    Problem Solver:
  • 17 Answers
Sounds like you may have to clean the flame sensor.
Posted on Jul 30, 2014
Furnace will not kick on
going out on high limit which requires manual reset
Dec 15, 2013 | Intertherm P3RA-048K Air Conditioner
Amana furnace. The furnace goes through the cycle but wont ignite. I have already checked the ignitor.
Try blowing out the jet Burners with compressed air especially the one nearest the Ignitor. Right through where the gas comes in. These can get dusty and cause ignition failures. Also check to see if the Ignitor is in the path of the burner and has not somehow gotten bent. 100 or so ohms on the Ignitor should be good.
Oct 10, 2012 | Amana GMVC80905CX Gas Furnace
I have a goodman high efficiency furnace, model gms9/gcs9. I've had several furnace techs look at it scratching thier heads. It won't fire up, the ignitor comes on but won't flame the unit. I...
check to see that your condensate line is not plugged. next check the p-trap where your line goes in. also check your flue abs flue pipe see as it comes out of roof is it open or does it have an elbow coming off of it i usually install with elbow preferably less water goes in the units resevoir hope that helps u
Apr 04, 2012 | Goodman Heating & Cooling
No heat, one flash says limit circuit open on my furnace
If your limit circuit open it is an indication of either a power surge opening the circuit OR that your furnance has another problem and the limiter opened because of it. You can buy and replace the limit circuit, but if it opens right away, you will need to go further into your furnace.
Jan 16, 2012 | Frigidaire Dryers
The furnace comes on just briefly then goes off, after a time it will come back on and stay on. Is this normal?
Yes, depending on exactly what you mean by furnace on. Many furnace fans react only when plenum temprature reaches a certain amount.... (helps keep from blowing cold air) The circulation fan can run several times after burner shoutdown, based on the temp....
Mar 01, 2011 | Honeywell Heating & Cooling
My heater isn't blowing any heat. I hear the fan come in, and i think i hear the gas come on, but nothing comes out of the vents. The fan only comes on for a couple of minutes and then goes off.
Ok so here is a sequence of the heater lighting and the solution for your problem...
1. Thermostat calls for heat. 2. Draft inducer motor starts. 3. Pressure switch attached by a small plastic or rubber tube senses the negative pressure produced by the draft inducer and closes. 4. Draft inducer runs for 30 seconds to a minute before you hear a gas hissing sound. The ignitor did not glow, the flame sensor (a small metal probe about 1/8" in diameter, with a white porcelain base) does not sense the flame, so after 8 to 10 seconds the hissing sounds stops with no ignition of gas to heat your home. Your furnace shuts down and goes into a lock out condition until you turn your power switch back off and on again. Then the sequence starts all over again with no ignition of the gas. Solution:You probably need to purchase and install a new ignitor. I would suggest that you inspect your ignitor closely for cracks.Make sure you do not touch the ignitor with your bare hands. If you do not visually see a crack, then you could have a furnace control board problem or a limit, rollout switch problem. Please see "limits, rollout switches & furnace control boards" further down on this page. The furnace's control board might not be supplying the voltage to the ignitor. If your furnace lights and the gas stays on for 8 to 10 seconds, then shuts right back off, then you need to clean your flame sensor with light sand paper or steel wool. You might need a new flame sensor, but most of the time they can be cleaned an will work well after cleaning. Please see the pictures below to help you identify a flame sensor.
Thanks and I hope this helps. Feedback apprec.
Jan 28, 2011 | Honeywell Electronic Programmable...
Lennox furnace 17 yeanrs old. flame comes on and the shuts down sometimes right away some times in a few minutes. We have the furnace go down to 58 at night. It takes all day to get back to 67.
Sounds like a dirty flame sensor.
Also 9 degrees is a large swing to recover. Most specialist will advise no more than a 5 degree set back, otherwise recovery time eliminates any savings you may achieve.
Dec 05, 2009 | Dayton (3E407) Heater
Trouble Wiring in Rheem heat pump
The red wire goes back to the furnace red, the blue back to the thermostat blue, the brown back to the furnace C terminal, the yellow back to thermostat Yellow (if there is a Y terminal on that furnace, land your Y's there. The purple wire outside comes back and ties to the W terminal on the furnace. Now you have a dual fuel unit so you will need a dual fuel kit or a thermostat that has dual fuel capability along with an outdoor sensor.
Jul 02, 2009 | Ruud UBHC Air Conditioner
Heating
If this is an older furnace, it is probably a wearing fan control.
Some can be adjusted, otherwise they need to be replaced.
Jan 02, 2009 | Heating & Cooling