put it on the wire you pulled off. Ground the threads of plug on metal of engine, have someone crank it, and watch for spark at that plug. If no spark, check another wire with same plug. No spark means you need to diagnose your ignition starting circuit. Among other things, this involves checking for power to coils, power to the computer (your check engine light DOES come on when key on, right?), a lot of things that a diagnostic flow-chart covers to pinpoint the problem. A good repair manual could walk you through it, if you have a multimeter. If not, you may need someone to help you. If you DO have both spark and fuel up to engine, it's simplified some, but still problematic. Crank position sensor? injector circuit? Good luck, M>, and don't give up.
Oct 25, 2011 | 1999 GMC Suburban
Myy 99 ford expedition won't stay start, it will crank up but wont stay crank have a full tank of gas
its going to either be a fuel problem or electrical,, so check fuel first ,, get a can of carb cleaner, or quick Start,, spray some in the air intake as someone tries to start the vehicle, if it runs as long as your spraying, ( don't so this too long ) then you have a fuel issue, the easiest thing to do is change the fuel filter , try that first ,, if that doesn't fix it, your going to have to check the fuel pump,, now,, if none of that helped,, pull a plug , whatever one is easiest to remove, and put the plug wire back on ,, hold the plug with insulated pliers , ( so you don't get zapped) and ground the end of the plug against a bolt head anyplace on the motor, hold it there while s friend or someone cranks the car over, you should get a nice blue spark at the tip of the plug,, if you do ,, its again a fuel problem,, if you don't,, check the cap and rotor, any tiny crack in the cap, or build up of corroded contact tips inside the cap, will cause these problems your having, clean them off as good as you can and also clean the rotor tip, see if that helps, if it does, replace the cap as soon as you can, and also the rotor, if this doesn't help, your going to have to get the coil checked, and trace everything back to the ignition
Sep 22, 2011 | 1999 Ford Expedition
2001 PT Cruiser turn key to start nothing, no power, lites etc... I jump start it and it starts right up. turn off and try to re start, nothing. jump started again fired right up, while running tested...
common car for starter problems hit the starter with a hammer while someone trys to start it if this works it is ure starter, if not the stater and neutral safety switch needs tested
Oct 14, 2010 | 2001 Chrysler PT Cruiser
Electrical Supplies Logo
47 people viewed this question
Top Ingersoll Rand Electrical Supplies Experts
cwradio73
Tom Chichester
Rhonda Webster
Rhonda Webster
Are you an Ingersoll Rand Electrical Supply Expert? Answer questions, earn points and help others